At a new block of flats,just come across an 'inlet' box underneath a manhole cover just below ground level. It is configured so that the drain cock cannot drain. Obviously this could freeze out the inlet in a harsh winter. From what I have been able to read this does not comply with 9990 or 5041-5. Any one had similar/have any solutions? Could the fact that it cannot be 'maintained' remedial works be enforced by the FSO?
-
Unlike planning applications there is no public access to BC applications and thus one cannot be sure if in this new block the inlet has been notified as an issue.
-
Thanks-the submitted plans I have seen show the inlet box's in the walls-so not built as proposed. Still can't see why the underground inlets would be approved-lots of views but no comments!
-
The answer lies with the FRS. Were they consulted by BC? Although if the plans showed the inlet in a wall with satisfactory access they would not comment. Did they do a completion inspection? The FSO only requires the RP to maintain what?s provided so I would suggest that BC should be addressing this. Have you spoken to the FRS?
-
Thanks Seetek, I have all those answers, in regard to FRS/BC. What I am after is some solutions-throwing hay straw into the pit and lighting it up ala MOF won't cut the mustard nowadays. Relaying the inlet into the building will be problematic. Some pipe lagging/trickle heating?
-
It's not the only time - I've seen a site with an underground inlet that was passed. Gets wet tested each year & seems to be OK. It's very unusual though, always been wall mounted everywhere else I've been to