Author Topic: Faulty mains failure generator.  (Read 9336 times)

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Faulty mains failure generator.
« on: September 15, 2014, 11:08:12 PM »
The emergency lighting has failed due to faulty mains failure generator. The installation is 20 plus years old but functional. Can you replace the generator with new without up dating the whole system?
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Faulty mains failure generator.
« Reply #1 on: September 15, 2014, 11:24:45 PM »
The usual answer Tom, fire risk assessment! What is the building used for, by whom and when, what is the coverage of the old system, is it sustained, maintained or non maintained, if the latter is it sensitive to sub circuit failure, are the levels of illumination adequate, are points of emphasis adequately covered , will the run up time be acceptable etc.
« Last Edit: September 16, 2014, 12:10:59 AM by kurnal »

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Faulty mains failure generator.
« Reply #2 on: September 16, 2014, 06:35:55 AM »
Sounds more like standby lighting than emergency lighting Tom.
We're not Brazil we're Northern Ireland.

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Faulty mains failure generator.
« Reply #3 on: September 16, 2014, 09:47:25 AM »
Thanks guys and I have got back to him to establish if it is standby lighting or emergency escape lighting or both.

If you check the BS 5266-1:1999 it accepts batteries and generators for emergency escape lighting but in the 2005/2011 versions they do not mention it, only certain aspects like servicing for instance. Therefore are generators acceptable for emergency escape lighting or should it be only used for standby lighting? Also if they were installed years ago can you say they are not now acceptable for emergency escape lighting?
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Faulty mains failure generator.
« Reply #4 on: September 16, 2014, 03:22:25 PM »
Thanks guys and I have got back to him to establish if it is standby lighting or emergency escape lighting or both.

If you check the BS 5266-1:1999 it accepts batteries and generators for emergency escape lighting but in the 2005/2011 versions they do not mention it, only certain aspects like servicing for instance. Therefore are generators acceptable for emergency escape lighting or should it be only used for standby lighting? Also if they were installed years ago can you say they are not now acceptable for emergency escape lighting?
Not very many generators installed which will provide sub circuit failure back up which is what you need for EL.
The existence of an emergency generator may allow standby lighting to be used, but it is not necessarily adequate for escape lighting.  The generator will only start on total power failure.  This is not the most likely result of fire, which is more likely to affect only a limited number of circuits.  Unless the generator supplies dedicated luminaires that are wired in fire resisting cable, it is unlikely to be adequate for the provision of escape lighting.
We're not Brazil we're Northern Ireland.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2477
    • http://www.firewizard.co.uk
Re: Faulty mains failure generator.
« Reply #5 on: September 16, 2014, 08:19:22 PM »
Not withstanding the extensive costs of correctly servicing & maintaining the generator (on top of the lighting testing) reasons at some sites I've been to are that:
a) local failure doesn't kick in the generator
b) changeover times are too slow, not meeting BS5266 requirements

Most sites have phased in self contained fittings and where generators are retained it's usually for non statutory standby/business continuity purposes on top of the 3 hour internal batteries in EL fittings.

A new generator will cost a fortune, especially with the logistics of removing the old one and installing the new (as many aren't in the best locations for access) and personally I'd rather focus the capital spend on self contained fittings/conversion kits.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Faulty mains failure generator.
« Reply #6 on: September 20, 2014, 04:23:53 PM »
Almost here, that almost sounded like a quotation in your posting?
Colin Todd, C S Todd & Associates

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Faulty mains failure generator.
« Reply #7 on: September 20, 2014, 11:39:38 PM »
Almost here, that almost sounded like a quotation in your posting?
It was almost Dot. Why have a dog and bark yourself?
We're not Brazil we're Northern Ireland.