Title: Kidde 24 zone panel fault
Post by: Davo on August 03, 2009, 03:06:17 PM
Fellow Posters

The above panel, 4 years old, shows common fault and system fault lit, also system normal on front display
I tried to interrogate but nothing happened
I looked inside, two yellow LEDs flashing, Host RX and Host TX

Am told the panel is u/s

Can anyone please enlighten me as to the problem?

thanks

davo


ps is it usual to join internal electric feeds to panel wiring by twisting and covering with Denzo?

davo
Title: Re: Kidde 24 zone panel fault
Post by: Galeon on August 03, 2009, 07:49:27 PM
Comms error , do you have a repeater ? , denzo once had a mate called that.
Title: Re: Kidde 24 zone panel fault
Post by: Davo on August 04, 2009, 08:51:50 AM
Galeon

Actually, yes, haven't looked at it though
Its a large building, three floors, several hundred devices

davo
Title: Re: Kidde 24 zone panel fault
Post by: Allen Higginson on August 04, 2009, 09:34:33 AM
If the display is showing healthy then there is a chance that there has been a fault but it has cleared.
Try pressing SW2 on the MCP card (back of the door) to clear the System Fault.
It's a VEGA for future reference by the way - you could try and talk to KIDDE themeselves as I always find their tech support great compared to a lot of others.
Title: Re: Kidde 24 zone panel fault
Post by: Davo on August 04, 2009, 02:46:27 PM
Buzzard905

Pressed the system fault reset  and all is well, thanks
Looks like you were right :D

davo
Title: Re: Kidde 24 zone panel fault
Post by: Allen Higginson on August 04, 2009, 03:23:04 PM
No worries!