FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Technical Advice => Topic started by: Sherpa on November 12, 2009, 05:21:12 PM

Title: Fire Alarm containment
Post by: Sherpa on November 12, 2009, 05:21:12 PM
Can fire alarm cables (extra low voltage) and PA system cables (low voltage) be run on the same traywork without seperation?
Title: Re: Fire Alarm containment
Post by: Mike Buckley on November 12, 2009, 06:50:42 PM
BS 5839 pt 1 26.2 l

"To avoid electromagnetic interference wth fire alarm signals, any recommendation by the manufacturer of the fire alarm equipment in respect of the seperation of fire alarm cables from the cables of other services shold be followed".

Ask the manufacturer of the cable!
Title: Re: Fire Alarm containment
Post by: Galeon on November 12, 2009, 11:19:12 PM
MICC would not be a problem , soft skinned another story , as per Mikes post.