FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Technical Advice => Topic started by: Ashley Wood on February 06, 2007, 11:06:12 AM

Title: One for the sprinkler gods & structural bods!
Post by: Ashley Wood on February 06, 2007, 11:06:12 AM
I have a single storey factory classified as 'High hazard' (new build). The building is a portal steel frame construction. If the building were being built without the sprinklers I would have to clad the steel. I am being told that this is not required due to the fact that a sprinkler system is being installed. If this is correct, what standard/s should apply to the sprinkler design?
Title: One for the sprinkler gods & structural bods!
Post by: kurnal on February 06, 2007, 05:04:35 PM
The answers will be found in Approved document B.

The protection may have been required for compliance with functional requirement B3, B4 or both. Table A1 and A2 in appendix A set the fire performance criteria, and to qualiify for the relaxation allowed against the installation of sprinklers the installation should comply with the recommendations in paragraphs 0.16 - 0.18
Title: One for the sprinkler gods & structural bods!
Post by: wee brian on February 06, 2007, 10:23:42 PM
As a general rule you dont need fire protection on single storey structures. If you are near the site boundary the external walls (and supporting structure) may need protection. ADB gives a 50% reduction on sprinklered buildings.
Title: One for the sprinkler gods & structural bods!
Post by: Ashley Wood on February 07, 2007, 12:23:25 PM
Thanks guys for your help.

Best regards

Ashley