memnon:
Anyone had any dealings with this companies extinguishers that appear to be one extinguisher for all fires?
Cant see any BS but they do claim EN3-7: 2004  +A1:2007.

AnthonyB:
They aren't kitemarked (but they are supposed to be in the process of getting a KM license for the 2,6 & 9l) but:
- The A, B, F & 35kV (electrical) ratings are independently verified by a French EN3 test lab
- The lithium battery claim is based on independent tests by the Swedish state laboratories
- The Class C claim is manufacturer only based on testing using the Australia/New Zealand test fire as EN3 doesn't have a test for Class C and assumes all powder extinguishers are suitable (but only powder. Note historically in the pre EN3 days it was not unknown for foam spray, CO2 & Halon extinguishers to be marked for Class C fires and some guidance supported it)
- The class D claim is manufacturer only and apparently based on the old German DIN standard magnesium test fire

It all depends on what risks you are considering it for - for many applications you can be assured of its efficacy, others you have to take it on trust with the manufacturer or do further research testing. I've accepted it for some applications, it's certainly better than powder for some traditional 'multi purpose' uses.

If you wonder what's in it - it's a bit like a liquid version of a powder extinguisher, having the same Ammonium salts as ABC powder extinguishers and possibly synthetic based foam (based on the patent and MSDS)

memnon:
Many thanks.
Id just had some office based clients asking if they can replace their 13A foam and 2 KG CO2 extinguishers with single multi use ones to cover general office type risks.
Look as if they should be ok although I do wonder if they will save anything by doing it as they are not that cheap.
How do you sort out numbers/sizes as none seem to show their fire ratings?

AnthonyB:
They all show fire ratings, but for reference:

2 litre - 13A:34B:25F
6 litre - 34A:113B:75F
9 litre - 55A:183B:75F

As most fire points are placed based on the old 13A/200 sq.m. rule of thumb despite increasing numbers of 6l foam being 21A this means you only need to use the 2l Firexo for a typical A/E fire point - on sites that have gone down this route the majority of replacements have been 2l, I've only used the 6l a couple of times, one where the 75F was needed and the other where it replaced 4 existing units at a single point and the 34A suited the actual floor area.

Shop around as retail costs vary - internet sites are, as usual, often at the cheaper end. Less overall extinguishers also results on basic servicing costs as well.

memnon:
Thanks Anthony