Author Topic: Part 1 vs Part 6  (Read 3340 times)

Offline North London

  • Newbie
  • *
  • Posts: 1
Part 1 vs Part 6
« on: February 01, 2007, 01:32:06 PM »
I have just completed a loft conversion and need to install fire precautions. My property is a second floor flat and I have just added a third floor.

The council have advised that I have I must comply with either of the following:

1. BS5839 Part 1 L3

or

2. BS5839 Part 6 Grade D LD1

Which they have said means detectors in escape routes and risk rooms (which they say is every room in the house except bath rooms) suitably interlinked.

This effectively means a very costly system given the grade and number of detectors(8 in total).

My understanding is that I really should only need detectors in the Kitchen and then on each landing/entrance (hence 3 in total)

Are they trying it on?

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Part 1 vs Part 6
« Reply #1 on: February 01, 2007, 02:20:56 PM »
It sounds as though the building has been divided into several separate dwelling units and is being treated as a house in multiple occupation. If this is the case they are applying the correct standard.