Author Topic: metal ties  (Read 42842 times)

Offline Thomas Brookes

  • Sr. Member
  • ****
  • Posts: 290
Re: metal ties
« Reply #30 on: June 06, 2009, 08:09:20 AM »
This is my point exactly.

Everyone has a slightly different opinion, why not just put it in the standard "only metal clipsor fixings are  to be used at spacings not exceeding 12 inches".

No more confusion.
I refuse to have a battle of wittts with an unarmed person.

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: metal ties
« Reply #31 on: June 06, 2009, 11:30:38 AM »
It's amazing, that when we install we use metal every 1 metre and plastic at intervals between that, and this is always approved by LPS1014 when we are audited.  Yet there are still so many opinions on this, probably why we see so many variants in installation methods.  It's interesting to see others points of views.
** Knowledge is power, I'm still working on both **

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: metal ties
« Reply #32 on: June 06, 2009, 09:54:04 PM »

As the man said......"it's a funny old game........!!! "
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: metal ties
« Reply #33 on: June 07, 2009, 02:06:29 AM »

As the man said......"it's a funny old game........!!! "
Small jumpers,boys for goal posts!

Offline GregC

  • Full Member
  • ***
  • Posts: 180
Re: metal ties
« Reply #34 on: June 08, 2009, 10:26:35 AM »


.........And does this then mean that even "enhanced" cable is no better than standard if it isn't clipped properly??


I would suggest that either cable has the potential not to meet it's specified abilities if it is not installed strictly in accordance with the manufacturer's recommendations.

If the manufacturer's recommendations are to a higher standard than the BS (or any other) recommendation then the manufacturer's recommendation takes precedence.

Ahh, but Wiz, the manufacturers do not call for metal clips, they ask for support at prescribed distances, do they not?
But plastic ones would not support Gregc.

Actually they would support the cable correctly, right up to the point they melt :)

The point I feel most people are missing is not the supporting of the cable that is the issue, its keeping the cable in the correct position in a fire condition to prevent it weakening and failing, the 1 metre spacings are almost as bad as no metal clips at all under those circumstance imo.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: metal ties
« Reply #35 on: June 08, 2009, 10:37:04 AM »
Greg
Like plastic clips a piece of string would support a cable right up to the point when it is burnt through.
Is "supporting the cable" and "keeping it in the correct position in the event of a fire" not the same?
We're not Brazil we're Northern Ireland.

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: metal ties
« Reply #36 on: June 08, 2009, 10:51:45 AM »
Personally I can't see how a cable metal tied every meter is going to significantly move ....

If it's that fragile perhaps we should all go back to MICC........
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: metal ties
« Reply #37 on: June 08, 2009, 12:07:58 PM »
Personally I can't see how a cable metal tied every meter is going to significantly move ....

If it's that fragile perhaps we should all go back to MICC........
Metal conduit and saddles it is then!

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: metal ties
« Reply #38 on: June 08, 2009, 01:26:13 PM »


.........And does this then mean that even "enhanced" cable is no better than standard if it isn't clipped properly??


I would suggest that either cable has the potential not to meet it's specified abilities if it is not installed strictly in accordance with the manufacturer's recommendations.

If the manufacturer's recommendations are to a higher standard than the BS (or any other) recommendation then the manufacturer's recommendation takes precedence.

Ahh, but Wiz, the manufacturers do not call for metal clips, they ask for support at prescribed distances, do they not?

Ahhh but Greg C, the BS asks for fixings equal to the fire resistance of the cable. As I said  'If the manufacturer's recommendations are to a higher standard than the BS (or any other) recommendation then the manufacturer's recommendation takes precedence. I said if, so if it doesn't, then BS rules!!!!!

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: metal ties
« Reply #39 on: June 08, 2009, 01:29:27 PM »


.........And does this then mean that even "enhanced" cable is no better than standard if it isn't clipped properly??


I would suggest that either cable has the potential not to meet it's specified abilities if it is not installed strictly in accordance with the manufacturer's recommendations.

If the manufacturer's recommendations are to a higher standard than the BS (or any other) recommendation then the manufacturer's recommendation takes precedence.

Ahh, but Wiz, the manufacturers do not call for metal clips, they ask for support at prescribed distances, do they not?

Ahhhhhhh but GregC. Now you're making things up! I never ever said that the manufacturers call for anything in particular.

In fact, that is often the problem!
« Last Edit: June 08, 2009, 01:41:59 PM by Wiz »

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: metal ties
« Reply #40 on: June 08, 2009, 01:39:35 PM »
It's amazing, that when we install we use metal every 1 metre and plastic at intervals between that, and this is always approved by LPS1014 when we are audited.  Yet there are still so many opinions on this, probably why we see so many variants in installation methods.  It's interesting to see others points of views.

It could be the auditors have actually ascertained the precise type and manufacture of the cable you have used and have checked that your fixing method/spacings is appropriate to the manufacturer's instructions for that type of cable.

Alternatively, the auditors haven't got a clue about the type of cable and it's fixing requirements and have just thought 'that doesn't look obviously wrong (i.e only plastic ties etc), so I'll assume it is o.k.'

It wouldn't surprise me if it was the latter, because I've found that most cable manufacturers provide scant information about fixing their cables.

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: metal ties
« Reply #41 on: June 08, 2009, 01:45:01 PM »
It's amazing, that when we install we use metal every 1 metre and plastic at intervals between that, and this is always approved by LPS1014 when we are audited.  Yet there are still so many opinions on this, probably why we see so many variants in installation methods.  It's interesting to see others points of views.

It could be the auditors have actually ascertained the precise type and manufacture of the cable you have used and have checked that your fixing method/spacings is appropriate to the manufacturer's instructions for that type of cable.

Alternatively, the auditors haven't got a clue about the type of cable and it's fixing requirements and have just thought 'that doesn't look obviously wrong (i.e only plastic ties etc), so I'll assume it is o.k.'

It wouldn't surprise me if it was the latter, because I've found that most cable manufacturers provide scant information about fixing their cables.

I wouldn't be suprised if it was the latter either.  What seems just a basic concept has really unearthed a can of worms
** Knowledge is power, I'm still working on both **

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: metal ties
« Reply #42 on: June 08, 2009, 01:49:27 PM »
This is my point exactly.

Everyone has a slightly different opinion, why not just put it in the standard "only metal clipsor fixings are  to be used at spacings not exceeding 12 inches".

No more confusion.

Thomas, as I previously said, a rigid recommendation unfairly disallows those cable manufacturers whose cable works correctly with fixing spacings every 1m instead of your suggested rigidly prescribed 12 inches.

The BS recommendation is perfectly well written.

It is up to the various cable manufacturers to fully and properly advise installers what type and spacing of fixing is required to meet the specified fire resistance.

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: metal ties
« Reply #43 on: June 08, 2009, 02:02:27 PM »
Having looked at a few data sheets from different cable manufacturers, for their types of cables (including the large manufacturers) the recommend the use of metal every 300mm H and 400mm V.  So this throws it all open, something which I have'nt realised, and stuck to the BS recommendation in the past.  Something which I think I will have to look into a bit deeper now
** Knowledge is power, I'm still working on both **

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: metal ties
« Reply #44 on: June 08, 2009, 02:31:25 PM »
I think generally we all know if for example when clipping toslab we would use metal P clips for example and in trunking etc we still have to provide clips.

When installing on metal baskets you're going to get the support from the basket, so one would assume metal tie wrap every metre in this case.

When we should look at the manufacturers recommendations would be if installing on the side or underneath of metal baskets which is quite often the case.  Where the majority of installs I see they would have metal every 1m with plastic at intervals.  This would be the time to strongly take into consideration the manufacturers recommendations in providing full metal table ties within intervals also.
** Knowledge is power, I'm still working on both **