Am I correct in asking for dry risers to be pressure tested every year and visually inspected 6 monthly? Any views or opinions welcome.
Title: Re: Dry Riser Testing
Post by: AnthonyB on November 06, 2009, 02:29:05 PM
If being maintained as per the current BS, yes.

If you don't follow the BS you need to demonstrate that your alternative regime is suitable & sufficient.