I am pretty certain your premises almost met the old prescriptive code, to be certain I would need to know the floor area, also a fire certificate was issued. In these days of risk assessment and flexibility I am very suprised if it does not continue the meet the standards of the current guides. I have included below the relevant Paragraph from the old guide, sorry its so long winded.
STAGE 3 — Travel within stairways and to final exits Number of stairways
Building with a single stairway
13.34. It will normally be necessary for a building to be provided with two or more stairways, but a single stairway of suitable capacity for the number of persons using the route may be considered satisfactory in the following circumstances:-
(a) the floor area of any upper floor of the building does not exceed 200m2, and distances of travel conform to those given in Table D of paragraph 13.7.
(b) the building has no more than 4 floors, or no upper floor is at a height of more than 11 metres;
(c) the stairway conforms with one of the arrangements described in paragraph 13.35; and
(d) in a building more than 2 floors in height access to the stairway from any room (other than a toilet containing no fire risk) is through two sets of fire doors. Exceptionally, where it is impracticable to achieve this, in premises of not more than 3 floors in height, access to the stairway from any room may be from a single fire door, subject to an automatic fire detection system being installed to the type L1 system in accordance with British Standard 5839: Part 1.
Para 13.7. Table D is the travel distances for escape in on direction only.
Para 13.35 lays down the conditions for the final exit.
I think wb has hit the nail on the head.