THE REGULATORY REFORM (FIRE SAFETY) ORDER 2005 => Q & A => Topic started by: CALTEX on January 16, 2007, 07:21:09 PM

Title: Fire alarm maintenance in schools during school hours.
Post by: CALTEX on January 16, 2007, 07:21:09 PM
Is there any hard and fast ruling covering routine fire alarm maintenance during school hours?
For example, if you carry out testing with sounders diabled in a bulding occupied by children, this effectively
leaves the premises without a means of evacuation. If possible I carry out a "walk test by zone" so that only
the part of the building being tested is left without protection, but this is rarely possible due to lack of zone info etc. If I disable a fire system with the building fully occupied are any H&S rule breached?
(All universities on our client list will not allow any disablements or testing during occupied hours.)
Title: Fire alarm maintenance in schools during school hours.
Post by: wee brian on January 16, 2007, 07:52:41 PM
No hard and fast rules

I doubt it makes much difference but it will depnd on the particular school. - risk assessment
Title: Fire alarm maintenance in schools during school hours.
Post by: Mike Buckley on January 17, 2007, 12:45:57 PM
The other proviso should be that all the staff have been informed and an alternative plan is available. This could just be a hand bell and an instruction for someone to phone reception to inform them of the fire.

It comes down to the reasonable practicable bit, if it is not practical to carry out the test whilst the school is unoccupied then alternative arrangements should be made.
Title: Fire alarm maintenance in schools during school hours.
Post by: wee brian on January 18, 2007, 01:16:49 PM
Lets face it - who in their right mind wants to work anywhere near teenagers - i'd want danger money
Title: Fire alarm maintenance in schools during school hours.
Post by: Andy Gwatkin on January 19, 2007, 07:58:49 PM
I look after schools and Uni,s as a Fire safety reference which covers 10 local education authorities ,not come across this issue before, as long as the premise follows the points mentioned above ,then i wouldn,t have a problem with it.I,d be grateful the fact that the system is being looked at,the end of the day you have to reasonable about the whole situation and that we cannot expect FA companies to work at weekends and at night time only
Title: Fire alarm maintenance in schools during school hours.
Post by: Chris Houston on January 20, 2007, 02:03:35 AM
Quote from: Big G
I,d be grateful the fact that the system is being looked at
What do you mean by this, it is a legal obligation that it is more than "looked at"?
Title: Fire alarm maintenance in schools during school hours.
Post by: Andy Gwatkin on January 20, 2007, 09:39:46 AM
I understand the protocol for the maintenance of FA systems fully,the comment was  a bit tongue in cheek !!  have you not come across a company that hasn,t carried out any maintenance at all on a FA system ???
Title: Fire alarm maintenance in schools during school hours.
Post by: Chris Houston on January 20, 2007, 10:00:00 AM
I still don't know what you mean.  Are you asking if I have encountered a fire alarm contractor who was paid money to maintain a system and then didn't?  Yes, I've seen this, but this doesn't mean I'll be telling people to be grateful that their contractors bother to turn up, I expect higher standards than that.
Title: Fire alarm maintenance in schools during school hours.
Post by: CALTEX on January 20, 2007, 12:13:43 PM
I think we are wandering away from the main issue here. Most school maintanance contracts that I have come across are priced for "normal working hours" but when you arrive on site nobody wants to hear sounders, so you are left with the option of abandoning the maintenance or disabling sounders during the test. Given the size and poor escape route planning in most schools that I have maintained, (not to mention the fact that fire escape passageways are commonly used for storage) I would not want my child in a building where some fire alarm engineer is wandering around in the building, a real evacuation is required, sounders are disabled and the only person who can re-enable them has to be located and returned to the panel in order for this to happen. Meanwhile fire/smoke is spreading etc...
A large University that we maintain has a fire warden system (hand held air horns & a warden/marshall on every floor) that can be put into action during any disablement. (Probably required to compensate for lower intelligence levels of students when compared to primary school kids!) so if a university has seen the need for this, presumably after risk assesment, then why do schools not do something along the same lines?
To respond to Mike Buckley, I have not come across any school that had an alternative system in palce for evacution in the event on alarm failure. What is even more worrying from a parents point of view ( I know this has been raised elsewhere in this forum) is that one local authority on our client base has about 40% of its schools on "mains only" systems, so some alternative evacuation plan should be in place anyway!
Back to my origial point, is there any legislation covering this issue?
If fire panel manufacturers have seen the need to design a "walk test by zone" feature into their systems, are the anticipating future legislation or does it already exist?
I am not personally prepared to put lives at risk so that maintenance quotas can be met.
Title: Fire alarm maintenance in schools during school hours.
Post by: Chris Houston on January 21, 2007, 12:31:15 PM
I don't think there is any legislation that covers the issue of when school fire alarm systems should be maintained.  Schools are required to comply with exactly the same legislation as everywhere else (the exceptions to this are pieces of legilation about education, tresspass, knifes etc, nothing to do with fires as far as I am aware.)
Title: Fire alarm maintenance in schools during school hours.
Post by: Ryan on January 22, 2007, 09:16:01 PM
I don't see the problem, as long as we know it is a test, its ok. At my school we have a tannoy system, and if anything is going on, they tell us. Guess not all schools have them.
Another thing I found weird at my school is that the extinguishers are all foam and CO2. Considering there isn't anything too flammable apart from paper and such, I would have thought Powder and CO2 would be a better option. Maybe its because foam can cool the fire better than Powder, but that makes no difference if no-one is in the building. We also have a 'Fire Brigade Foam Inlet' Which to me looks like a dry riser, but again, why foam?
Title: Fire alarm maintenance in schools during school hours.
Post by: kurnal on January 22, 2007, 09:39:32 PM
Dry powder is a great and versatile firefighting agent. But in a building it reduces visibility, can affect people with breathing problems and creates a lot of dust, which can ruin delicate equipment. So use it where you have to but if there is another option then use it.
All premises have to make provision for dealing with class A fires. Water is great for this because of its cooling effect. But modern foam sprays are also very effective on class A fires and can also be used on class B (flammable liquids). So foam is more versatile. Size for size, a 6 litre foam spray has the class A firefighting capacity of a 9 litre water extinguisher. So they can be smaller and lighter but pack the same punch. You can now buy a water extinguishers containing detergent like additives to the extent that a 3 litre water with additives extinguisher has the same rating as a 9 litre water without. But with only 3 litres to play with you have to be accurate and decisive in their use- cos they dont last long.  So foam spray is usually my first choice these days as a general purpose extinguisher
Title: Fire alarm maintenance in schools during school hours.
Post by: kurnal on January 22, 2007, 09:40:43 PM
The foam inlet will probably be the fire brigade to pump foam into a basement oil fired boiler house.
Title: Fire alarm maintenance in schools during school hours.
Post by: Ryan on January 22, 2007, 10:21:41 PM
Now I think of it, that about the boiler is true ;) Thanks for that about the extinguishers, I would have always used Powder as the general purpose, but Now I'll think again
Title: Fire alarm maintenance in schools during school hours.
Post by: Richard Earl on January 23, 2007, 09:33:41 PM
hi most of my schools that i service have bought into a pager system linked to the fire panel, then when the bells a disconnected the pager still workes, they also have an alarm verificaton time built in to the system. most areaddresable systems though.
Title: Fire alarm maintenance in schools during school hours.
Post by: Ark Angel on January 27, 2007, 11:00:43 AM
With the schools that I come across some ask the very question, "what happens if I have a real fire while your testing"? to combat this the school provide a body who sits in front of the panel watching it. I tell him where I'm testing and then he keeps an eye on fires coming in. Should he see a fire from another area where I'm not working he makes a desicision based on the school's procedures to investigate or sound the alarms.

I've known colleagues who have had systems disabled and then real fires have occurred. Not a nice situation to be in!
Title: Fire alarm maintenance in schools during school hours.
Post by: Ryan on January 27, 2007, 06:07:48 PM
That would be very rare though
Title: Fire alarm maintenance in schools during school hours.
Post by: Ark Angel on January 28, 2007, 10:58:40 AM
Indeed it is very rare, but nowadays who wants to take that chance? Certainly not me. I always tell the customer that the system will be disabled prior to testing and let them make their own arrangements.
Title: Fire alarm maintenance in schools during school hours.
Post by: IrishFire on February 01, 2007, 08:29:35 PM
Very rare that I get asked that question, but if you think about it it's up to the client to provide fire watch during your servicing.
Title: Fire alarm maintenance in schools during school hours.
Post by: FireFly40 on June 21, 2007, 08:37:32 PM
Wee Brians right schools are nasty places to roam around when kids are particularly with smoke pole and bgu test keys I always do them out of hours. If you must do them occupied take a panel watcher and radios. If the kids find out the fire alarms off watch for loads of smashed glasses (they used to switch the fire alarms off round here on the last day of term for same reason) Another thing to check is staff are aware of non working alarm and alternative arrangements. In about 1985 I was walking around a job smoking and poking - panel reseting with the old reset unit walked into office explained to bloke testing fire alarm etc etc He asked me stuff I told him stuff carried on (nice bloke, I thought) next thing over tannoy everybody out dangerous health and safety issue I thought the chemical place next door had had a leak so made my way to grass with 1500 other people only to have site manager tear into me in front of them all.No it was me turning off bells on FA .He didnt tell the amassed crowd that I had been doing it for years
and it was him who asked for no bells when testing.(the bloke was shop steward)
If you do have to take bells off on a live building get H&S persons signature first
A lot of maint. Companies have a disclaimer like this in their certificates.
 Always think of your own backside your company will shovel s**t onto you if it goes into the fan. I once went confidently into a bo**icking meeting with a gaffer - only
to have him say to the panel and heres the man responsible and walk out
When the chips are down youve got no friends and take no prisoners!
Title: Fire alarm maintenance in schools during school hours.
Post by: Graeme on June 22, 2007, 08:15:42 PM
i have the standard bs that alarm devices were not permitted to be tested but were tested last on-date-person-signature etc.
Title: Fire alarm maintenance in schools during school hours.
Post by: PhilHallmark on September 06, 2007, 08:37:58 PM
A second engineer at the panel, whereby both the servicing engineer and the guy at the panel - sounders disabled - linked with a radio, is a good solution in many cases. As long as the salesman selling the contract has allowed for it!
2 men per service should be standard practice to ensure the alarm can be fully activated if required. Oh and danger money for working allongside the little darlings.