What is difference between Grade A pt 6 system and 5839 Pt 1 system?
-
Very little. The differences are detailed in Part 6 with regard to sound levels, height of MCP's, hearing impaired people and some other bits. There is a table in part 6 that allows you to reflect on the differences.
-
Thanks jokar. I am right in thinking that Fire Alarm call points are still required?
-
not always
Part 6 18.2
Note 1-it will be generally appropriate to at least consider MCP's on a grade A system.
-
The big difference is standby battery capacity.