FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Fire Safety => Topic started by: stewbow on September 20, 2006, 04:39:16 PM

Title: Adding to an existing system
Post by: stewbow on September 20, 2006, 04:39:16 PM
Sorry if I am over-using any maximum new topic rules!!!

I did post this message on another site a while ago, but that site mainly dealt with security systems, though it did yeald some very good replies.

Thought I'd see what you guys make of it.

My question is:-

In a type of property such as a Guest House or Hotel that already has a Fire Alarm System installed ( to the 1971 Fire Precautions standard with a Fire Certificate ). Normally you have a situation where heat detectors are sited in the ground floor kitchen, lounge and dining room, and the odd smoke detector is fitted on the landings. Sounders are usually on alternate landings.
Under the new Regulatory Reform Order, Fire Certificates go out of the window, and a decent Fire Risk Assessment will reccommend an L2 System.
So! I would much preffer to do a complete new installation, but it could also be possible to add say 4 smoke detectors and 4 sounders on each floor to the existing cableing ( covering all of the bedrooms ) but this would mean adding FIre Rated 1.5mm cable on to 1mm twin and earth.

If it was a couple of detectors and sounders, I would normally add on and issue a modification certificate, but how far can you go with adding on, and could you then call it an L2 system?


Greatfull for any help and advice

Stuart
Title: Adding to an existing system
Post by: Wiz on September 20, 2006, 06:05:11 PM
From my understanding of BS5839 part 1 2002 you are allowed to add to an existing non-compliant system. Obviously the additional equipment, installation materials and work must be to latest recommendations of the Standard.

Colin Todd in his book explaining BS5839 Part 1 2002 suggests that the 'cut-off point' would probably be where the new works would double the size of the existing non-complianrt system. After this cut-off point a complete new compliant system should instead be installed.

To get to a L2 system you must have first complied with the recommendations of both L4 & L3 systems. An L2 system is basically L3 system with additional automatic fire detectors. An explanation should be provided of where and why these additional AFD have been included in the system design information.

A system that doesn't meet the criteria of a L1, L3 or L4 system may be described as an L5 system, but again a full explanation of the fire engineering principles used in deciding that a L5 system has been decided upon, must be included in the system design information. My advice is never design a L5 system unless you have a university degree in fire engineering!

I'm sure that if I have got any of the above wrong, there will be many later replies 'correcting' me because there are a lot of very 'able' people who post on this site, and I always learn so much from their advice!

I'm sure you will also be advised to have a full fire risk assessment carried out before you decide to carry out any modifications and ensure that all relevant parties i.e the building owner, the building insurer, the building user, the local authority and fire service are all happy with the findings of the risk assessment and the system category that the finished system will comply to.
Title: Adding to an existing system
Post by: kurnal on September 20, 2006, 06:31:29 PM
As a fire risk assessor do I need to be at all concerned if I encounter an older system, say to L1 coverage, in which the sounder circuits are in fire rated cable but the detectors and call points are wired in pvc twin and earth? I always thought  that the EOL resistor would give open or short circuit fault monitoring and that was ok for the 1988 standard?
I usually comment that the system is not up to current standards but whilst it remains serviceable there is no justification to make changes. Whats the view of the engineers?
Title: Adding to an existing system
Post by: stewbow on September 20, 2006, 06:50:39 PM
The new HMG guide re Sleeping Accommodation (and all the FO's that I have spoken to) says that in a Hotel / Guest House situation an L2 System is required. The difference being the requirements of detectors in rooms where people sleep that open onto escape routes (bedrooms) and the need for 75dB at the bedheads.

I don't see an argument for you not to recommend a new system!
Title: Adding to an existing system
Post by: Graeme on September 20, 2006, 07:27:00 PM
Quote from: kurnal
As a fire risk assessor do I need to be at all concerned if I encounter an older system, say to L1 coverage, in which the sounder circuits are in fire rated cable but the detectors and call points are wired in pvc twin and earth? I always thought  that the EOL resistor would give open or short circuit fault monitoring and that was ok for the 1988 standard?
I usually comment that the system is not up to current standards but whilst it remains serviceable there is no justification to make changes. Whats the view of the engineers?
If the system is in good working order then you can't realistically expect the owner will rip it out and install a new one.
If the system was asked to be made to an L2 with say a couple of detectors and sounders in rooms in a small Hotel,
then run this by the FO or whoever is asking and do new works to 2002 standards with modification cert.
If the work was major then i would recommend a new system but the owner will likely get another opinion and go with what he wants(little as possible cost) so you may loose out to some other company who will just add on.

If however the system is asked to be fully compliant to 2002 then it would have to be a re-wire.

Wiz-spot on. L2=same as L3 but added AFD in areas of a fire risk.
Title: Adding to an existing system
Post by: stewbow on September 20, 2006, 08:16:14 PM
It's only early days, but I've noticed straight away that the attitude here in this forum is that the system probably could be ok or added to, whereas on the other forum, which is mainly frequented by installation engineers, it was 99% a new system or don't touch it with a barge pole!

very interesting
Title: Adding to an existing system
Post by: kurnal on September 21, 2006, 07:03:40 AM
Steve you have hit the nail on the head. On this forum I think you will get a more rounded view.
The duty of care of  the responsible person under the fire safety order is as far as is reasonably practicable.

Of course if you ask a specialists advice you will get a specialists answer. The answer will be technically perfect but where does that fit into the term reasonably practicable? Case law says that cost can be taken into account to some extent- for example if the cost of the improvement will make the business non- viable then a long term plan or bankruptcy may be the only options.

In your hotel, its very likely that fiire doors, emergency lighting, fire extinguishers, panic hardware,  signs and notices, the external fire escapes also do not comply with current standards- because all these standards have changed in the last few years.  Ask a specialist in any area and they will give their best advice in that area. But there will be a need to put all of these issues into the bigger picture and decide a prority list and a long term plan.

For me in your hotel there may be two options- full system replacement or patch up. The cost/ benefit in the short term may point towards a patch up. We get instant improvement to the exisiting level of safety as quickly and easily as possible. It might even be that you wire a new loop in firetuff or something and put the new and existing detectors in that area  on that. But we give the owner an advisory that the system does not comply, an overview of its maintainability in the long term and let him decide.

Heres another analogy. I take my car in to the garage for a misfire and they recommend a new fuel injection system. But If I spent all that money I would be peeved if it then turned out that the chassis is rotten and the brakes are shot.  If I take the car in for an MOT they will give me a general safety check covering all areas that helps me to decide how to best spend my money.

Your other forum is the engine tuner, this one the MOT bay.
Title: Adding to an existing system
Post by: Wiz on September 21, 2006, 09:40:00 AM
Quote from: kurnal
As a fire risk assessor do I need to be at all concerned if I encounter an older system, say to L1 coverage, in which the sounder circuits are in fire rated cable but the detectors and call points are wired in pvc twin and earth? I always thought  that the EOL resistor would give open or short circuit fault monitoring and that was ok for the 1988 standard?
I usually comment that the system is not up to current standards but whilst it remains serviceable there is no justification to make changes. Whats the view of the engineers?
When the standard was such that a 'short' on detection wiring gave a fire condition at the control panel rather than a fault condition, and that the use of non-fire resistant cables was also permissable, I often wonderd if there could ever be the situation that heat from a fire might be enough to melt the insulation of the cable, and then possibly the conductors would short together and give a fire condition at the panel! I almost belived this might have been a 'system design' feature so I was quite surprised when the 'short to fault' became the standard whilst non-fire resistant cables were still allowed. I thought this change lost the potential for having a sort of automatic linear fire detection system at no extra cost!!!!!!! :)
Title: Adding to an existing system
Post by: Wiz on September 21, 2006, 10:49:10 PM
Stewbow, further to earlier replies, I've been giving this query a bit more thought.

I have always found that when you 'condemn' something as not being up to latest standards, the customer often starts seeing you in a negative light because you have brought the 'bad news'. That's why we often have to defend ourselves with the 'don't shoot the messanger ' line.

This negativity may also lead to the customer distrusting you and then you losing any chance of doing work for them now, or in the future. If you can show that you understand the customer's problems and show that you are trying to work out the best solution for them, then you have more chance of maintaining their trust.

I have always understood that new regulations are invariably not retrospective. This is understandable if you consider that a hotel owner, for exmple, could have a costly new fire alarm installation and just 6 months later a new British Standard, for example, was issued and someone could walk in and tell them that their costly new six-month old system was no longer any good because it didn't comply!

As I said previously BS5839 part 1 2002 allows you to add to an existing currently non-compliant system but this must always be weighed up against just how poor their existing system may be and, more importantly, if it really does meet the current needs for a safe system for the way they are using the building.

However, if you are convinced that you really need to encourage them that their system is seriously in need of a complete overhaul you could consider the following couple of points.

Whilst I understand that some properties had to have certain licences issued for a particular use of that property, and these licences may have requested certain minimum requirements for the licence to be issued, that this might not be the case any longer (I'm no expert in this area!), and that new requirements may all be solely based on a fire risk assessment and not a licence. It occurs to me that the insurers for the building may have minimum requirements for the insurance to be valid. This may be worth checking out because it will be no use extending a non-compliant system, if the insurance small print states something like 'the whole fire detection and alarm system must comply fully with all current recommendations of BS 5839 part 1 2002.

I'm not sure exactly how old the existing system is from your query, but it also occurs to me that the existing equipment installed might be past it's 'sell by date' anyway. Automatic detectors normally have a manufacturers recommended working life of about 10 years and eventually, even cable will deteriorate in time. The total costs of any new proposed works and any essential 'out of date' equipment replacement costs could start to get much closer to the costs of a complete new compliant system and encorage the customer to realise the latter option is the most cost-effective for them in the long run.
Title: Adding to an existing system
Post by: kurnal on September 21, 2006, 10:57:47 PM
Thats spot on Wiz. Very well put.
Title: Adding to an existing system
Post by: Wiz on September 22, 2006, 09:42:24 AM
Quote from: kurnal
Thats spot on Wiz. Very well put.
Thanks Kurnal. I only ever try to be of help to others, and it is good to think that maybe I am being of help and not a hinderance!
Title: Adding to an existing system
Post by: stewbow on September 22, 2006, 07:00:13 PM
Wiz

I have looked on a couple of occassions, but can't find in Colin Todd's book the part that you mention about extending systems, any directions please?

stuart
Title: Adding to an existing system
Post by: Wiz on September 22, 2006, 08:38:58 PM
Quote from: stewbow
Wiz

I have looked on a couple of occassions, but can't find in Colin Todd's book the part that you mention about extending systems, any directions please?

stuart
Stuart,

My copy of the book is at work, but I'll confirm the page number containing the info as soon as I can.
Title: Adding to an existing system
Post by: Wiz on September 23, 2006, 12:44:44 PM
Quote from: stewbow
Wiz

I have looked on a couple of occassions, but can't find in Colin Todd's book the part that you mention about extending systems, any directions please?

stuart
Stuart,

The reference in BS 5839 part 1 2002 can be found in the last paragraph of Section 1 general, 1 Scope.

The reference in Colin Todd's 'A guide to the BS Code' can be found from the middle area of page 23

Regards

Wiz
Title: Adding to an existing system
Post by: stewbow on September 23, 2006, 03:56:05 PM
I found the section in Colin Todd's Guide where he talks about doubling the size of a system, but the last paragraph of section 1, scope on page 1 of the BS doesn't mention anything about doubling the size of a System, where exactly does Colin draw his resources from?
or I is right in front of my nose and Im can't see it??
Title: Adding to an existing system
Post by: Wiz on September 23, 2006, 05:24:49 PM
Quote from: stewbow
I found the section in Colin Todd's Guide where he talks about doubling the size of a system, but the last paragraph of section 1, scope on page 1 of the BS doesn't mention anything about doubling the size of a System, where exactly does Colin draw his resources from?
or I is right in front of my nose and Im can't see it??
Stuart,

The BS states that you are allowed to extend a non-compliant system but gives no further guidance.

Colin Todd's guide gives an opinion as to where the cut-off point might be, but also states that there is probably 'no right or wrong answer as to the point at which a desicion should be made to install a complete new system'.

It all seems pretty clear to me.

And what is abundantly clear from the above, is that the advice you were given elsewhere, that your only option was to tell the customer that they had to have a complete new system because it did not comply with current standards is flawed.

I would assume that Mr Todd formed his opinion based on his vast experience and knowledge.

If you feel he has no right, or is not sufficiently experienced enough, to form these opinions, you will have to take that up with him. I understand that he is, or has been, a member of this forum.
Title: Adding to an existing system
Post by: Graeme on September 23, 2006, 07:05:49 PM
Major work-new system
small modifications fine but to new regs.

Insurance asks for a 2002 system=new one

what size of system are we talking about and what needs done?
Title: Adding to an existing system
Post by: stewbow on September 24, 2006, 10:16:45 AM
Quote from: Graeme Millar
Major work-new system
small modifications fine but to new regs.

Insurance asks for a 2002 system=new one

what size of system are we talking about and what needs done?
Typically, a small, mid terraced Victorian hotel / guest house with about 12 bedrooms from basement upto 2nd or 3rd floor capable of taking around 25 guests.
These places at present would have heat detection in the kitchens, dining rooms, and lounges, and smoke detection on alternate landings.
At present, the bedrooms have no detection and low sound pressure levels.

Our local FOs have been saying for tha last couple of years that the 2 things they are most concerned about bringing up to date, (when the RRO comes in) are Fire Doors and Fire Alarm Systems.

Stuart
Title: Adding to an existing system
Post by: Graeme on September 24, 2006, 11:30:32 AM
simple answer then

If the FO is asking for the system to be brought up to date that means to 2002 standards.

Clarify it with him is your best way to go.

He might of been asking for a system to comply with L2 which only may need a couple of afd but also brought up to date which to me means everything.
Title: Adding to an existing system
Post by: stewbow on September 27, 2006, 08:35:18 PM
BS 5839 Part 1:2002
46.4.2
b) Before modifying a fire alarm system, care should be taken to ensure that the proposed modifications do not detrimentally affect the compliance of the system with fire safety legislation; where doubts exist there should be consultation with the relevant enforcement authority.



In a building that has over 300 m2 in floor space and at present only has a single detection zone, if you increase, in area, the size of the detection zone (by putting smoke detectors in bedrooms), are you making the system more non-compliant?
Title: Adding to an existing system
Post by: Wiz on September 27, 2006, 10:27:26 PM
Quote from: stewbow
BS 5839 Part 1:2002
46.4.2
b) Before modifying a fire alarm system, care should be taken to ensure that the proposed modifications do not detrimentally affect the compliance of the system with fire safety legislation; where doubts exist there should be consultation with the relevant enforcement authority.



In a building that has over 300 m2 in floor space and at present only has a single detection zone, if you increase, in area, the size of the detection zone (by putting smoke detectors in bedrooms), are you making the system more non-compliant?
Stuart,
The above explanation doesn't mean you can't add to an existing non-compliant system. The reference to fire safety legislation surely doesn't imply it means the BS only, if at all, otherwise the BS would be contradicting itself!!!

Could it not be argued that the existing single zone system already covers the bedroom areas in size, if not detection coverage, and that adding detectors in the bedrooms is not actually increasing the size of the single zone?

I don't think you can ever say something is 'more non-compliant'. Something is either compliant or it isn't!

I'm not saying that your system would not benefit from upgrading. It appears you are even being asked to upgrade it. But you want to tell your customer that he has to renew his existing system and you are looking for BS 5839 part 1 2002 to confirm your views. I'm only saying that you can't tell your customer that  BS 5839 Part 1 2002 doesn't allow you to add equipment to his system just because the existing system is non-compliant. The BS clearly states that you can, and Colin Todd's book provides some guidance on the recommendation, if not a precise definition!

I hope you enjoy your in-depth reading of the BS searching for confirmation of your views. I wish I could tell you what you want to hear, but then I would be giving you mis-information.

If all our numerous opinions above have not helped at all, and you can't find what you are looking for in BS, you will be in the same boat as many of us, and I would like to invite you to join the rest of us here residing at The Home For The Slightly Bewildered!!!!