		FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Fire Safety => Topic started by: Mushy on March 17, 2008, 09:40:52 AM
		
			
			- 
				Hi
 
 I've seen a report lately that says that 10% of the fire detection system (smoke and heat) should be tested annually....why only 10%?
 
 Thanks
- 
				Hi Mushy
 
 Which report was this?
- 
				Hi
 
 I've seen a report lately that says that 10% of the fire detection system (smoke and heat) should be tested annually....why only 10%?
 
 Thanks
 You sure it wasn't a typo and someone dropped a 0 ??
- 
				doesn't sound right to me
			
- 
				British Standard 5839 Part 1, 2002 recommends 100% annually.  As a 6 month check on the battery is also needed, most companies do 50% every 6 months.  The previous version of 5839 recommended quarterly testing and therefore 25% quarterly is not uncommon.  10% annualy would be unacceptable and is probably a typo I would suggest.
			
- 
				Thanks all...I thought it was a tad odd
			
- 
				I was going to ask if it was Chubb, but I think they normally add zeros rather than drop them, dont they?????
			
- 
				I was going to ask if it was Chubb, but I think they normally add zeros rather than drop them, dont they????? lol