Author Topic: 7273-4 General Question  (Read 12045 times)

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: 7273-4 General Question
« Reply #15 on: November 17, 2015, 09:33:29 AM »
Apparently understanding 7273 is on the list along with doing crosswords and learning a foreign language as one of the things to hold off early onset alzheimer's ........  ;D
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: 7273-4 General Question
« Reply #16 on: November 17, 2015, 08:39:14 PM »
In respect of the recent BS 7273-4 Revision Iunderstand that BAFE have issued the following directive: (thanks Dave)


All parts of BS 7273 are normative within BS 5839-1:2013 and clause 9.2(a) of BS 5839-1:2013 specifically states:

?The system should conform to the recommendations of any applicable part of BS 7273?.

In order for a system to be compliant to BS 5839-1:2013 it must, where applicable, meet the recommendations of BS 7273-4:2015. Therefore, when preparing system design proposals (specifications) where there is intention to interface to devices covered by BS 7273-4:2015 then the system design proposal must, in addition to any other relevant standards, call up BS 7273-4:2015 and state the category of actuation it is proposed to install (see BS 7273-4:2015, clause 4.2).
When selecting fire alarm control & indicating equipment, in addition to ensuring that the equipment you select is third party certificated to BS EN 54-2, you should also take care to ensure the equipment selected can meet the recommendations for operation & fault monitoring contained within BS 7273-4:2015; if in doubt you should consult the manufacturers of the CIE.

With effect from 01 October 2015 systems must, where applicable, be designed to comply with the recommendations of BS 7273-4:2015 and our auditors will audit systems against the recommendations of BS 7273-4:2015 in addition to the recommendations of BS 5839-1:2013 and any other applicable standards.

This would seem to indicate that things have moved on? or have they?
« Last Edit: November 17, 2015, 08:46:51 PM by kurnal »

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: 7273-4 General Question
« Reply #17 on: November 18, 2015, 10:34:06 AM »
Yep .... our inspector is certainly more on the ball ............. !
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic