lyledunn:
What is the difference between ?escape route? and ?means of escape?

Crusher:
From my perspective/understanding, 'means of escape' includes everything required to leave the premises from your location at the time of alarm/discovery, until you are at a safe place outside of the building i.e. at the bus stop.

This would include rooms, corridors, spaces, protected routes, fire exits, external stairs, evac lifts, ramps, hoists etc. It would also extend to locks on gates in enclosed yards!

lyledunn:
It might seem a bit of a daft question that I am posing but I am trying to understand a requirement in BS7671 which impacts on some crucial aspects of electrical installation work
So, would you consider a protected corridor in a hotel, for example, to be a protected escape route?

wee brian:
In an open plan office the whole floor is an escape route - doesn't really make sense but that's codes for you

lyledunn:
My question had its roots in an ambiguous requirement for protected escape routes in BS7671A2 2022. However, a corrigendum was released by IET just this month to clarify the situation. All now reasonably clear.