FIRE SAFETY => Fire Alarm Systems => Topic started by: Sherpa on October 20, 2010, 05:35:24 PM
-
Gents
Am i correct in saying that under BS5839 A2 you can install fire alarm cables in pyro along side PA cables in FP200?....When i say along side they are to installed on the same traywork..
I always thought they could not be mixed, but now am been told otherwise.
thanks
Sherpa
-
MICC cable has it's own mechanical protection and is not likely to be damaged by other cables being installed in the same tray.
Not seen that part in A2 but that's not to say it there. Most jobs i have been on now have one tray for all ELV cables to be installed on.
-
To do what you say is fine with the only proviso that neither manufacturer says you shouldn't (for EMC reasons).
-