Green Boxes
« on: January 18, 2011, 01:38:24 PM »
This question is not related to any particular permise or incident just as a thought I had.

Does the team think there is a need to individually test the "Green Boxes" which release electronically locked doors in the same way that MCPs are tested?

All I have found is in BS 5588 pt 12.

"L.4.7 Automatic opening doors
The operation of fail-safe mechanisms should be tested once a month, either by “breaking-out” the doorset
or by simulating failure of the mains power supply, as appropriate. The results of the test should be
recorded. Any doors that are found to be faulty should be repaired or replaced."

(Candidates should not attempt to write on both sides of the paper at the same time)
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: Green Boxes
« Reply #1 on: January 18, 2011, 01:41:29 PM »
Yes. Although not very often

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Green Boxes
« Reply #2 on: January 18, 2011, 02:05:40 PM »
Commonsense suggests that anything on which reliance is expected in safety situations needs to be tested for correct operation on a regular basis.

BS7273-4 Clause 22.3 a) recommends that the Emergency Door Release switch (green box) is tested at least once in a twelve month period.

My own opinion is that because the EDR is the ultimate safety device on a system (if all other controls fail, operation of it should always be able to allow emergency access through the door) it should therefore be tested as regularly as possible. A twelve month testing cycle seems far too long to me.

Midland Retty

  • Guest
Re: Green Boxes
« Reply #3 on: January 18, 2011, 02:07:35 PM »
Hi Mike

Brief answer is yes they certainly need to be tested, because you need to be confident that when required, the units will work.

Monthly tests sound reasonable, but again it does depend upon the location and MOE arrangements, and if it is a relatively small premsies, and BGUs are located by every MCP, then why not test them weekly along with the MCPs as a matter of course?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Green Boxes
« Reply #4 on: January 18, 2011, 04:12:16 PM »
BS7273 Section 22 recommends that user checks are carried out weekly.
We're not Brazil we're Northern Ireland.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Green Boxes
« Reply #5 on: January 18, 2011, 04:54:48 PM »
BS7273 Section 22 recommends that user checks are carried out weekly.

N.T., your post makes my earlier answer to appear to be wrong!

However, the bit in BS you are referring to only recommends that the door release mechanism is tested with a fire signal weekly. The original question was about testing the 'green boxes' not the door release mechanisms.

Please do not confuse the issue by quoting recommendations that are not precisely applicable to the question!

Midland Retty

  • Guest
Re: Green Boxes
« Reply #6 on: January 18, 2011, 05:16:59 PM »
Yes I have to concur with Wiz - basically the release mechanisms are checked when the manual call points are tested weekly

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Re: Green Boxes
« Reply #7 on: January 18, 2011, 05:31:39 PM »
Wiz,

is it true then that you are becoming an expert on 7273 part 4 as well as Mr Todd?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Green Boxes
« Reply #8 on: January 18, 2011, 05:32:17 PM »
Question was:-
"Does the team think there is a need to individually test the "Green Boxes" which release electronically locked doors in the same way that MCPs are tested?

In your reply you seem to be suggesting that green boxes are tested to see if they work, not that they release the securing device? How do you do that without the device operating? How can you tell they work unless they do what they are suppose to do?
Same way that how can you tell the MCP is working unless it performs the function for which it intended, ie sound the alarm.

Do you think that the question only related to the working of the box, not what it does?
Does 22.1.2 not imply that the purpose of the test is to check the working of the release mechanism, weekly?
But maybe I am wrong and you are always right.



« Last Edit: January 18, 2011, 05:55:38 PM by nearlythere »
We're not Brazil we're Northern Ireland.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Green Boxes
« Reply #9 on: January 18, 2011, 05:34:38 PM »
Yes I have to concur with Wiz - basically the release mechanisms are checked when the manual call points are tested weekly

But then you are also much more civilised and mannered in your response.
We're not Brazil we're Northern Ireland.

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Re: Green Boxes
« Reply #10 on: January 18, 2011, 08:06:00 PM »
The question was specifically about the boxes. The actual door releases are usually tested during the weekly fire alarm test, a MCP is tested the alarm goes off and people ensure that the doors unlock. I raised the question as to whether there was a test routine for the actual box to that it would operate independantly of the alarm. Afterall the aim of the box is to release the door, if it fails to release with the alarm. As such I feel it should be tested independantly and the results recorded.
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Green Boxes
« Reply #11 on: January 18, 2011, 11:00:32 PM »
I do agree however I think the little green buggers should be the same make as the red buggers , lot of sites where i go to are happy with the kac type , thats kiddeminster alarm company for all us old uns, but some of these green releases can be a nightmare even for an engineer - just thought i would throw that into the ring.
« Last Edit: January 19, 2011, 03:33:50 AM by Galeon »
Its time to make a counter attack !

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2489
    • http://www.firewizard.co.uk
Re: Green Boxes
« Reply #12 on: January 19, 2011, 01:04:14 AM »
They do need testing for sure. I once put a test key in one and not only didn't it release the door lock, it isolated the normal 'Push to exit' button as well so that wouldn't work either!

Fortunately I just removed the key but in a real emergency if the glass had been broken everyone would be trapped.

Sadly every week a different make of call point box seems to appear and I need to chase down and 'aquire' another different reset/test key....

Oh for the days you could get away with carrying just KAC, Gent & Menvier plastic keys, an Allen key, triangle key and screwdriver and this test/reset/replace glass in 99% of call points.

I now carry well over a dozen MCP & EL test keys (plus the Allen key, triangle key and screwdriver) and still need to find more different ones....
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Green Boxes
« Reply #13 on: January 19, 2011, 08:49:49 AM »
Wiz,

is it true then that you are becoming an expert on 7273 part 4 as well as Mr Todd?

No Jokar, but I had to read it to form the negative opinions I have about it!

However, obviously, even I can understand some of it.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Green Boxes
« Reply #14 on: January 19, 2011, 09:22:37 AM »
The question was specifically about the boxes. The actual door releases are usually tested during the weekly fire alarm test, a MCP is tested the alarm goes off and people ensure that the doors unlock. I raised the question as to whether there was a test routine for the actual box to that it would operate independantly of the alarm. Afterall the aim of the box is to release the door, if it fails to release with the alarm. As such I feel it should be tested independantly and the results recorded.

So I did answer your question correctly and precisely, Mike. I wouldn't want to quote BS recommendations which are not strictly relevant.

The only recommendation in BS7273-4 for testing the Emergency Door Release switch (green box) is that it is carried out every year. The weekly test recommendation only mentions using a fire alarm signal to ensure the door release mechanism operates and has no mention of the EDR.

Personally, I feel that once a year is nowhere near often enough for such an important part of the system.

Interestingly, the weekly test is under the heading of Routine Testing, whilst the annual testing of EDRs is under the heading Inspection and Testing. With the latter being carried out by a 'competent' person.

I can't see why the Routine Testing (presumably carried out by premises staff) shouldn't include the EDR, so that it is tested weekly. But this is only my opinion and not the BS recommendation. They obviously don't consider the EDR as important as the other equipment on the fire signal path in ensuring the correct operation of the door release mechanism.

« Last Edit: January 19, 2011, 09:36:40 AM by Wiz »