Thank you in sharing your opinions regarding this subject. So because there is no direct BS or other guidance document stating or recommending that ancillary equipment interfaced to the fire alarm system must be tested and recorded over a set period. Then unless life safety is at significant risk, would I be right to say its what value you put on the building & its assist or weather your business could withstand interruption to normal business from a fire incident.
I dont think that is the conclusion drawn as a result of this thread. Rather the requirement for testing is within other BS documents than BS5839.
Consider the range of typical interfaces to fire alarm systems.
Heating systems
Ventilation systems- including fire vents for property protection and air conditioning
Sprinkler systems
Gas mains
electronic door locks
magnetic hold open devices on fire doors
auto diallers
Fixed installations- inergen et al
Mutes to the PA systems in shops and places of entertainment
Paging systems for deaf people
Paging systems for fire wardens
Lift installations
fire shutters for compartmentation
fire shutters for life safety
Fire curtains
It would be a brave engineer who made the decision as to which of these were provided for property protection alone. And dont overlook the nature of faults that can arise- the hardware may be fine but the configuration data for the panel cause and effect, or on larger systems the network cofiguration may be corrupted.
All interfaces must be tested. Having seen so many failures especially on modern state of the art analogue addressable and networked systems, it would be gross negligence not to do so in my opinion.