Have a gas boiler in a small room approx. 3sq.m, to heat a shop/commercial unit. The room is 60 min fire resisting construction with FD60S door and heat detector. There will be a passive wall vent in the external wall. BS5588 suggests that smoke venting is required from a boiler room, but doesnt say what type/size it should be. Do I have enough safety provisions here? Do you think I need to provide an automatic smoke vent or suppression system?
Thanks
-
Sounds a bit over the top to me.
-
Sounds fine as it is- many boilers are quite safely installed on the wall of the premises they serve without being enclosed in a fire resisting compartment. Depends on the size of the installation and the use of the premises.
Main thing is not to allow combustible storage to accumulate in the boiler room- out of sight out of mind.
-
Have a gas boiler in a small room approx. 3sq.m, to heat a shop/commercial unit. The room is 60 min fire resisting construction with FD60S door and heat detector. There will be a passive wall vent in the external wall. BS5588 suggests that smoke venting is required from a boiler room, but doesnt say what type/size it should be. Do I have enough safety provisions here? Do you think I need to provide an automatic smoke vent or suppression system?
Thanks
Bear in mind that oil burners on fire would produce more smoke than a gas burner which would produce very little other than that from any surrounding combustibles.
-
But they may explode blowing the whole building to kingdom come
-
Hello Muggins
You would not require any additional precautions over and above those you have already mentioned . Smoke vent / supression system would certainly not be required.
-
Thanks for your help
-
I see boiler rooms day in and day out and can't remember any that has smoke vents.
A 60 minute compartment with fire detection sounds pretty good to me.
-