FIRE SAFETY => Fire Alarm Systems => Topic started by: William 29 on April 11, 2014, 04:25:28 PM

Title: Call point testing in flats
Post by: William 29 on April 11, 2014, 04:25:28 PM
Quick question for some opinions:

Housing provider has large numbers of flats and sheltered schemes, they are sending someone out to them all every week to test the call points (as per the BS). The fire alarm contractor does maintenance visits on all premises types 4 times per year (2 visit too many in some cases I know) but what if they tested the call points on these visits at the same time? i.e. tested all or a quarter of the call points so that over the year the same objective is achieved. It cost around £50k a year for them to test the call points weekly internally.

I cant see an issue?

Thanks
Title: Re: Call point testing in flats
Post by: Tom Sutton on April 11, 2014, 06:27:40 PM
I understand the purpose of the weekly test is to ensure the system will work if called upon, that's why it is weekly and not principally to test the MCP, however that is also achieved over a period of time. 
Title: Re: Call point testing in flats
Post by: AnthonyB on April 11, 2014, 08:02:28 PM
3 months with a system potentially not able to receive a signal from a device and activate all the sounders is a long time in sleeping risk....

Make the saving (or some of it) by knocking the service visits down to 2 if appropriate for the system.

Do they not have to do weekly inspections of the communal parts anyway? If so they should simply move the testing in house and train their own staff to do it
Title: Re: Call point testing in flats
Post by: William 29 on April 12, 2014, 10:48:14 AM
The in house staff already test the call points weekly, that's the issue. My understanding was the main purpose of the test was to check that the MCP operates and the alarm is audible? However you wouldn't be able to check this in the flat on every occasion. They would make attempts to do this when the contractor visits 4 times a year.

I know this goes against the BS but given we are talking 100's of blocks, weekly testing would seem an unnecessary burden? The systems are being maintained (Article 17) effectively, and in many cases over what the BS requires, any faults are logged and actioned. I would argue that is reasonable compensation?
Title: Re: Call point testing in flats
Post by: William 29 on April 12, 2014, 11:09:03 AM
Could the RP fully comply with this anyway in the case of flats?


44.2 Recommendations for weekly testing by the user

When testing the fire detection and fire alarm system, there may be a need to isolate ancillary outputs.

The following recommendations apply.
a) Every week, a manual call point should be operated during normal working hours. It should be confirmed that the control equipment is capable of processing a fire alarm signal and providing an output to fire alarm sounders, and to ensure that the fire alarm signal is correctly received at any alarm receiving centre to which fire alarm signals are transmitted. It is not necessary to confirm that all fire alarm sounder circuits operate correctly at the time of this test.

b) The weekly test should be carried out at approximately the same time each week; occupants should then be instructed that they should report any instance of poor audibility of the fire alarm signal. In systems with staged alarms incorporating an “Alert” and an “Evacuate” signal, the two signals should be operated, where practicable, sequentially in the order they would occur at the time of a fire (i.e. “Alert” and then “Evacuate”).

c) In premises in which some employees only work during hours other than that at which the fire detection and fire alarm system is normally tested, an additional test(s) should be carried out at least once a month to ensure familiarity of these employees with the fire alarm signal(s).

d) A different manual call point should be used at the time of every weekly test, so that all manual call points in the building are tested in rotation over a prolonged period. There is no maximum limit for this period (e.g. in a system with 150 manual call points, the user will test each manual call point every 150 weeks). The result of the weekly test and the identity of the manual call point used should be recorded in the system logbook [see 40.2d)].



Title: Re: Call point testing in flats
Post by: colin todd on April 13, 2014, 05:59:07 PM
Wullie, the weekly test is there simply to check that the system hasnt fallen over and died. It is not to check audibility or that the MCP has not failed. Any such things are just a bonus. Here's the plan, Bill, member of staff puts system in one man test, member of staff puts key in call point......DING A LING A LING....member of staff takes key out of call point.... total silence apart from the sound of wrinklies chomping on their tea and buns.  Job done.
Title: Re: Call point testing in flats
Post by: William 29 on April 13, 2014, 08:00:15 PM
So would you have an issue with doing the test monthly or quarterly then in flats or sheltered schemes where there are large numbers of premises if its just really to check if the system is alive?
Title: Re: Call point testing in flats
Post by: nearlythere on April 13, 2014, 10:09:13 PM
So would you have an issue with doing the test monthly or quarterly then in flats or sheltered schemes where there are large numbers of premises if its just really to check if the system is alive?
You are going against a CoP William. But you can do the users checks when you like. It will be open to the court to determine if the frequency other than as recommended was adequate or not.
Title: Re: Call point testing in flats
Post by: colin todd on April 14, 2014, 12:10:27 AM
I would stick to weekly Wills. Just like Nearly o' Nough says.
Title: Re: Call point testing in flats
Post by: Clevelandfire 3 on April 14, 2014, 11:08:43 AM
Should you not be checking the panel daily? ok not activ8ting a call point, but depending on size of block you should have a panel to tell you if the system is healthy.
Title: Re: Call point testing in flats
Post by: kurnal on April 14, 2014, 06:35:44 PM
Are all these systems needed? If installed in ADB compliant blocks of flats and not a requirement it would be more cost effective to remove them than to keep testing and maintaining them in perpetuity
Title: Re: Call point testing in flats
Post by: Dinnertime Dave on April 14, 2014, 07:06:09 PM
Needed in the sheltered schemes, but why they are in general needs flats is anyone's guess. Think we have discussed this before, more than once.
Title: Re: Call point testing in flats
Post by: nearlythere on April 14, 2014, 08:22:52 PM
Are all these systems needed? If installed in ADB compliant blocks of flats and not a requirement it would be more cost effective to remove them than to keep testing and maintaining them in perpetuity
If you ask a dodgy fire alarm installer "do I need a fire alarm system and if so what catagory would I need"?what do you expect the answer to be?
Title: Re: Call point testing in flats
Post by: Dinnertime Dave on April 14, 2014, 09:29:30 PM
Are all these systems needed? If installed in ADB compliant blocks of flats and not a requirement it would be more cost effective to remove them than to keep testing and maintaining them in perpetuity
If you ask a dodgy fire alarm installer "do I need a fire alarm system and if so what catagory would I need"?what do you expect the answer to be?

Clearly yes and L1.

But, I have been on courses at the fire service college and some inspecting officers answer to any problem is an L1 fire warning system.
Title: Re: Call point testing in flats
Post by: colin todd on April 15, 2014, 06:48:47 PM
Suppers, you have not been on a course at THE fire services college, unless you took a trip to Gullane.  You simply went on a course at A fire services college somewhere in some god -forsaken area of Glucstershire.
Title: Re: Call point testing in flats
Post by: hammer1 on June 23, 2014, 09:53:40 PM
Evening chaps,

Been a while since on this great forum to post exactly this query. Reading BS the main purpose of the weekly test is testing the circuit that links to the sounders (however not solely for this purpose to ensure ALL sounders are operational).........however in my experience I have seen the testers silence the sounders when doing the test for obvious reasons when at a residential (management/ communication/confusion issues), therefore compromises one of the aspects of doing such a test under BS.

Add the fact in regards to some residential you may only have x 1 manual break glass call point and in comparison to commercial buildings you may have 20 or even 100. Testing the one in residential, 4 times a month over the 12 month period??

BS Part 1 also states about (employees?) working out of hours that a monthly bell test should be included to ensure they are familiar with the sounders, so if we are going to stick by the book, are we going to have testes around 7pm when most folk are home in their flats as the current weekly at 10am, 70% folk are not in and at work??

If we are only doing it weekly to ensure it is alive, what about the 7 days in-between??

Also, I feel the BS Part 6 referring to Part 1 on testing/maintenance should have been looked at during the revision as the two can have very different scenarios in this regard.

Think we need to read section 44.1 on BS Part 1 as we should not miss the main purpose and goal of maintenance/testing.


Can I ask your opinions on what you would do in such sceneries if I was your client. i am talking about converted houses here pre 1991 building regulations with a communal fire alarm system, interlinked with flats which have a 'all out' policy and only x 1 break glass call point located by the main entrance door to the building.

Thank you in advance.
Title: Re: Call point testing in flats
Post by: hammer1 on June 23, 2014, 10:02:46 PM
So would you have an issue with doing the test monthly or quarterly then in flats or sheltered schemes where there are large numbers of premises if its just really to check if the system is alive?
You are going against a CoP William. But you can do the users checks when you like. It will be open to the court to determine if the frequency other than as recommended was adequate or not.

I totally understand this, however what about where you have portfolios of housing stock in the 100s which is the case in London, where sometimes a charity control such stock of normal converted buildings (usually Victorian/Edwardian) this blocks are unmanned and it is impossible to conduct a weekly check of all the stock?. Having a weekly test could cost thousands in which the charity really has not the money, however risk assessing the specifics and recommending monthly tests? would not be adequate?. For example the BS for emergency lighting recommends daily checks, are you saying the charity should employ some one to do a daily check of the housing stock ? surely anyone can see in the 'real' would not be practicable and is ever hardly done in the world of Managing Agents? Why is this not the same the weekly requirement?.
Title: Re: Call point testing in flats
Post by: AnthonyB on June 24, 2014, 08:20:24 PM
You could argue that in a sleeping risk premises where the structure & lack of escape provisions is such that full simultaneous evacuation is needed the risk to life from any defect in a fire alarm system is far greater than that in normal commercial premises and if you were to move any sites weekly tests to monthly it would be the office block, not the flats.

Of course if it's purpose built or a conversion that has had the requisite features installed and the sounders are there because it's the done thing then you could isolate the sounders (as the system is an L5 to activate the smoke management) - but if you moved the testing to monthly as it's not really an alarm you would fall foul of not following the standard practice to test your smoke vents etc weekly.

An FRA could support a variation in testing, but would you be sure it would stand up in court?
Title: Re: Call point testing in flats
Post by: hammer1 on June 25, 2014, 06:17:04 PM
You could argue that in a sleeping risk premises where the structure & lack of escape provisions is such that full simultaneous evacuation is needed the risk to life from any defect in a fire alarm system is far greater than that in normal commercial premises and if you were to move any sites weekly tests to monthly it would be the office block, not the flats.

Of course if it's purpose built or a conversion that has had the requisite features installed and the sounders are there because it's the done thing then you could isolate the sounders (as the system is an L5 to activate the smoke management) - but if you moved the testing to monthly as it's not really an alarm you would fall foul of not following the standard practice to test your smoke vents etc weekly.

An FRA could support a variation in testing, but would you be sure it would stand up in court?

I understand, but if we look into the text of the BS and the reason behind the weekly test, it states employees, it states monthly out of hours tests all of which are not applicable for residential. As I say I have seen in most cases the tester silence the sounders for residential, no point having call points if the sounders don't work?. I see that we are cherry picking parts of the BS to enforce and parts not to enforce, why is that??

Is there any case studies where its gone to court where the RP had a quarterly test inspection and a monthly call point test?? I would hope a Judge would read the detail and the reasons behind the BS and that the RP is trying to ensure to the best of their ability the required testing/maintenance is in place, surely a RP with no testing/maintenance would be going to Court first.

I thought the point of risk assessing is to move away from prescriptive and assess each site individually? If we stuck to the book on all BS and building regs the world would come to a halt surely not?.

Like I say, where unmanned I have never seen the daily checks of E/L completed, but this is in the BS? why is that acceptable? and like on another thread, I am seeing more and more 100% fire alarm testing taking place. Buildings which have had visits from fire offices at various times.

What about have a monthly test, however instead of a quarterly 25%, you have a quarterly 100% therefore increasing the maintenance regime to compensate?
Title: Re: Call point testing in flats
Post by: nearlythere on June 25, 2014, 09:13:24 PM
What we need is a national course of action say like everybody in the country carries out their weekly sound check for the full 59.9999 seconds all at the same time and cause a situation worse than fracking and blame the 5839 committee ie Dot  which will side a national petition breaking the 100K barrier for debate in the House and an end to this nonsense. On the otherhand just cover your ears.
Title: Re: Call point testing in flats
Post by: hammer1 on June 26, 2014, 06:05:20 PM
What we need is a national course of action say like everybody in the country carries out their weekly sound check for the full 59.9999 seconds all at the same time and cause a situation worse than fracking and blame the 5839 committee ie Dot  which will side a national petition breaking the 100K barrier for debate in the House and an end to this nonsense. On the otherhand just cover your ears.

No, just a bit of simple common sense would of done. But what can you say when it is fire alarm engineers, installation companies, scare tactics consultants (ensure work load does not drop) who form these committees, sort of loses the purpose and end goal of life safety, who are we to have common sense above business??......obviously a tongue n cheek look on things ;D
Title: Re: Call point testing in flats
Post by: Fishy on June 30, 2014, 01:22:05 PM
So would you have an issue with doing the test monthly or quarterly then in flats or sheltered schemes where there are large numbers of premises if its just really to check if the system is alive?
You are going against a CoP William. But you can do the users checks when you like. It will be open to the court to determine if the frequency other than as recommended was adequate or not.

I totally understand this, however what about where you have portfolios of housing stock in the 100s which is the case in London, where sometimes a charity control such stock of normal converted buildings (usually Victorian/Edwardian) this blocks are unmanned and it is impossible to conduct a weekly check of all the stock?. Having a weekly test could cost thousands in which the charity really has not the money, however risk assessing the specifics and recommending monthly tests? would not be adequate?. For example the BS for emergency lighting recommends daily checks, are you saying the charity should employ some one to do a daily check of the housing stock ? surely anyone can see in the 'real' would not be practicable and is ever hardly done in the world of Managing Agents? Why is this not the same the weekly requirement?.

The BS ENs are there essentially as a 'benchmark' of what ought to be acceptable; you don't have to follow them, but if you don't you would be best advised to argue why the alternative you choose and/or recommend offers an equivalent level of safety (risk) to that covered by the national guidance.  The test is what's "reasonably practicable".  As others have said, if you have sleeping risks in old/converted buildings (where the fire alarm provides a significant risk reduction measure) then perhaps there's an argument that the weekly test is more important than in 'typical' premises of the same type, rather than less?

Affordability or lack of funds is not an excuse - whether a charity is involved or not.  The law assumes that if you choose to undertake an activity, you have first determined you can afford to do it safely (otherwise you don't do it).  It's a bit like driving with bald tyres on your car - the excuse "I couldn't afford new tyres Officer..." won't go far.  Demonstrating you lack cash just influences the size of the fine!
Title: Re: Call point testing in flats
Post by: Dinnertime Dave on June 30, 2014, 04:36:39 PM
There is also the argument often heard - " If you don't need them in the first place there is no need to maintain them"
Title: Re: Call point testing in flats
Post by: longjohn on June 30, 2014, 05:48:34 PM
There is also the argument often heard - " If you don't need them in the first place there is no need to maintain them"

Was thinking that myself Dave, are they purpose built flats, some of them?
Title: Re: Call point testing in flats
Post by: hammer1 on July 01, 2014, 03:36:37 PM
So would you have an issue with doing the test monthly or quarterly then in flats or sheltered schemes where there are large numbers of premises if its just really to check if the system is alive?
You are going against a CoP William. But you can do the users checks when you like. It will be open to the court to determine if the frequency other than as recommended was adequate or not.

I totally understand this, however what about where you have portfolios of housing stock in the 100s which is the case in London, where sometimes a charity control such stock of normal converted buildings (usually Victorian/Edwardian) this blocks are unmanned and it is impossible to conduct a weekly check of all the stock?. Having a weekly test could cost thousands in which the charity really has not the money, however risk assessing the specifics and recommending monthly tests? would not be adequate?. For example the BS for emergency lighting recommends daily checks, are you saying the charity should employ some one to do a daily check of the housing stock ? surely anyone can see in the 'real' would not be practicable and is ever hardly done in the world of Managing Agents? Why is this not the same the weekly requirement?.

The BS ENs are there essentially as a 'benchmark' of what ought to be acceptable; you don't have to follow them, but if you don't you would be best advised to argue why the alternative you choose and/or recommend offers an equivalent level of safety (risk) to that covered by the national guidance.  The test is what's "reasonably practicable".  As others have said, if you have sleeping risks in old/converted buildings (where the fire alarm provides a significant risk reduction measure) then perhaps there's an argument that the weekly test is more important than in 'typical' premises of the same type, rather than less?

Affordability or lack of funds is not an excuse - whether a charity is involved or not.  The law assumes that if you choose to undertake an activity, you have first determined you can afford to do it safely (otherwise you don't do it).  It's a bit like driving with bald tyres on your car - the excuse "I couldn't afford new tyres Officer..." won't go far.  Demonstrating you lack cash just influences the size of the fine!

All converted (Victorian/Edwardian buildings), we have had to prioritise as 50% had no AFD system at all, so you can imagine the costs involved in just that so that has taken precedence, and also having quarterly maintenance  (25%) tests regime set up.

That is it, what is deemed as reasonably practicable, I am just looking into the text of why we have weekly tests in the BS document and it just does not link into residential. Surely seeing the amount spent installing and setting up maintenance to a good stating point in a Court Of Law if the RP is acting reasonable practicable?. I think there is more argument/justification extending the weekly tests than not.

I am aware there are very experienced assessors on here and I have dealt with many Charities, housing associations across UK and to be honest only a very small percentage in these types of buildings with similar AFD systems have gone down the weekly route, so I wonder have many have come across this issue in their work??

As I say, BS5266 state daily checks, in all my years have never seen this applied to unmanned sites.
Title: Re: Call point testing in flats
Post by: colin todd on July 02, 2014, 09:57:22 PM
Daily checks were dropped from BS 5266-1 years ago.
Title: Re: Call point testing in flats
Post by: kurnal on July 03, 2014, 12:38:29 AM
Nobody will tell you directly what you want to hear Hammer1. it doesn't work like that. none of us can see all the circumstances of the case .

If I were you I would make a bullet point summary in the form of a SWOT analysis or a GAP analysis, make my decision and be prepared to fight my corner on the basis of my decision, backed up by the notes held on file. You won't go wrong if you know and understand what  the COP says and why, then make a decent case for varying from that standard and doing all that you see as being reasonably practicable. The bs is guidance after all.
Title: Re: Call point testing in flats
Post by: hammer1 on July 03, 2014, 11:09:33 AM
Daily checks were dropped from BS 5266-1 years ago.

Thank God for that, next you be saying 6 monthly have been dropped??.....only jesting there. Shame no one has told the contractors :)
Title: Re: Call point testing in flats
Post by: hammer1 on July 03, 2014, 11:10:35 AM
Nobody will tell you directly what you want to hear Hammer1. it doesn't work like that. none of us can see all the circumstances of the case .

If I were you I would make a bullet point summary in the form of a SWOT analysis or a GAP analysis, make my decision and be prepared to fight my corner on the basis of my decision, backed up by the notes held on file. You won't go wrong if you know and understand what  the COP says and why, then make a decent case for varying from that standard and doing all that you see as being reasonably practicable. The bs is guidance after all.

Thanks for your feedback, was just raising the debate and playing devils advocate.

Cheers
Title: Re: Call point testing in flats
Post by: Fishy on July 03, 2014, 11:38:10 AM
There is also the argument often heard - " If you don't need them in the first place there is no need to maintain them"

The old "Reverse ALARP" argument... http://www.hse.gov.uk/research/rrpdf/rr151.pdf
Title: Re: Call point testing in flats
Post by: kurnal on July 03, 2014, 11:46:01 AM
The counter to the reverse alarp argument can be,  in many cases,  "if I built this today what would the current design benchmarks say I need to install to create an acceptable level of safety"?
Title: Re: Call point testing in flats
Post by: hammer1 on November 17, 2014, 09:23:14 AM
Daily checks were dropped from BS 5266-1 years ago.

Are they still not in BS5266 Part 8? in regards to a visual inspection?.
Title: Re: Call point testing in flats
Post by: TFEM on November 20, 2014, 10:29:36 AM
Gentlemen, the following is taken from Williams third post on this topic.

44.2 Recommendations for weekly testing by the user

When testing the fire detection and fire alarm system, there may be a need to isolate ancillary outputs.

The following recommendations apply.
a) Every week, a manual call point should be operated during normal working hours. It should be confirmed that the control equipment is capable of processing a fire alarm signal and providing an output to fire alarm sounders, and to ensure that the fire alarm signal is correctly received at any alarm receiving centre to which fire alarm signals are transmitted. It is not necessary to confirm that all fire alarm sounder circuits operate correctly at the time of this test.


Could somebody please explain what this last sentence actually means to somebody that doesn't do alarms but is involved on the periphery of a dispute over whether the sounders can be turned off during a call point test. We've already established that it isn't purely a test of the little red box on the wall.

Thanks.

John
Title: Re: Call point testing in flats
Post by: Graeme on November 20, 2014, 10:56:47 AM
basically that means if you test the break glass unit -then you should hear the sounders going and if connected to a remote monitoring centre, they have received the fire signal.

you are not expected to run round the building and confirm that all the sounders are working.

and test the system through the day.
Title: Re: Call point testing in flats
Post by: AnthonyB on November 20, 2014, 09:09:21 PM
The live sounder testing element of the weekly test rises in importance where site make their service firms do silent service visits - if you didn't check the sounders weekly they would never get tested in many buildings.
Title: Re: Call point testing in flats
Post by: TFEM on November 21, 2014, 08:02:19 AM
Thanks......so would I be right in saying that the sounders in the circuit/zone that the tested call point is on should be audible thereby confirming that the alarm system is operating correctly?

Sounders in other zones can be silenced for the duration of that specific call point test?

John
Title: Re: Call point testing in flats
Post by: Mike Buckley on November 21, 2014, 09:29:33 AM
No, all the sounders should sound to show that the entire system is working correctly.

The usual practice is to test the fire alarm at a set day and time every week. Hopefully if the alarm does not sound in another area of the building someone will come up to you and ask you why the fire alarm test didn't happen, which would indicate a fault. The purpose of using a different call point each test is to check that every zone is working on a rotating basis.

Generally fire alarm systems are very robust and do not go wrong that often so this procedure is adequate.

Obviously if there is a zoned fire evacuation system in place and the fire alarm will only go off in certain areas, each zone of the evacuation system needs to be teste4d weekly.
Title: Re: Call point testing in flats
Post by: kurnal on November 21, 2014, 01:11:24 PM
The other purpose of the weekly test is to demonstrate the sound of the alarm to the staff. Silent mode is not quite so effective in this regard. ;)
Title: Re: Call point testing in flats
Post by: colin todd on November 22, 2014, 06:53:48 PM

Quote
Daily checks were dropped from BS 5266-1 years ago.
Are they still not in BS5266 Part 8? in regards to a visual inspection?.
Quote


No Hammy, they are not. Only a check of the visual indicator on a CB PSU, which are far from common.

TFEM, All that is necessary is to operate a single call point, and check that the CIE is not dead by hearing alarms sounding.  As someone said, you hope that people will tell you if the alarm is not adequately audible in their area.

 
 
 
Title: Re: Call point testing in flats
Post by: TFEM on November 30, 2014, 07:06:50 PM
Thanks for your help gentlemen.

The guy that was annoyed by a tinkling bell once a week has instructed the responsible person to carry on as before following advice from their fire risk assessor, fire alarm company,  your comments on the forum, uncle Tom Cobbly and the realisation that he can't win.

John