If a detector is mounted near an air conditioning unit output, surely they should be at least one metre away, howevever BS5839 only refers to siting them 1 metre from air inlets?
''Detectors should not be mounted within one metre of any air inlet of a forced ventilation system''
-
Doesn't that mean the vent where the cooled air comes IN (inlet) to the compartment???
-
Also, how many times do you see a detector head that has a ceiling fan close by pushing the smoke away
-
If a detector is mounted near an air conditioning unit output, surely they should be at least one metre away, howevever BS5839 only refers to siting them 1 metre from air inlets?
''Detectors should not be mounted within one metre of any air inlet of a forced ventilation system''
I've often wondered about this one as well.
I have presumed that a detector being too close to an inlet means it could end up in a 'dead spot' of the air currents being sucked in and thereby miss any smoke. If so, why would this also not be true of outlets and therefore require a BS recommendation to mount detectors a certain distance away from outlets?
I await all you H & V experts to provide an explanation!
-
I dont think we should be too pedantic. The important thing is that we all have an understanding of factors that could lead to a delay in our goal of suitably early warning of fire and design accordingly.
BS5839 has evolved over the years and detectors can be used for protecting a space, protecting escape routes, protecting business continuity or to operate plant, equipment and systems. I dont think the meaning of every word was reconsidered as the document was extended and reviewed. I think messy makes a good point and the clause was probably written with his scenario in mind.