Post by: Graeme on May 12, 2007, 07:22:31 PM
I know that the standards asks for support i.e metal clips that can withstand the same temperature as the cable itself when the cable relies on them as sole means of support

but if an installer uses metal clips onto a brick wall does the fire rating of the support extend to the plastic wall plugs used to put the screws into for the metal clips as these plugs are supporting the cable as well?
Title: Support of cable to BS5839-1
Post by: kurnal on May 12, 2007, 07:53:49 PM
Yes its a good point in theory but sense and reason must come into it as well.
Usuallt the load on a clip is perpendicular to the screw, it would be more critical if in line with the screw shank.

And in the real world for how long do we  the resilience of the alarm cable to be maintained? Surely once the alarm has actuated and people evacuated then it doesnt really matter if the smoke detector falls off the ceiling and the sounders melt- its done its job. I would suggest the plastic plugs drilled into brick are much better protected than the rest of the exposed system notwithstanding the screw.
Title: Support of cable to BS5839-1
Post by: Graeme on May 13, 2007, 09:11:10 AM
That was my thinking that the wall plug is protected inside the wall but i am just curious.
The cable is also supposed to stay on the wall after the alarm has evacuated the building.
Title: Support of cable to BS5839-1
Post by: Wiz on May 13, 2007, 10:44:57 PM
Has anyone done any tests to see if the fixings for a cable being used for the connection of sounders, and clipped to a ceiling, does not suffer from the rawlplug melting by the heat from a fire below and the cable breaking as it falls down?.
A building with phased evacuation may require the alarm sounders to be able to operate for long periods after a fire may be detected ( This must surely be for almost an hour if we are talking about a system with more than four phases of evacuation thereby requiring 'enhanced' grade cable.
Whilst I can understand professor K's points when we are talking about cable fixed to walls, I think that Graeme's question is possibly more relevant to fixings on ceilings - I could imagine rawlplug style fixings failing pretty quickly.
Title: Support of cable to BS5839-1
Post by: John Webb on May 14, 2007, 11:30:20 AM
An even bigger problem is when there is a false ceiling to whose tiles sounders and visual beacons are fitted. As the ceiling is damaged by a developing fire and starts to collapse the wiring can be mechanically disrupted with consequential loss of alarm. This may have happened at the 1993 Littlewoods store fire at Chesterfield within four minutes of the deliberate ignition of clothing on display. There was little warning of the fire on the floor of origin due probably to this damage. (See the Derbyshire Fire & Rescue Service's Fire Investigation Report page 47, paras 2.5.7,8 & 9)
Title: Support of cable to BS5839-1
Post by: kurnal on May 14, 2007, 11:51:46 AM
John do you have access to that FI report??

I should have remembered that incident and have been looking for that report for other purposes without success.

The conclusions to be drawn so far are therefore that :
1- fire alarm cables should never rely on any structure for their support that does not itself have guaranteed integrity in a fire for a suitable duration (which may be significant period depending on the evacuation strategy of the building)
2- Cable fixings need to be considered in their entirety including the ancillary screws and rawl plugs or similar.

3- In newly built IT suites I have seen fire alarm cables fastened to cable trays intended for network cables with plastic tie wraps- the trays having been installed at first fix-  and havn't thought about questioning their integrity before now.

Is there anything in BS7671 or similar that covers this Dr Wiz?
Starting to regret my flippant initial response now Graeme!!
Title: Support of cable to BS5839-1
Post by: John Webb on May 14, 2007, 01:50:23 PM
Kurnal,
I have a photo-copy, not an original, so the photos aren't very good. Penny Morgan (who occasionally contributes to the forum) and myself were the Fire Research Station team (with a photographer) who assisted Derbyshire F&RS with the investigation, so I saw the damage in person.

What was it you were particularly interested in?  Do e-mail me direct if you wish.
Title: Support of cable to BS5839-1
Post by: Thebeardedyorkshireman on May 14, 2007, 03:39:35 PM
Kurnal
Without going off on one, it was the good doctor and myself who did the cable tests at BICC warrington which added to the issue surrounding the cable changes to BS 5839, 2002.
We were angling for enhanced to be pyro only, for a variety of reasons including the cable clip issue. Pyro can be sufficiently supported by resting on support walls and ceiling grid. In a high temp fire test, soft skin cables rapidly expand in diameter to resemble cylindrical cigar ash. When unsupported (in our tests, just to protect the innocent) they failed to perform. When firmly clipped with metal clips this whole fragile structure remains for a duration of time, acting as an insulator both inter-conductor and to earth (if present) If the clip failed or was not present, the 'cigar ash' fell away and you had a short circuit ( the cable does not break which is the point of all this claptrap ) please dont add water or mechnical movement children or we will be here forever.
 This is a very short 'jist' of some very long and detailed testing and represents my personal views & recollection only.

In short, if you lay the cable 'on' tray it is supported along its entire length and plastic clips are fine. If you clip it to a vertical tray or to the underside of a metal tray you should use metal clips spaced in accordance with the manufacturers instructions. This may answer your IT room situation. You could allways use pyro, which is a cable designed to do a job, not a cable designed to pass a test
Dave
Title: Support of cable to BS5839-1
Post by: Wiz on May 14, 2007, 04:40:54 PM
Dave (TBY), any experience / knowledge of plastic plug fixings melting in a fire within 30 / 60 mins?
Title: Support of cable to BS5839-1
Post by: kurnal on May 14, 2007, 04:57:52 PM
Thanks Dave. Nice insight as well into your and Dr Wiz' past.

So you have both Been Incarcerated in Corrective Care before have you?

No wonder Wiz is such a wet lettuce when it it comes to escaping from this home for the bewildered. Too much exposure to plastics fumes has addled his brain - you should have made sure he did not inhale when smoking those cigars. Now he cant tell the difference between a manikin  and a mannequin
Title: Support of cable to BS5839-1
Post by: Thebeardedyorkshireman on May 15, 2007, 12:07:34 PM
Wiz
we carried out no tests on the plastic plugs in a fire condition.
We can make a few observations if they will be of help though. The makers of FP200 (used to be called Pirreli) make a fixing gun which fires a stud through a metal clip to support the cable. This may be a better fire rated fixing,but you would need to talk to their techies.
A metal tray fixed to the ceiling with rawl bolts or para anchors and the cable laid on the top and fixed with steel clips is probably as good as it gets for an enhanced cable run.
If the enhanced run includes detectors and sounders along its length and electrically connected to the cable then the weakest link would be when the head melts and falls out, thus severing the continuity of the conductors. It may be that this would occur before the plastic plug melts. The base of the detector would normally be installed with screws into same plugs therefore providing another potential weakness. If you make the judgement that plastic plugs are bad news then you would need to eradicate all similar low temperature weaknesses from your enhanced circuit.
Thus in say a hospital basement duct you would have your enhanced circuits running through the area with detection on a separate sub loop with isolators which could be classed as sacrificial after raising the alarm.
This was the point of our tests in that cables running through an area on fire still have to function to provide facilities to other areas. In this context function means an ability to pass electronic data not just an electrical circuit which illuminates a bulb. I hope this is not an egg sucking situation but I will stop rattling on now.
Regards
Dave
ps what happened to the matron in the black stockings?
Title: Support of cable to BS5839-1
Post by: Wiz on May 16, 2007, 12:34:49 PM
Thanks for the above Dave.

It seems the answer might be as I thought it might be;

1) It looks like no-one has specifically looked at the possible problems of the use plastic plug fixings for fire resistant cable.

2) It is probable that the heat needed to seriously detrimentally affect a plastic plug fixing located within a wall is likely to be so great, that it will have seriously detrimentally affected lots of other things before it affects the fixing!

Is the above a fair summary?

For your info, I already have experience of the special fixing gun that is available. It works o.k., but is so powerful it often blows away all the plaster around each fixing! Also the cost of fixings is very high.

Wiz

p.s. Most of us in this home for the constantly bewildered are being dosed with drugs to stop us thinking about matron's black stockings. The drugs are obviously not working on you and I suspect you will soon be getting a visit from Professor Kurnal to find out what is going on.
Title: Support of cable to BS5839-1
Post by: Fishy on May 16, 2007, 01:12:04 PM
I wouldn't agree at all that "It is probable that the heat needed to seriously detrimentally affect a plastic plug fixing located within a wall is likely to be so great, that it will have seriously detrimentally affected lots of other things before it affects the fixing".  I recall that these are typically polyethylene or nylon.  In either case they the screws would quickly transfer enough heat through to the plugs to melt them - the melt zone only needs to reach the depth of the threads and they'll just drop out - especially on a ceiling.

Interestingly, I cannot find any BS or manufacturers' instructions that deals with this in any detail.  Pirelli just recommend their proprietary fixing system, for example.
Title: Support of cable to BS5839-1
Post by: kurnal on May 16, 2007, 02:02:12 PM
You are right fishy and so often surface mounted cables are simply installed using standard plastic wiring clips rather than the recommended  plastic coated metal P clips. And till Graeme raised it I for one have always observed it and not passed comment.
Title: Support of cable to BS5839-1
Post by: Thebeardedyorkshireman on May 16, 2007, 02:05:52 PM
I have just spoken to a technical chap from 'Rawlplug' who confirms that they have never conducted tests of a type we are refering to on a plastic plug. He concured that the wall mount may be preferable to a ceiling mount and that the dia of the hole, length of the screw,dia of screw and amount of compaction of the plug material would all be variables in the final outcome. The temperature would be the major consideration ( but we all know that).
If you use pyro and the clips fail the probability is that the cable will continue to work up to allmost the melting point of the copper. I do not believe that the new cables, including enhanced, will continue to function.
Perhaps this calls for additional fixing methods above and beyond that which is normally accepted if the full benefit of the cable integrity is necessary to ensure a working fire stratergy. In short, clip it on a metal tray bolted to the structure.
It would be necessary for somebody to specify this at the time of tender or you will get plastic plugs and screws.
With hindsight I wish we had tested the fixings when we had the furnace available to us. Its brookside now.
Maybe we need a note in the BS on the next revision?
Dave
Title: Support of cable to BS5839-1
Post by: kurnal on May 16, 2007, 02:10:30 PM
Wiz
Just to keep you up to date lucky escaped by using matrons stockings as a rope. She has to go commando now. When she bends over to tuck us in  at night I get reminded  of a photo I once saw of Dave smiling but I cant make the connection. Pass the  methyl bromide.
Title: Support of cable to BS5839-1
Post by: Thebeardedyorkshireman on May 16, 2007, 03:14:30 PM
Kurnal
I have the dodgy video of matron pretending to be a student who cant hear the bells and needs to be rescued (see the other posts)
I will be away from the ranch for a few days plus the fire expo. If I email the material down to you, can you forward it on to the other guy,when and if he confirms its what he requires please? If this is acceptable, just ping me an email in order that I have your details.
Regards
Dave
ps must be the other Dave as I have never smiled in my life
Title: Support of cable to BS5839-1
Post by: kurnal on May 16, 2007, 03:43:25 PM
Perhaps it was indigestion then. Have sent the mail thanks.
Title: Support of cable to BS5839-1
Post by: Graeme on May 16, 2007, 06:25:33 PM
Thanks for all the replies.

It looks like there is no evidence against using wall plugs,which i,m sure will be a relief to most fire alarm installers.
There is not  always going to be cable trays in bulidings which are not new builds and trunking is a cost effective containment.

If wall plugs were to become a un-approved method of fixing,then this would be a major headache and increase installation prices.
Title: Support of cable to BS5839-1
Post by: Wiz on May 16, 2007, 09:37:35 PM
Sensible input and considered opinions to Graeme's question. Even a bit of humour. This is how forums should work. Well done everyone.
Title: Support of cable to BS5839-1
Post by: Fishy on May 17, 2007, 02:26:30 PM
Quote from: Graeme
Thanks for all the replies.

It looks like there is no evidence against using wall plugs,which i,m sure will be a relief to most fire alarm installers.
There is not  always going to be cable trays in bulidings which are not new builds and trunking is a cost effective containment.

If wall plugs were to become a un-approved method of fixing,then this would be a major headache and increase installation prices.
...but Graeme... BS 5839-1, including the December 2004 amendment, states quite clearly that the "Methods of cable support should be non-combustible and such that circuit integrity will not be reduced below that afforded by the cable used, and should withstand a similar temperature and duration to that of the cable, while maintaining adequate support".  Plastic plugs are combustible; are an essential component of the "cable support" and therefore don't comply.
Title: Support of cable to BS5839-1
Post by: Markymark on May 17, 2007, 09:47:50 PM
May I just quickly pass comment. I have seen (at first hand) large storage heaters "fall" off the wall due to the plastic plugs melting. These storage heaters are extremly heavy and thus at least 8 fixings are required. The plastic plugs must not be used but fibre rawl plugs are to be used as these do not melt. It will add a cost to fire alarm installations but I am not sure of their performance in much higher temperatures.
Title: Support of cable to BS5839-1
Post by: Graeme on May 17, 2007, 09:54:24 PM
Hi Fishy

Its' that exact clause which made me start this topic.What other options are there  for fixing a cable to a brick wall?

thanks

G
Title: Support of cable to BS5839-1
Post by: Wiz on May 18, 2007, 10:53:51 AM
Quote from: Markymark
May I just quickly pass comment. I have seen (at first hand) large storage heaters "fall" off the wall due to the plastic plugs melting. These storage heaters are extremly heavy and thus at least 8 fixings are required. The plastic plugs must not be used but fibre rawl plugs are to be used as these do not melt. It will add a cost to fire alarm installations but I am not sure of their performance in much higher temperatures.
Very interesting post. Can anyone carry out some tests to see if fibre style wall plug fixings operate better than plastic style wall plug fixings in a fire?
Title: Support of cable to BS5839-1
Post by: Wiz on May 18, 2007, 11:11:40 AM
Quote from: Fishy
Quote from: Graeme
Thanks for all the replies.

It looks like there is no evidence against using wall plugs,which i,m sure will be a relief to most fire alarm installers.
There is not  always going to be cable trays in bulidings which are not new builds and trunking is a cost effective containment.

If wall plugs were to become a un-approved method of fixing,then this would be a major headache and increase installation prices.
...but Graeme... BS 5839-1, including the December 2004 amendment, states quite clearly that the "Methods of cable support should be non-combustible and such that circuit integrity will not be reduced below that afforded by the cable used, and should withstand a similar temperature and duration to that of the cable, while maintaining adequate support".  Plastic plugs are combustible; are an essential component of the "cable support" and therefore don't comply.
Fishy, the words 'non-combustible' were only added in the December 2004 ammendment and I personally found the addition somewhat confusing, since the original clause already seemed to be recommending that fire resistance integrity should be equal to that of the cable it was supporting.

Surely, everything is combustible if the right temperature is applied to it?

If the word combustible was to be used shouldn't it have said something like 'the cable support should be no more combustible than the cable it is supporting' !

Is anything really non-combustible?
Title: Support of cable to BS5839-1
Post by: John Webb on May 18, 2007, 09:28:19 PM
It is possible to get quite small expanding 'Rawlbolts' which are entirely of metal construction and which do not need a hole much bigger than that of a plastic wall plug. Could this be the solution?
Title: Support of cable to BS5839-1
Post by: Graeme on May 18, 2007, 10:41:54 PM
found these

http://www.b2bchinasources.com/China-Manufacturers-16444/Metal-Wall-Plug.html

don't know how much they will be though.
Title: Support of cable to BS5839-1
Post by: Graeme on May 18, 2007, 10:46:44 PM
and

http://www.uk.prysmian.com/en_GB/cables_systems/energy/catalogue_pdf/firefix/Firefix_singleclip.pdf;jsessionid=GD0ZD2FUZ5RRFFYKJOPCFFA

might go for this as it look better fun and i can be like all the lazy joiners nowadays with their nail guns.
Title: Support of cable to BS5839-1
Post by: John Webb on May 19, 2007, 01:18:56 PM
Screwfix www.screwfix.com do a number of all-metal wall plugs, mostly by Fischer, for brick, concrete and plasterboard. These are available to take M6, M8 and M10 standard threaded screws. For example, a 'Drop-in anchor' for an M6 screw is £9.50 per 100 inc. VAT.

An M6 'Sleeve anchor' requires an 8mm hole and is sold at £48 for 500.

There is also a 'Nail Anchor' which requires a 6mm hole and has a large diameter head to, I presume, allow it to be driven into the hole. Of most interest to us it says 'Fire-rated F120' - again this is a Fischer fitting. (If you have a Spring 2007 printed Screwfix catalogue, bottom left of page 42.)
Title: Support of cable to BS5839-1
Post by: Graeme on May 19, 2007, 08:17:59 PM
Hi John

Can you paste the web page for the fischer metal wall plugs please?

i can only find nylon ones.

Thanks
Title: Support of cable to BS5839-1
Post by: John Webb on May 20, 2007, 09:08:09 AM
Graeme,
I was quoting entirely from my printed copy. I'll look at the Screwfix website probably tonight and post something if I can find it.
Title: Support of cable to BS5839-1
Post by: John Webb on May 20, 2007, 02:03:40 PM
Graeme,
The Fischer metal wall plugs are under 'Expansion Plugs'. hopefully you will get there as follows:
http://www.screwfix.com/app/sfd/cat/cat.jsp?cId=101581&ts=62602

The Nail Anchor is under 'Shield Anchors' - item 22643:
http://www.screwfix.com/app/sfd/cat/cat.jsp?cId=100058&ts=62942
Title: Support of cable to BS5839-1
Post by: Tom Sutton on May 20, 2007, 02:58:38 PM
Try  http://www.b2bchinasources.com/showroom.php?c=6543&f=5&p=0000023318 gives the details but not the price however there is a contact.
Title: Support of cable to BS5839-1
Post by: Graeme on May 20, 2007, 09:51:36 PM
Thanks John

Those are the pages that i have been looking at.

http://www.screwfix.com/app/sfd/cat/cat.jsp?cId=101219&ts=94124

This shows the metal wall plugs that Twsutton his posted a link to but if you look they do not look like they stock metal although they say so,just nylon ones.
Title: Support of cable to BS5839-1
Post by: bill_davis on May 23, 2007, 03:59:03 PM
I'm a client and not a designer. On a DIN standards project I worked on a few years ago, the emergency cables had to be supported to survive the life of the fire resistant- say mineral insulated - cables , ie, cable trays had to be fastened to a slab with supports that would survive 60 or 90 minutes, or cables had to be clamped to 1hour or higher walls with fire resistant clamps, etc.

On the project I am on now, the designers are saying that British Codes don't require such support. I can't believe that and I think that BS5839-1 may cover this part of the application. Unfortunately I don't have access to the codes.

Can someone please confirm the applicable circumstances? Does BS5839-1 or another code contain this requirement? Or is there truly no required support systems under the BS codes.

Thanks much,

Bill Davis
Title: Support of cable to BS5839-1
Post by: Graeme on May 23, 2007, 05:19:38 PM
f) Methods of cable support should be such that circuit integrity will not be reduced below that afforded
by the cable used, and should withstand a similar temperature and duration to that of the cable, while
maintaining adequate support.

make your own main up if you apply this to wall plugs as there is some who do and some who don't.

This does however certainly apply to the use of metal cable ties and metal clips.
Title: Support of cable to BS5839-1
Post by: bill_davis on May 25, 2007, 09:18:37 AM
Graeme,

Thank you for your input! Is the f) actually from BS5839-1? If so, could you also please give me the paragraph number?

Happy Whit Monday; we're off to Damascus. It should be interesting.

Bill Davis
Title: Support of cable to BS5839-1
Post by: Wiz on May 25, 2007, 11:01:27 AM
Quote from: bill_davis
Graeme,

Thank you for your input! Is the f) actually from BS5839-1? If so, could you also please give me the paragraph number?


Bill Davis
If I may help out and save Graeme answering, it is clause 26.2 f) of BS5839 Part 1 2002.
Title: Support of cable to BS5839-1
Post by: bill_davis on May 25, 2007, 01:11:33 PM
GREAT!  Thanks, Wiz.

Bill
Title: Support of cable to BS5839-1
Post by: FireFly40 on June 09, 2007, 11:43:57 PM
I saw some screws with clips in the fire alarm bit of the german version of wickes (toom) there was no english part on the label but a rough translation was " mega hardened thready bit on screw so screw straight into concrete no plug required " thought at first lazy foreigners dont even bother using plugs especially as they came with their own really short masonry drill , but after using some of their twin and earth ( round so it doesnt twist up like a snake and green/yellow already on the earth which is the same size as the L/N) realized we can learn stuff from fritz. These are probably the beasts you need. Probably be available in UK in 20 years or so. Rule Brittania uber alles
Title: Support of cable to BS5839-1
Post by: Goodsparks on June 11, 2007, 06:18:15 PM
Like these. (been around for a while)

http://www.screwfix.com/app/sfd/cat/pro.jsp?ts=82231&id=12531

Paul
Title: Support of cable to BS5839-1
Post by: FireFly40 on June 11, 2007, 10:53:59 PM
Yes those are the fellas certainly save all the expense of mini rawlbolt anchors etc. Never used em though but I bet theyre the dogs wotsits
Thanks Paul
Title: Support of cable to BS5839-1
Post by: GregC on February 07, 2008, 04:43:21 PM
Hi, I have been lurking on these boards for many many months and found them to be very educational so many thanks for all your posts to date.

Sorry to resurrect this topic but I have searched everywhere for an answer that should be simple and relates to this topic.

What is the minimum spacing between fixings on either a wall or cieling or inverted tray, the only item I can find or have found so far is the HSE vibrations requirement being 3 fixings per metre and that was on Pirellis "buy our fixing guns" page.

If anyone can point me in the right direction it would be greatly appreciated

Cheers
Title: Support of cable to BS5839-1
Post by: David Rooney on February 07, 2008, 05:03:31 PM
Quote from: GregC
Hi, I have been lurking on these boards for many many months and found them to be very educational so many thanks for all your posts to date.

Sorry to resurrect this topic but I have searched everywhere for an answer that should be simple and relates to this topic.

What is the minimum spacing between fixings on either a wall or cieling or inverted tray, the only item I can find or have found so far is the HSE vibrations requirement being 3 fixings per metre and that was on Pirellis "buy our fixing guns" page.

If anyone can point me in the right direction it would be greatly appreciated

Cheers
BS 7671 - 16th edition electrical regs..... soon to be 17th edition.
Title: Support of cable to BS5839-1
Post by: Graeme on February 08, 2008, 07:17:10 PM
soft skin   every 300 horizontal and 400 vertical
Title: Support of cable to BS5839-1
Post by: Galeon on February 11, 2008, 02:18:04 PM
For all you older people , at least we dont need to worry about the wooden / fibre plug , now there is a thought ?
Title: Support of cable to BS5839-1
Post by: GregC on February 11, 2008, 02:28:50 PM
Well I did find the details on 300mm and 400mm, what my query was centered upon was the possible relaxation of these fixings distances as I have an electrical contractor who is arguing they can be relaxed if a risk assesment is carried out.

I since found an ECA circular that advises this relaxation is on drops to smoke detectors on cielings from the slab above, I have yet to find anything that says you can expand on 300mm on horizontal fixings though.
Title: Support of cable to BS5839-1
Post by: Graeme on February 11, 2008, 05:58:30 PM
can't see how a risk assessment would be relevant to how a cable was supported to keep it functional during a fire.
sounds like contractor is looking for a way out.
Title: Support of cable to BS5839-1
Post by: David Rooney on February 12, 2008, 01:42:16 PM
Quote from: GregC
Well I did find the details on 300mm and 400mm, what my query was centered upon was the possible relaxation of these fixings distances as I have an electrical contractor who is arguing they can be relaxed if a risk assesment is carried out.

I since found an ECA circular that advises this relaxation is on drops to smoke detectors on cielings from the slab above, I have yet to find anything that says you can expand on 300mm on horizontal fixings though.
I'd ask the contractor to produce the regulation that says it......