Hi all, wonder if you could help.
A 3 storey residential property is split into two blocks, one containing 4 units and the other 9 units. In the larger block, with 3 units per floor, there is a protected staircase. In the smaller block, there are 2 flats on the 1st and 2nd storey only but no staircase protection is provided; the ground floor is purely for access. The property was built in 1995 as far as i can find. Any ideas why this might be, is a protected stair not required if only 2 units per floor and if so, where can i find information on this?
Thanks
-
See the footnote to paragraph 2.19 on page 26 of ADB B1 2006.
You need to quote the 2001 version, I believe the content is the same but IIR the numbers might be different.
-
See also pages 88 and 89 of the purpose built flats guide issued last August, it provides the ADB benchmark and relaxations for small single stair blocks.
-