THE REGULATORY REFORM (FIRE SAFETY) ORDER 2005 => Q & A => Topic started by: PaulT on March 27, 2008, 09:43:46 AM
-
Is there a simply method for calculating the maximum numbers of persons who can occupy a floor and building. The information refers to general office space.
Any answer appreciated.
-
Start with AD pt B, purpose groups, then the table for occupancy/floor space factors.
-
Look at the LCLG Guide number 1 for Offices and shops. Assign a risk category as detailed in that document, measure the opening widths for the doors and look at the tables. A 700mm door will allow X number of people dependent on the risk you assign.
CLG guides are a free download from www.communities.gov.uk You need the means of escape section in part 2.
-
Help,
When opening a night club is there a rule for the number of compulsary toilets related to capacity?
Judita
-
Judita, I think you are asking the wrong forum this question.
-
Help,
When opening a night club is there a rule for the number of compulsary toilets related to capacity?
Judita
Hi Judita
In asnwwer to your question yes you should have a set ammount of toilets available related to capacity.
However Im sure what the facts and figures are - you would need to approach your local environmental health department for guidance
-
6/m2 for office building according to ADB
-
Judita, have a look at BS 6465-1:2006 - Sanitary installations. Code of practice for the design of sanitary facilities and scales of provision of sanitary and associated appliances.
-
There is a thread already on here that may be of some use. http://www.fire.org.uk/punbb/upload/viewtopic.php?id=3270