FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Technical Advice => Topic started by: Allen Higginson on September 06, 2008, 12:13:57 AM

Title: Extinguishing system in cabinet enclosures.
Post by: Allen Higginson on September 06, 2008, 12:13:57 AM
Just looking an opinion or two - I am currently looking at a proposed extinguishing system protecting cabinet enclosures.The client has already had a solution provided to then using an inert gas system but our guys have raised concerns about using inert because of the discharge pressures involved and possible damage to the enclosures.Their opinion is to use HFC-227ea  on this occasion (our inert gases are either CO2 or nitrogen).
Title: Extinguishing system in cabinet enclosures.
Post by: John Webb on September 06, 2008, 09:44:25 AM
Do the cabinets contain electrical equipment, flammable liquids or....?
How is the discharge initiated?
Title: Extinguishing system in cabinet enclosures.
Post by: kurnal on September 06, 2008, 03:50:00 PM
Before buying any halon replacement system personally I would seek some assurances from the supplier in respect of sustainability should future environmental legislation change.

Other than that reservation, it does offer advantages over the simple inert gases adn particularly over CO2 on computer sytems.

An alternative solution might be to consider oxyreduct by Wagner to cover the room itself rather than the cabinets. Or consider whether,  if staff are on site to act,  early detection may be the answer- such as Vesda sniffing inside the cabinets to detect a fire before it starts?
Title: Extinguishing system in cabinet enclosures.
Post by: Allen Higginson on September 06, 2008, 04:32:05 PM
Thanks for the replies - the cabinets control burners that are on generators that provide power to most of Northern Ireland! Although the voltages involved are low (<12v as they are only control signals) and there is plenty of ventilation within the cabinets they have been surveyed by the parent company and they want automated extinguishing using dertection within the cabinets.These will be on the double knock principle.
I know where you're coming from Kumal in relaltion to 227 and other hfc gases and their longevity but it is an alternative in view of the pressure problems within the cabinets.
TBH we are providing a comparitive quote and it has to be as "like for like" as possible.
Title: Extinguishing system in cabinet enclosures.
Post by: Galeon on September 06, 2008, 11:02:10 PM
Ig 55 ?
Title: Extinguishing system in cabinet enclosures.
Post by: Allen Higginson on September 06, 2008, 11:14:29 PM
Quote from: Galeon
Ig 55 ?
That was our initial plan but we don't do containers less than 80 litre and you can't half fill them - actually,I've contradicted myself there by listening to an "expert" in relation to asset damage.The Sinorix CDT is Ig55 stored at 300 bar but limited to 60 bar at the outlet.The problem I have is the cylinder size.
Title: Extinguishing system in cabinet enclosures.
Post by: Galeon on September 07, 2008, 12:58:34 AM
Pity you cant get to put them outside and pipe it in , apparently it don't freeze either
Title: Extinguishing system in cabinet enclosures.
Post by: Allen Higginson on September 07, 2008, 01:27:07 AM
Quote from: Galeon
Pity you cant get to put them outside and pipe it in , apparently it don't freeze either
The issue is the quantity of gas as we planned to mount/locate the cylinder beside the cabinets.I have been told that you can't half fill a cylinder for the amount that we need (apparantly).
Title: Extinguishing system in cabinet enclosures.
Post by: kurnal on September 07, 2008, 07:16:36 AM
There are several American companies that do these small self contained systems- I was looking at some a while ago and will check my notes tomorrow to see if I recorded the manufacturers.
The most basic was a small 2kg container of halon equivalent connected to a frangible plastic tube that lead round the machine and if the tube melted the gas was discharged. Certainly not double knock and obviously not very sensitive, may be ok once a fire starts and if one shot from one outlet can be guaranteed to flood all areas- my cabinets were multicompartment so I dismissed this and carried on looking. I did see some similar systems that were smoke detector controlled but by then my client had decided to go for detection and manual intervention instead.
Title: Extinguishing system in cabinet enclosures.
Post by: patrickhamblin on September 07, 2008, 07:55:39 PM
I would make three points - if there is 'plenty of ventilation' how will the concentration be maintained for a satisfactory time to meet the requirements of the Design Codes (BS ISO 14520); if the discharge is in such a small cabinet, has the aspect of damage to equipment simply from the discharge been considered and what is being done on detection of a fire to isolate the source (i.e. switch off power) to prevent reignition?
I would prefer to see aspirating smoke detection and good emergency response (assuming the location is permanently manned) rather than extinguishing gas detection in this situation. I believe far less damage would be done.
Title: Extinguishing system in cabinet enclosures.
Post by: Goodsparks on September 09, 2008, 05:08:54 PM
http://www.firetrace.co.uk/products.html

Guys seemed quite helpful when I last dealt with them.

Paul
Title: Extinguishing system in cabinet enclosures.
Post by: Allen Higginson on September 10, 2008, 02:21:59 AM
Quote from: patrickhamblin
I would make three points - if there is 'plenty of ventilation' how will the concentration be maintained for a satisfactory time to meet the requirements of the Design Codes (BS ISO 14520); if the discharge is in such a small cabinet, has the aspect of damage to equipment simply from the discharge been considered and what is being done on detection of a fire to isolate the source (i.e. switch off power) to prevent reignition?
I would prefer to see aspirating smoke detection and good emergency response (assuming the location is permanently manned) rather than extinguishing gas detection in this situation. I believe far less damage would be done.
The cabs are probably as secure as any area protected by an inert gas can be (integrity tests N/A) but using IG55 through our system drops the pressure at the point of discharge (ie - nozzle).
I would agree that a VESDA (or equvalent) detection system would be more advantageous in this application as they could decide locally to deploy a portable extinguisher at whatever unit has indicated a smoke detected source.
Shutting the power off isn't a option.
Title: Extinguishing system in cabinet enclosures.
Post by: The Reiver on September 11, 2008, 10:40:42 AM
What size are these cabinets ?

I am thinking along the same lines as Goodsparks here. Automatic but direct attack to fire source rather than total cabinet flood.
Therefore the "high pressure upon release" variable is taken out of the equation. There will of course be some release pressure but nothing  more than you would come across with a hand portable

I am presuming by "possible damage to the enclosures" you are refering to sudden atmospheric expansion upon discharge.
Title: Extinguishing system in cabinet enclosures.
Post by: Psuedonym on September 14, 2008, 06:55:24 PM
There are internal cabinet (server type cabinets, typically 5/6 shelves) enclosure systems out there if its of any interest. Gloria desiged a system many moons ago (it may or may not still be available I haven't checked, sorry): an automatic self contained (Detection and expellant release) Co2 system which was fitted within a cabinet unit designed and manufactured specifically to slide straight into a cabinet. The only "fitting" required was fitting four nuts and screws into the cabinet shelving.
A 2Kg Co2 unit was easily replacable (test/recharge) and any additional internal pressure would be dealt with via the existing cooling fan fitted at the cabinet roof and side vents.
As the co2 was a limited amount (2Kg) the room integrity would not be affected.
Title: Extinguishing system in cabinet enclosures.
Post by: AnthonyB on September 15, 2008, 12:56:03 AM
Not mentioned as a standard UK stock product on Gloria.co.uk, but Gloria does still make them:

 http://tinyurl.com/5da26t   (shortened from the mile long address on gloria.de)

Sadly you need to speak German as UTC got rid of their old (& better) dual language site
Title: Extinguishing system in cabinet enclosures.
Post by: Jeff Gale on September 15, 2008, 12:57:05 PM
Hi further to your question about cabinet protection and leakage from cabinets, i have installed several systems using Firetrace, where the tubing is secured around the inside of the cabinet and the system is discharged by the tubing being "melted" at the hot spot, or is discharged indirectly from nozzles mounted within the cabinet, signalled from a detector(s) within the cabinet. The cylinder can be mounted adjacent to the cabinet and has several different options for type of suppressant.

if its any help I'm in Belfast later this week
Title: Extinguishing system in cabinet enclosures.
Post by: Psuedonym on September 17, 2008, 06:19:42 PM
Quote from: AnthonyB
Not mentioned as a standard UK stock product on Gloria.co.uk, but Gloria does still make them:

 http://tinyurl.com/5da26t   (shortened from the mile long address on gloria.de)

Sadly you need to speak German as UTC got rid of their old (& better) dual language site
Yup, cheers Anthony, thats the chaps I was waffling on about. Just couldn't remember the name though.
Title: Extinguishing system in cabinet enclosures.
Post by: Allen Higginson on September 17, 2008, 11:10:37 PM
Quote from: Jeff Gale
Hi further to your question about cabinet protection and leakage from cabinets, i have installed several systems using Firetrace, where the tubing is secured around the inside of the cabinet and the system is discharged by the tubing being "melted" at the hot spot, or is discharged indirectly from nozzles mounted within the cabinet, signalled from a detector(s) within the cabinet. The cylinder can be mounted adjacent to the cabinet and has several different options for type of suppressant.

if its any help I'm in Belfast later this week
Cheers bud but third party gear is a bit of a no no with the fatherland!!!
Title: Extinguishing system in cabinet enclosures.
Post by: Nick G on September 30, 2008, 10:41:02 PM
Mr Buzzard - Thanks for suggesting Firetrace (I admit a vested interest!!) Ok - in any case for anyone interested and to make the product as self explanatory as possible without a salesman darkening anybody's doorstep we have uploaded videos for different "in-cabinet" solutions to Youtube. so go to www.youtube.com and just search for "Firetrace" and you'll find a whole bunch of stuff relating to electrical cabinets, bus engines, wind turbines, vehicles and all kinds of (as the Americans say) "Micro-Enclosures... or local applications... and Firetrace is approved (FM, CE, UL + many others) for use worldwide including ze fatherland!
Title: Extinguishing system in cabinet enclosures.
Post by: Allen Higginson on October 01, 2008, 09:34:28 AM
Quote from: Nick G
Mr Buzzard - Thanks for suggesting Firetrace (I admit a vested interest!!) Ok - in any case for anyone interested and to make the product as self explanatory as possible without a salesman darkening anybody's doorstep we have uploaded videos for different "in-cabinet" solutions to Youtube. so go to www.youtube.com and just search for "Firetrace" and you'll find a whole bunch of stuff relating to electrical cabinets, bus engines, wind turbines, vehicles and all kinds of (as the Americans say) "Micro-Enclosures... or local applications... and Firetrace is approved (FM, CE, UL + many others) for use worldwide including ze fatherland!
I didn't.