Title: Access for fire appliances
Post by: Tom Sutton on August 20, 2008, 08:23:09 PM
Quote
I have a problem concerning B5 (Fire appliance access) to a two storey outbuilding of a listed building (a Pub/coaching house) which has been converted into four dwellings.  The access is through an arched entrance 2.7m x 2.7m - not big enough for a Fire appliance.  The dwellings form a terrace, the closest dwelling is wholly within 45m of the High Street to which a Fire appliance can reach. The furthest point of the fourth dwelling is ~70m from a Fire appliance.
 
A 63mm dia 'wash-out' main and valve has been fitted by the water company, fed from the town mains. Its pressure has been recorded over a five days at 3.5bar and flow rate estimated as ~500ltr/min. It is within 30m of all points on the dwellings. I was 'advised' that the Fire brigade could adopt this as a Fire Hydrant but this does not appear to be the case.
 
Due to a catalogue of confusion, argument and delay etc. the dwellings are finished but the Building Inspector will not pass them because of B5. (nor will he advise how the problem can be overcome).
I recently received the above inquiry any ideas.
Title: Access for fire appliances
Post by: jokar on August 20, 2008, 08:40:11 PM
Speak to the FRS and find out what they are stalling on.  Nowadays, FRS are seeking residential sprinklers as a engineered solution for access difficulties such as this.  I know that this is impractical but it may well be why it hs been held up.
Title: Access for fire appliances
Post by: Izan FSO on August 20, 2008, 09:32:41 PM
Quote from: jokar
Speak to the FRS and find out what they are stalling on.  Nowadays, FRS are seeking residential sprinklers as a engineered solution for access difficulties such as this.  I know that this is impractical but it may well be why it hs been held up.
Why speak to FRS? it is in the hands of building control (although we are stautory consultees) it is up to building control to approve compliance with ADB, however if they are stuck for a solution they may ask us for advice as to what we would accept.

The other case is that it is an AI and not local authority BC and it may be that the FRS have not yet been consulted. I had an application land on my desk today from an AI for a premises that has been open and trading for weeks following a major refit. we have some major issues with the finished scheme and now have an up hill battle to get it right.
Title: Access for fire appliances
Post by: kurnal on August 20, 2008, 10:27:52 PM
Nothing in the building Regulations is about property protection- its all about life safety.

If its just one or two of the properties that fall outside the the 45m guidance then address those specific issues. Improve the standard of fire safety in those properties - reduce the likelihood of someone needing rescue by the fire service- install a water mist or domestic sprinkler system, or beef up the passive fire protection to the means of escape?
The hydrant could be relevant if there is not another hydrant within say 100m of the appliance parking position (the 90m hydrant rule in B5 only applies to buildings with a compartment size exceeding 280sq m)  - otherwise a hydrant on the inner side of the arch does not contribute much at all to life safety of the residents.
Title: Access for fire appliances
Post by: jokar on August 21, 2008, 09:31:41 AM
IZAN FSO.  Isn't B5 for the safety of firefighters?
Title: Access for fire appliances
Post by: CivvyFSO on August 21, 2008, 09:47:05 AM
Most BC bodies will strictly follow what the FRS want with regards B5 requirements. It is access for our boys and girls. We should know how they operate, we should know where things can be relaxed and what should be insisted upon.

Is it a fire hydrant or a riser they have installed? A hydrant wont help the case.

If a riser was installed then in all honesty it would probably be more messing about for the crews connecting up to the riser than rolling out an extra length of hose from the appliance. We do have to fight for our access and facilities as we only get the one bite during the building regs process, but sometimes it is simply impossible to achieve the requirements and allowances have to be made and we need to be reasonable. As nice as a sprinkler system would be, the crews are still having to roll out the extra length of hose and we should have a good level of compartmentation between the flats and it is only 2 storey.

What we do need to avoid is where people try to use a gate width as an excuse for not putting the hard standing required for an appliance.
Title: Access for fire appliances
Post by: CivvyFSO on August 21, 2008, 09:55:06 AM
Quote from: jokar
IZAN FSO.  Isn't B5 for the safety of firefighters?
It is still technically for the life safety of the people in and around the building. It is facilities to assist the fire service, not to protect them.

It is still technically building control who should be ensuring the requirements are met. However your point is valid, and that is why the BC bodies tend to follow the FRS's lead on this requirement.
Title: Access for fire appliances
Post by: Tom Sutton on August 21, 2008, 11:37:30 AM
Quote
Part of my problem has been a difficulty engaging with the Fire brigade.  They have been reluctant/too busy to discuss the problem or possible options and been unwilling to attend a meeting either at site or at their offices.

Today I contacted a company supplying dry risers and they have prepared a solution for a similar problem where the excess distance is 7m (ie 7 + 45m).  Do you think this might be suitable in my case?
It looks the FRS will not speak to him and the BC will not give advice so what should he do. Present, for instance, the dry riser proposals and see if BC will accept it? Are there any other ideas that he may consider other than the dry riser and res sprinklers which has been suggested?
Title: Access for fire appliances
Post by: CivvyFSO on August 21, 2008, 11:46:41 AM
The dry riser solution is in ADB.

16.3 Note 1 : If the provisions in paragraph 16.2 or 16.3 (the 45m from all points...) cannot be met, a fire main should be provided in accordance with paragraph 15.3.

This is a riser within the building with access to the inlet no more than 18m away,(i.e. Inlet could be near the gate.) not a hydrant. Since this would be accepted under ADB, then he should speak to the FRS to see if they want to go through the motions of connecting to a riser in a 2 storey building, or if running 1 more length of hose out is more suitable.
Title: Access for fire appliances
Post by: messy on August 21, 2008, 09:10:23 PM
Do you why the WO can't be converted into a hydrant?

In my experience, it's fairly common for hydrants to be fitted as wash outs in the first place
Title: Access for fire appliances
Post by: kurnal on August 21, 2008, 09:24:14 PM
Quote from: CivvyFSO
The dry riser solution is in ADB.

16.3 Note 1 : If the provisions in paragraph 16.2 or 16.3 (the 45m from all points...) cannot be met, a fire main should be provided in accordance with paragraph 15.3.

This is a riser within the building with access to the inlet no more than 18m away,(i.e. Inlet could be near the gate.) not a hydrant. Since this would be accepted under ADB, then he should speak to the FRS to see if they want to go through the motions of connecting to a riser in a 2 storey building, or if running 1 more length of hose out is more suitable.
Yes I agree civvy- but in practical terms what benefit does it give? (I dont mean to shoot the messenger by the way - I know we feel the same from your own posting)

 Why spend good money on a such a pointless and expensive solution? In this case distance from access point to furthest point of floor area is 70m. A compliant layout would be 45m.

So What? 45m is two lengths of hose to run out.  70m is nearly 3 lengths of hose (direct distance).  If life is at risk how long does it take to run out threee lengths compared to two? an extra  5 seconds?  

How long does it take to find the fire main inlet, smash the glass, unroll a hose and couple, run in to the other end of the main, find the outlets, couple another length of hose, flake it cos you are on top of the job, then have the problem of all the kinks as you charge the hose- at least 60 seconds longer.

Sometimes there is an attitude amongst inspectors that "You are not compliant in this area so what will you give me in exchange?" - thats the type who would insist on a fire main in this situation. On the other hand of course it could also be the fault of the architect or fire consultant for not digging in their heels and arguing for common sense.
Title: Access for fire appliances
Post by: Tom Sutton on August 21, 2008, 10:45:38 PM
CivvyFSO are you not using ADB Vol 2 to solve a situation in ADB Vol 1. I am with Kurnal on this one I think a dry main would be pointless, considering its domestic dwellings, other than BI wanting some compensatory solution.

Messy, I see a WO as a hydrant the FRS do not pay for but in this case maybe the size of main (63mm) is the stumbling block the smallest I have seen hydrant fitted was 75mm. Any experts on BS 750.
Title: Access for fire appliances
Post by: FSO on August 22, 2008, 10:03:37 AM
This sounds a little annoying. If the FRS were on the ball, this should have been picked up at planning stage under local enactments. Failing that BC should have picked this up at lines on paper stage!

9251 sprinklers would be our answer everytime for a problem like this. We have a big push on these at the moment.
Title: Access for fire appliances
Post by: kurnal on August 22, 2008, 03:18:53 PM
I agree with regard to BS9251 sprinklers- they are fatastic and in an ideal world every home would have them. But would they be a proportionate requirement to the minimal increase in risk caused by the extension of the travel distance for fire service access from 45m to 70m, ir would it , in enforcement terms be a sledgehammer to crack a nut?

Could we not save the fire service an equivalent amount of time to compensate for the additional distance by having an autodialler linked to the fire alarm system, or a big sign with the address number and an external strobe linked to to the fire alarm system or a sign showing the location of the nearest hydrant or full detection to LD1 in the property so that the fire is detected at the earliest opportunity allowing the maximum opportunity to escape?
What do you think?
Title: Access for fire appliances
Post by: Tom Sutton on August 22, 2008, 09:28:25 PM
As the result of posting #11 the response was "At last.  The voice of reason! I agree fully with your logic and I shall let you know if the building inspector will also agree".

On a personal level what I do not understand is why the 45metres when I rode the big red lorries we a hose reel that reached 240 feet (73 metres) also four lengths of 1 3/4 connected flaked hose and a 1/2 inch branch in a locker next to the pump that reached 300 feet (91.4 metres.)?
Title: Access for fire appliances
Post by: Ricardo on August 23, 2008, 09:02:53 AM
Quote from: twsutton
On a personal level what I do not understand is why the 45metres ?
I always took the 45metres distance,as being a reasonable distance for FF's to travel from a parking space to a dwelling/house, with their (heavier)equipment such as ladders, BA, without getting tooo exhausted.
Title: Access for fire appliances
Post by: wee brian on August 23, 2008, 10:54:59 PM
based on the BDAG work 45 is a bit too far. So you dont want to go over it much.
Title: Access for fire appliances
Post by: kurnal on August 24, 2008, 12:09:14 AM
Quote from: wee brian
based on the BDAG work 45 is a bit too far. So you dont want to go over it much.
We need goals nothing wrong with that. But come on in the circumstances described the additional 25m is totally insignificant in terms of effort.

25m extra on level ground to a low rise 2 storey house fire is going to be far less effort than carrying your kit up even a single flight of stairs. But how many people when assessing plans for access to the footprint take account of the distance to travel upstairs- could be up to 7 storeys without a firefighting lift!

The only relevance I can see is in terms of hosereel lengths. since appliances carry 60m  usually per drum, then 45m is within striking distance of a single reel in practical terms.

But even this doesnt really stand up to logic- cos we cant take hosereel up a high rise tower block and have to rely on delivery hose and risers. So why would hosereels be imperative for a dwelling? And if they were, why is a fire main a reasonable alternative to access?
Title: Access for fire appliances
Post by: Tom Sutton on August 24, 2008, 11:17:18 AM
Quote from: wee brian
based on the BDAG work 45 is a bit too far. So you dont want to go over it much.
Thanks wee brian you learn something new everyday. But only had a quick shuffty at the research but it seems to me that the 45M refer to the distance from a fire fighting staircase, then you would need a dry riser. This would I would agree with in full BA and dragging a 70mm hose behind you, I wouldn’t wish to travel any further. However there is a lot of stuff available and I need to delve deeper.
Title: Access for fire appliances
Post by: FSO on August 26, 2008, 10:19:45 AM
Our hose reels are 56 metres.

As I am sure you are aware, research into flashover and backdraft training has found that the most effective pressure for firefighting within a compartment is 15 bar.

Of course you are all aware that this pressure is unachieveable through a main delivery. That is why 45 metres to us is quite important.

Of course high pressure hose reels are extendable but this should not be relied upon. Also, where possible you will want to have the pump as close to the BA team as possible for effective communication between the ECO and pump operator.

Kurnal, I agree with your comments as regard to BS9251 sprinklers. I would consider enhanced detection as a compensation. I will however always recommend sprinklers as I feel this is the safest option and this is a perfect oppertunity to get them installed in another premises.

I remember a quote from John Prescott stating that sprinklers would be mandatory in new builds by 2008. Its a sign of the way things are going. Its only a matter of time.
Title: Access for fire appliances
Post by: Tom Sutton on August 26, 2008, 11:19:09 AM
FSO I didn’t realise how short the hose reels are now days, we also carried four lengths of flaked 44mm hose complete with branch has that practise been discontinued. Regarding communication what about the pack sets?
Title: Access for fire appliances
Post by: FSO on August 26, 2008, 12:43:15 PM
When you say pack sets, do you mean hand held radios?

Yes it would be lovely, but there are only 3 on an appliance. In initial stages of an incident, 1 would be with the BA team, 1 would be with the ECO and the last one with OIC. I appreciate its a nice to have, but it is nice as a pump op to be able to see the incident where possible.

Also with running out 70mm lengths as a covering jet will take a fair amount of water from the appliance before you can find a decent hydrant to supplement. (around 100 litres per 23 metre length).

We have never had flaked lengths in the back.
Title: Access for fire appliances
Post by: Tom Sutton on August 26, 2008, 02:17:58 PM
Quote from: FSO
When you say pack sets, do you mean hand held radios?

Yes it would be lovely, but there are only 3 on an appliance. In initial stages of an incident, 1 would be with the BA team, 1 would be with the ECO and the last one with OIC. I appreciate its a nice to have, but it is nice as a pump op to be able to see the incident where possible.

Also with running out 70mm lengths as a covering jet will take a fair amount of water from the appliance before you can find a decent hydrant to supplement. (around 100 litres per 23 metre length).

We have never had flaked lengths in the back.
YES. It just lets you know how old I am.

Would the BA team be carrying Hand Held Radios in a small domestic?

I am not suggesting 70mm we carried 1.75 inch hose which would be 44mm in today’s money.
Title: Access for fire appliances
Post by: kurnal on August 26, 2008, 02:22:53 PM
Quote from: FSO
I remember a quote from John Prescott stating that sprinklers would be mandatory in new builds by 2008. Its a sign of the way things are going. Its only a matter of time.
Who's he? Where is he now? Wasnt he someone whose government  tried

To persuade us all to use public transport while he ran two of the largest cars available?

To embrace a non violent society but was filmed on TV news  thumping someone?

Who said he was trying to free the fire service from racial and sexual harassment but was forced out of office as a result of an affair with his secretary?


I could go on. But everyime I think of him George Orwells Animal farm comes into mind.

I agree we need a National strategy for the implementation of  domestic sprinklers. The research work overseen by the ODPM a few years ago was thought by many to be flawed. I believe sprinklers need to be targetted to protect the lives of those most at risk from fire. We should start with all new social housing and new HMOs, but nobody is brave enough to do it. Instead we just pick on a few unfortunate souls who fall a little outside the guidance in ADB5 and impose sprinklers or dry mains upon them, regardless of risk, cost/benefit or circumstance.
Title: Access for fire appliances
Post by: FSO on August 26, 2008, 02:50:27 PM
Quote from: twsutton
Quote from: FSO
When you say pack sets, do you mean hand held radios?

Yes it would be lovely, but there are only 3 on an appliance. In initial stages of an incident, 1 would be with the BA team, 1 would be with the ECO and the last one with OIC. I appreciate its a nice to have, but it is nice as a pump op to be able to see the incident where possible.

Also with running out 70mm lengths as a covering jet will take a fair amount of water from the appliance before you can find a decent hydrant to supplement. (around 100 litres per 23 metre length).

We have never had flaked lengths in the back.
YES. It just lets you know how old I am.

Would the BA team be carrying Hand Held Radios in a small domestic?

I am not suggesting 70mm we carried 1.75 inch hose which would be 44mm in today’s money.
Generally, yes they would be. The mic and lead on our sets is permanently attached to the facemask. Also the BA comms set can only be used on BA channels.

Also TB1/97 does say that where possible comms should be used.
Title: Access for fire appliances
Post by: FSO on August 26, 2008, 02:56:33 PM
Quote from: kurnal
Quote from: FSO
I remember a quote from John Prescott stating that sprinklers would be mandatory in new builds by 2008. Its a sign of the way things are going. Its only a matter of time.
Who's he? Where is he now? Wasnt he someone whose government  tried

To persuade us all to use public transport while he ran two of the largest cars available?

To embrace a non violent society but was filmed on TV news  thumping someone?

Who said he was trying to free the fire service from racial and sexual harassment but was forced out of office as a result of an affair with his secretary?


I could go on. But everyime I think of him George Orwells Animal farm comes into mind.

I agree we need a National strategy for the implementation of  domestic sprinklers. The research work overseen by the ODPM a few years ago was thought by many to be flawed. I believe sprinklers need to be targetted to protect the lives of those most at risk from fire. We should start with all new social housing and new HMOs, but nobody is brave enough to do it. Instead we just pick on a few unfortunate souls who fall a little outside the guidance in ADB5 and impose sprinklers or dry mains upon them, regardless of risk, cost/benefit or circumstance.
I agree to a point Kurnal.

The dry main idea is silly. I have seen it happen in the past but I do not see what it achieves.

So, you say regardless of risk. Should I be expecting a risk assessment from the new occupants?? Of course not.
You can only assume who is going to move into a property. Of course they might move out in a years time. What happens then???

From my experience in community fire safety, the wealthier families are generally ignorrant towards fire safety placing them at pretty much the same risk to some social housing families.

Lets get it right while its still lines on paper!
Title: Access for fire appliances
Post by: CivvyFSO on September 01, 2008, 11:45:09 AM
Quote from: twsutton
CivvyFSO are you not using ADB Vol 2 to solve a situation in ADB Vol 1.
No. Flats (which this seemed to be talking about) are dealt with in ADB vol 2.

Quote from: twsutton
but it seems to me that the 45M refer to the distance from a fire fighting staircase
Access should be provided for the pump to get within 45m of every point of the projected plan area. (ADB Vol 2 Para 16.2b)

Older versions of ADB had this 45m stopping at the door to the flat.

Don't get me wrong here, I am not arguing that a riser needs to be in place in this instance, I am pointing out  what the guidance document states.
Title: Access for fire appliances
Post by: Tom Sutton on September 01, 2008, 04:03:04 PM
Civvy its a conversion of a coach house into four terraced houses which is under a conservation order. I agree with you it is clear about the 45M in both volume 1 and 2 but why 45M and what happens if you cannot achieve it?

I have tried to find the answers at http://www.bre.co.uk/adb/page.jsp?sid=395 to no avail at the moment
Title: Access for fire appliances
Post by: CivvyFSO on September 01, 2008, 04:32:07 PM
Ah, my misunderstanding sorry. I thought it was 4 flats.

If it is impossible/extremely impractical to acheive then the FRS/BC need to be reasonable in their approach. If the extra risk warrants sprinklers or a riser then those are viable options.
Title: Access for fire appliances
Post by: wee brian on September 01, 2008, 04:40:53 PM
http://www.planningportal.gov.uk/england/professionals/en/1115315762230.html

Scroll down to the B5 queries - not a great help but it may clear a few things up.
Title: Access for fire appliances
Post by: Tom Sutton on September 01, 2008, 07:46:42 PM
Civvy I can understand the res sprinklers but a riser, we are talking about two storey terraced house or do you mean a fire main?