I have a scenario where an L1 system is being proposed for a school, which is fine.
The school is split on two levels, where one end of the school goes up full height of the building i.e. the corridor is 7 metres high, and has glazed roof lights in the roof of this corridor providing natural light. The roof lights are 2.5 m2 and are approx 2 metres in depth.
Is there a requirement to provide automatic detection within the roof lights or will detection on the underside ceiling suffice?
Many thanks in advance.
-
to the standard any rooflight over 800mm in depth.
-
As Graeme says, detection is required in 'lantern lights' over 800mm in depth but also in any lantern light (less than 800mm in depth) also used for ventilation.
-
Thanks guys. Good definitive answer. I shall apply this.