Author Topic: Smoke Detector Spacing  (Read 26530 times)

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Smoke Detector Spacing
« Reply #15 on: August 07, 2006, 12:32:45 PM »
Just to add a bit of spice to the mixture, bear in mind that, although LPCB does do the standards testing etc., some insurance companies, FM Global for example, want to apply their own standards which are more stringent than LPCB.

Fun, fun fun!
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Chris Houston

  • Guest
Smoke Detector Spacing
« Reply #16 on: August 07, 2006, 03:29:03 PM »
Yes, they might, but I suspect most UK insurers would accept the former.  It's probably only at the high risk end of the market where this would be an issue.

Offline mahzad_sha

  • Newbie
  • *
  • Posts: 2
Smoke Detector Spacing
« Reply #17 on: April 23, 2007, 11:02:31 AM »
Can anyone give me some guidance about what is the relation of smoke dedetector spacing and celling height?is there any table for that?

Chris Houston

  • Guest
Smoke Detector Spacing
« Reply #18 on: April 23, 2007, 11:15:09 AM »
Quote from: mahzad_sha
Can anyone give me some guidance about what is the relation of smoke dedetector spacing and celling height?is there any table for that?
That's not really how it works.  British Standard 5839, Part 1, 2002 contains all the recommendations.

The general idea is that the approved smoke detectors should be considered effective to cover a circular area with a radius of 7.5m. It is easier to relate this to a 10m x 10m grid.  The height at which they are effective is a separate matter, not connected to the radius.

Offline Gel

  • Full Member
  • ***
  • Posts: 101
Smoke Detector Spacing
« Reply #19 on: April 24, 2007, 10:31:29 AM »
I have posted some NFPA data on issue at:

http://www.kiddefyrnetics.co.uk/utcfs/ws-405/Assets/NFPA%20Smoke%20alarm%20spacing.pdf

May add to debate.

Offline mahzad_sha

  • Newbie
  • *
  • Posts: 2
Smoke Detector Spacing
« Reply #20 on: April 24, 2007, 01:07:17 PM »
MAY I ASK MY QUESTION IN A DIFFERENT WAY?
I MEANT WHEN WE HAVE 2 ROOMS ONE WITH THE HEIGHT OF 2 m , THE OTHER WITH THE HEIGHT OF 8 m & BOTH ARE 50 m2 ,DO WE HAVE TO USE 1 SMOKE DETECTOR FOR EACH ROOM?
THANKS FOR YOUR HELP

Chris Houston

  • Guest
Smoke Detector Spacing
« Reply #21 on: April 24, 2007, 01:28:16 PM »
Assuming detection is necessary, assuming the rooms are approximatly as long as they are wide, assuming the detectors are EN54, then yes.

Offline philex

  • Newbie
  • *
  • Posts: 1
Smoke Detector Spacing
« Reply #22 on: June 12, 2007, 08:00:40 PM »
what is the spacing between smoke detectors???
what is the spacing between water sprinkles???

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Smoke Detector Spacing
« Reply #23 on: June 12, 2007, 09:13:37 PM »
smoke detector spacing depends on the shape of the space the detectors are to be installed in- a 7.5m radius of operation is normal but there are variations depending on whether its a  room or corridor and the shape of any ceiling if not flat, and any beams or obstructions..

Sprinkler spacing depends on a number of factors in the same way - there are ceiling sprinklers and in rack sprinklers, and the spacing is normally about 3m for ceiling sprinklers but again they  may be closer if there are obstructions. In rack sprinklers tend to be closer spaced horizontally and vertically.

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Smoke Detector Spacing
« Reply #24 on: June 13, 2007, 12:10:06 AM »
Basic rule of thumb for your standard room is that a detector will cover 10 square metres (10 by 10).As kurnal has stated though it can increase due to pitch of roofs etc.

Offline Thebeardedyorkshireman

  • Jr. Member
  • **
  • Posts: 96
Smoke Detector Spacing
« Reply #25 on: June 13, 2007, 04:55:52 PM »
Is that not 100 SqM?

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Smoke Detector Spacing
« Reply #26 on: June 14, 2007, 08:52:36 AM »
Quote from: Buzzard905
Basic rule of thumb for your standard room is that a detector will cover 10 square metres (10 by 10).As kurnal has stated though it can increase due to pitch of roofs etc.
The 'rule of thumb' is really just for a quick estimation of how many 'point' detectors an open area may require. You divide the area (in square metres) by 100 for smoke detectors and 50 for heat detectors. Precise detector location by using all the recommendations in BS would then be necessary to ensure correct coverage.

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Smoke Detector Spacing
« Reply #27 on: June 14, 2007, 08:47:44 PM »
Quote from: Thebeardedyorkshireman
Is that not 100 SqM?
Stands in corner with pointy hat on!

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Smoke Detector Spacing
« Reply #28 on: June 14, 2007, 08:49:26 PM »
Quote from: Wiz
Quote from: Buzzard905
Basic rule of thumb for your standard room is that a detector will cover 10 square metres (10 by 10).As kurnal has stated though it can increase due to pitch of roofs etc.
The 'rule of thumb' is really just for a quick estimation of how many 'point' detectors an open area may require. You divide the area (in square metres) by 100 for smoke detectors and 50 for heat detectors. Precise detector location by using all the recommendations in BS would then be necessary to ensure correct coverage.
110% in agreement - just so happens that I was specifying for a nice 78m by 35m open area where beams are not an option!