Hi
When you "Scan for Contamination Faults" on the AFP panel it then asks you to "Enter Adjustment Value % of Manufacturers Recommended Limit".
Does anyone know what this setting should be for XP95 devices. If the setting is left at 00 the contamination level is at 34.
I have spoken to C-Tec and Apollo and they were no help at all. Cheers
-
Sounds like a good reason not to use this equipment to me.
-
Here here !!
Although when asking for % levels wouldn't the panel determine the % range from the standard 'normal' analogue levels for Apollo.
Generally an Apollo Optical detector will sit fine at a reading of 34, generally anything from 28-40 is fine.. if it falls below around the 28 mark it may go into a fault condition.... If the detector reading was starting to creep above 40-45 mark, I would think about cleaning the detector.
therefore the % level would be that out of Apollo's so called norm.. Would be worth entering, say 20% and see which detectors are highlighted then checking these analogue values.
Incidentely.. the Apollo reading of 34 may not necessarily mean 34%.. it's just the analogue value determined by the Apollo protocol.
-
Further to Big Fella's concise answer , I cant see why Apollo didn't have an answer , as this panel would have been on their approved list , this function is merely the same as putting a loop tester on the wiring , I think their loop tester may have had something to do with control equipment way back .
The man who I always speak to is Andy Haynes at Apollo who is first class , try and see if you can get him.
-
Further to the Apollo analogue values the given value for the detectors is 25 +/- 7.
-
Here here !!
Although when asking for % levels wouldn't the panel determine the % range from the standard 'normal' analogue levels for Apollo.
Generally an Apollo Optical detector will sit fine at a reading of 34, generally anything from 28-40 is fine.. if it falls below around the 28 mark it may go into a fault condition.... If the detector reading was starting to creep above 40-45 mark, I would think about cleaning the detector.
therefore the % level would be that out of Apollo's so called norm.. Would be worth entering, say 20% and see which detectors are highlighted then checking these analogue values.
Incidentely.. the Apollo reading of 34 may not necessarily mean 34%.. it's just the analogue value determined by the Apollo protocol.
The practical normal analogue value reading for Apollo optical detector, I have seen up till now is 23-24 this is not within the tolerance 28-40 as you said, and the panels wasn't in fault condition! as far as I have been aware
Also 16 constant reading for MCPs.
What do you think?
-
That's what Buzz said 25 up + & - 7 so there is no issue with the reading you have got , agree mcp @ 16 so is sounders and ancillary devices , 4 being fault.