FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Technical Advice => Topic started by: Davro on September 05, 2008, 09:26:04 PM
-
Got to go on a call out next week sometime for this type of panel of which is in fault on a unused zone. Does anybody out there can me tell what the eol module is and where to get one from?
Conventinal system.
-
Got to go on a call out next week sometime for this type of panel of which is in fault on a unused zone. Does anybody out there can me tell what the eol module is and where to get one from?
Conventinal system.
They are not EOL resistors rather EOL units probably (active EOL), can't be ordered only from their manufacturers
-
You may need to contact Cooper company.
-
We get EOLM-1 units from CEF, alternatively try Sunfish Services http://www.sunfishservices.com/ not a cheap eol unit tho (£13.00 ish)
-
We get EOLM-1 units from CEF, alternatively try Sunfish Services http://www.sunfishservices.com/ not a cheap eol unit tho (£13.00 ish)
very good link, Sunfish service deals with various alarm stuff
-
Might be the same as the Kentec eol , worth a try .
-
Might be the same as the Kentec eol , worth a try .
They are very different in appearance, we do not let our lads fit none OEM EOLs etc.
Try explaining that one to the coroner!!! It would be like fitting VW brake pads to a Toyota!
-
Might be the same as the Kentec eol , worth a try .
They are very different in appearance, we do not let our lads fit none OEM EOLs etc.
Try explaining that one to the coroner!!! It would be like fitting VW brake pads to a Toyota!
In this case it's for an unused zone but possible panel damage/malfunction may occur.
-
John
I did say might ,so does that let me off with the coroner ?
-
John
I did say might ,so does that let me off with the coroner ?
Depends on how many people you killed!