FireNet Community
FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Technical Advice => Topic started by: Ashley Wood on September 30, 2008, 08:04:39 AM
-
I am doing an FRA of a cold storage facility in a couple of week’s time. One of the areas is an ammonia plant room. Has anyone any experience either from the FRA point of view or the operational point of view? If anyone has done an FRA of a similar facility and would like to share the bit about the ammonia plant room with me, that would be great. I am assuming that the ammonia is NH3?
-
Yes, it is. You might find the following paragraph useful:
The combustion of ammonia in air is very difficult in the absence of a catalyst (such as platinum gauze), as the temperature of the flame is usually lower than the ignition temperature of the ammonia-air mixture. The flammable range of ammonia in air is 16–25%.
-
Thanks Big A, What fire fighting equipment would you expect to find?
-
Hi Ashley
Take a look at these links, may be of some use to you
http://www.hpa.org.uk/webw/HPAweb&Page&HPAwebAutoListName/Page/1158313434449?p=1158313434449
http://www.hse.gov.uk/risk/casestudies/pdf/coldstorage.pdf
-
Thanks Recard, most helpfull.