FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Technical Advice => Topic started by: Benzerari on March 26, 2009, 12:59:51 PM

Title: FAS with two different levels of protection !
Post by: Benzerari on March 26, 2009, 12:59:51 PM
In a building of two separate entrances and two back exits as well, one for each part, (left side and right side), the whole building is covered with one single conventional system, the right side of the building is covered with M system, only manual call points where there are a theater and many officies including common area..., the left side of the building is covered to L2 system, with quite the same surface as the right side. the other issue is that the panel has 2 zones, but only one zone used for the whole site, it's about (50m*100m)

Does that sounds OK? or the building has to be re-assessed?
Title: Re: FAS with two different levels of protection !
Post by: kurnal on March 26, 2009, 03:19:58 PM
Theres nothing necessarily wrong provided the coverage and protection delivered by the fire alarm is appropriate to the particular scenario.

If there is adequate  fire compartmentation between the two parts and an M system is appropriate to the way one side of the building is used, and if a fire in this side cannot affect the safety of persons in the other side then it may be ok. It really needs a risk assessment to confirm this though.
Title: Re: FAS with two different levels of protection !
Post by: Benzerari on March 26, 2009, 05:24:54 PM
But what about the zoning?
Title: Re: FAS with two different levels of protection !
Post by: Big_Fella on March 26, 2009, 06:36:10 PM
2000m2 is maximum recommended for a zone... Would need to look at the exact size per zone, but looks like they may go over this
Title: Re: FAS with two different levels of protection !
Post by: kurnal on March 26, 2009, 06:39:41 PM
Yes. good point about the zones, missed that on first reading. That makes it crazy - apart from the size of the zones if different occupiers have been put in the same zone.Dont suppose its addressable?. 
Title: Re: FAS with two different levels of protection !
Post by: Graeme on March 26, 2009, 06:45:44 PM
conventional
Title: Re: FAS with two different levels of protection !
Post by: Benzerari on March 26, 2009, 07:44:52 PM
conventional

Indeed; very old fire sense 2 zones conventional panel, only one used for the whole site!
Title: Re: FAS with two different levels of protection !
Post by: Allen Higginson on March 26, 2009, 08:58:06 PM
It was initially an M category system so the zone could go up to 10000m2 then the smokes were added afterwards?
Maybe the detectors were meant to be on their own zone (which as it is only covering half could be around the 2000m2 mark) and the MCP's on their own zone and someone made a boo boo?
Title: Re: FAS with two different levels of protection !
Post by: Graeme on March 26, 2009, 09:56:11 PM
or maybe it was done by a sparky...that's usually the case when it's wrong.
Title: Re: FAS with two different levels of protection !
Post by: Allen Higginson on March 26, 2009, 11:57:21 PM
or maybe it was done by a sparky...that's usually the case when it's wrong.
Now,now Graeme!!!
Title: Re: FAS with two different levels of protection !
Post by: Benzerari on March 27, 2009, 10:36:11 AM
It was initially an M category system so the zone could go up to 10000m2 then the smokes were added afterwards?
Maybe the detectors were meant to be on their own zone (which as it is only covering half could be around the 2000m2 mark) and the MCP's on their own zone and someone made a boo boo?


That's good guess, as the left side of the building has new install stuff; trunkings, detectors and MCPs, while the right side has old MCPs and hidden cabling.

Fully comprehensive contract, not sure who should pay to put it right
Title: Re: FAS with two different levels of protection !
Post by: Graeme on March 27, 2009, 12:22:16 PM
if it is recent work then in an ideal world whoever done it should but i would put money on that unless the customer is willing then no one and it will probably never get done.
Title: Re: FAS with two different levels of protection !
Post by: Benzerari on March 28, 2009, 11:33:00 AM
if it is recent work then in an ideal world whoever done it should but i would put money on that unless the customer is willing then no one and it will probably never get done.

It isn't a recent work but we took over the site for maintenance..., also the main panel is in the side of the manual system..., Buzz's guess is likely to be right.