FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Technical Advice => Topic started by: Davo on August 03, 2009, 03:06:17 PM
-
Fellow Posters
The above panel, 4 years old, shows common fault and system fault lit, also system normal on front display
I tried to interrogate but nothing happened
I looked inside, two yellow LEDs flashing, Host RX and Host TX
Am told the panel is u/s
Can anyone please enlighten me as to the problem?
thanks
davo
ps is it usual to join internal electric feeds to panel wiring by twisting and covering with Denzo?
davo
-
Comms error , do you have a repeater ? , denzo once had a mate called that.
-
Galeon
Actually, yes, haven't looked at it though
Its a large building, three floors, several hundred devices
davo
-
If the display is showing healthy then there is a chance that there has been a fault but it has cleared.
Try pressing SW2 on the MCP card (back of the door) to clear the System Fault.
It's a VEGA for future reference by the way - you could try and talk to KIDDE themeselves as I always find their tech support great compared to a lot of others.
-
Buzzard905
Pressed the system fault reset and all is well, thanks
Looks like you were right :D
davo
-
No worries!