Post by: Mushy on March 17, 2008, 09:40:52 AM
Hi

I've seen a report lately that says that 10% of the fire detection system (smoke and heat) should be tested annually....why only 10%?

Thanks
Title: testing of fire detection system
Post by: Midland Retty on March 17, 2008, 02:15:16 PM
Hi Mushy

Which report was this?
Title: testing of fire detection system
Post by: Allen Higginson on March 17, 2008, 11:58:28 PM
Quote from: Mushy
Hi

I've seen a report lately that says that 10% of the fire detection system (smoke and heat) should be tested annually....why only 10%?

Thanks
You sure it wasn't a typo and someone dropped a 0 ??
Title: testing of fire detection system
Post by: Clevelandfire on March 18, 2008, 12:16:37 AM
doesn't sound right to me
Title: testing of fire detection system
Post by: Chris Houston on March 18, 2008, 12:20:53 AM
British Standard 5839 Part 1, 2002 recommends 100% annually.  As a 6 month check on the battery is also needed, most companies do 50% every 6 months.  The previous version of 5839 recommended quarterly testing and therefore 25% quarterly is not uncommon.  10% annualy would be unacceptable and is probably a typo I would suggest.
Title: testing of fire detection system
Post by: Mushy on March 18, 2008, 12:38:32 PM
Thanks all...I thought it was a tad odd
Title: testing of fire detection system
Post by: Mar62 on April 14, 2008, 04:18:18 PM
I was going to ask if it was Chubb, but I think they normally add zeros rather than drop them, dont they?????
Title: testing of fire detection system
Post by: jasper on April 15, 2008, 09:24:19 PM
Quote from: Martin672
I was going to ask if it was Chubb, but I think they normally add zeros rather than drop them, dont they?????
lol