Title: clymac mcp offline
Post by: Davro on August 12, 2008, 08:47:56 PM
Just been given a contract to service a clymac panel. Not a problem there but a fault was left from last service company and it was a mcp saying offline. Not come accross this before, but if it does need a new mcp can i still get the old style ones or does it have to be the new type (drop down front) and if it is the new type, do i have to learn it onto the panel or would it be o.k. Also the commissioning code has been changed.
Title: clymac mcp offline
Post by: Thebeardedyorkshireman on August 13, 2008, 11:54:50 AM
Davro
We have one on the shelf if you want it. Just check the loop voltage at the mcp, copy the address code onto the new one and press the reset on the back of the panel. It should log it back on with all the original text etc etc.
Assume it's a ZP3. Email me for the code instructions, not for public view
Dave