Title: fixed electrical testing
Post by: jasper on May 27, 2008, 07:48:44 PM
Hi all, I have been trawling the internet to find the frequency for fixed electrical testing on small blocks of flats, these have sockets etc. on the shared moe so I thought there would be a requirement
Title: fixed electrical testing
Post by: kurnal on May 27, 2008, 08:19:41 PM
I think BS7671 (IEE Wiring Regs) would recommend 5 years for installations in the common areas, or more frequently if the environment is hostile. Heres a very short extract from Modern Wiring Practice by Steward and Stubbs

"The determination of the frequency of periodic inspection is covered by lEE Regulation 732-01-01. No specific period is laid down, and an assessment needs to be made as to the use of the installation, the likely frequency of maintenance, and the possible external influences likely to be encountered. The person carrying out the inspection and testing, and completing the inspection certificate needs to take account of these issues. In the absence of other local or national regulations, a maximum period of five years would be applied, with shorter periods where appropriate"
Title: fixed electrical testing
Post by: jasper on May 27, 2008, 08:28:12 PM
thanks Kurnal
Title: fixed electrical testing
Post by: John Webb on May 28, 2008, 10:18:32 AM
The latest version of the IEE Regs, published earlier this year, (BS 7671: 2008) has seen a significant revision of the order of chapters. The Regulation about periodic inspection and testing is now Chapter 62. It does not make much change. Detailed advice is contained within the IET (formerly IEE) book on the Testing and Inspection of Electrical installations.

(Part 7 and its various sections deal with the problems of the particular requirements of special installations such as bathrooms, agricultural premises, exhibitions and the like.)