d) If the system Category is such that automatic fire detection should be provided in any area that
contains a horizontal void of 800 mm or more in height, automatic fire detection should also be provided
in the void.
BS 5839-1:2002
--
I would interpret that as saying "If a detector is required in any room that has a void > 800m over it, then the void needs to be detected."
Then see:-
--
NOTE 4 If the fire risk within a void of 800 mm or more is considered to be low, consideration might be given to omission of fire
detection from the void, subject to the agreement of the interested parties (see Clause 6), but this should be recorded as a variation
on the relevant system certificate. This might arise, for example, if the probability of ignition and development of fire in the void
were very low, or if the void were limited in extent so that spread of fire beyond the room of origin, via the void, were unlikely.
BS 5839-1:2002
---
So, if the risk is as you say it would seem reasonable.
(When you say there are no combustibles in the voids, are there false floors for all the data cables? Data cables can soon add to the fire loading in voids and they don't tend to appear until the building is occupied.)