FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Fire Safety => Topic started by: Mushy on November 13, 2009, 10:05:09 AM

Title: Self closers on bedroom fire doors
Post by: Mushy on November 13, 2009, 10:05:09 AM
Hi

 Junior doctors sleep in 6 bedrooms off a first floor corridor in a hospital...these rooms have recently been past by building control and the fire and rescue service as fire doors with smoke seals and intumescent strips...but no self closers...

me being an old wrinkly I'm used to sleeping accomodation fire doors having S/C's on them!...anyone differ in that view?
Title: Re: Self closers on bedroom fire doors
Post by: CivvyFSO on November 13, 2009, 10:18:30 AM
I would agree with you. In the event of someone leaving a room that is on fire we need the door to close behind them.
Title: Re: Self closers on bedroom fire doors
Post by: kurnal on November 13, 2009, 12:21:45 PM
Yes its a historical thing. Prior to the late 1980s it was convention not to put self closers on bedroom doors where there was two way travel in the corridor, only dead ends were protected. But then lives were lost in a  hotel fires where the room occupant- a member of staff - fled his room leaving the door open. As a result the convention changed towards closers on all bedroom doors. 
Title: Re: Self closers on bedroom fire doors
Post by: wee brian on November 13, 2009, 01:02:51 PM
Theres some get out clauses in the HTMs for bedroom doors.

They are intended for patient rooms I don't think it's right to apply them to staff accom.
Title: Re: Self closers on bedroom fire doors
Post by: Bobbins on November 13, 2009, 03:12:37 PM
If it is not to a store room or service cupboard ie 'kept locked', then it needs a closer to be considered a fire door; for obvious reasons it must self close when used in the event of a fire. (as others have pointed out.)
Title: Re: Self closers on bedroom fire doors
Post by: Rex on November 13, 2009, 05:59:29 PM
Hi

 Junior doctors sleep in 6 bedrooms off a first floor corridor in a hospital...these rooms have recently been past by building control and the fire and rescue service as fire doors with smoke seals and intumescent strips...but no self closers...

me being an old wrinkly I'm used to sleeping accomodation fire doors having S/C's on them!...anyone differ in that view?

Mushy,
You are correct, HM Government Heathcare Premises Guide is applicable, from another wrinkly,
Title: Re: Self closers on bedroom fire doors
Post by: Clevelandfire 3 on November 13, 2009, 07:24:51 PM
If you cant guarantee that a fire door will be maintained in the closed position during a fire you need self closers, some so called experts will argue with that and think you can risk assess it out and that people will remember to close fire doors. Thats fine, if they can personally say that staff will have the presence of mind to close the door behind them in the event if fire, and are so sure about it that they will put their money where there mouth is and agree to pay me £30,000 if they don't then I'll go along with it.  What do you say to that Mushy
Title: Re: Self closers on bedroom fire doors
Post by: wee brian on November 16, 2009, 09:41:56 AM
Nice, well reasoned argument.
Title: Re: Self closers on bedroom fire doors
Post by: Mushy on November 17, 2009, 09:45:49 AM
well Clevelandfire...who can argue with that... this was passed by building control in consultation with the fire authority...how I'm not sure!

"and agree to pay me £30,000 if they don't then I'll go along with it"

only 30 grand?
Title: Re: Self closers on bedroom fire doors
Post by: wee brian on November 17, 2009, 01:14:09 PM
Para B2 Page 54 0f HTM 05-02

"With the exception of fire doors to patients' bedrooms in mental health accommodation, and doors which are kept locked shut, fire doors should be fitted with an automatic self closing device....."

So they would need closers.  I thought the exemption went further but that's what the book says.
Title: Re: Self closers on bedroom fire doors
Post by: FSO on November 17, 2009, 05:54:46 PM
I presume it is not sprinkerled?
Title: Re: Self closers on bedroom fire doors
Post by: CivvyFSO on November 18, 2009, 12:00:05 AM
Oh don't you dare start with that one again!


;)
Title: Re: Self closers on bedroom fire doors
Post by: Mushy on November 18, 2009, 09:36:18 AM
Para B2 Page 54 0f HTM 05-02

"With the exception of fire doors to patients' bedrooms in mental health accommodation, and doors which are kept locked shut, fire doors should be fitted with an automatic self closing device....."

So they would need closers.  I thought the exemption went further but that's what the book says.

well wee brian

I can tell you that the ward bay doors at this hospital are fire doors but don't have self closers on
Title: Re: Self closers on bedroom fire doors
Post by: Davo on November 19, 2009, 11:36:23 AM
Difficult moving beds whilst holding open against closers ;D

davo
Title: Re: Self closers on bedroom fire doors
Post by: Colin Newman on November 19, 2009, 05:24:05 PM
HTM 81 para B2 didn't include the "in mental health accommodation" qualification and merely referred to patient bedrooms in the exclusion of door closers.
Title: Re: Self closers on bedroom fire doors
Post by: wee brian on November 19, 2009, 07:28:20 PM
Cheers Colin

My grey cells weren't completely letting me down then. That slipped in quietly, or was I just not paying attention?

My recollection was that door closers were considered to be more trouble than they were worth for patient rooms. There must have been a change of heart.



Title: Re: Self closers on bedroom fire doors
Post by: Colin Newman on November 19, 2009, 07:39:03 PM
I have no idea why the qualification was introduced.  It doesn't really make much sense when you consider that the justification for excluding door closers from patient bedrooms as per HTM 81 was to assist patient evacuation! 

I'm not aware that evacuating patients from bedrooms other than those in mental health accommodation has become any easier than was the case in 1996 when HTM 81 was published.  ???
Title: Re: Self closers on bedroom fire doors
Post by: Mushy on November 20, 2009, 11:02:32 AM
I've recently been involved in a training session full evacuation of a 19 bed ward with individual bays and can tell you it would have been a hindrence with closers on the doors. I think the theory is (was) that the wards are manned (womaned) 24/7 so any fire in a bay would be detected early and the staff are trained to close doors once evacuated...and thats what happened in this case

but for doctors quarters away from the wards that is a different thing altogether
Title: Re: Self closers on bedroom fire doors
Post by: wee brian on November 20, 2009, 04:12:22 PM
Agreed, I'd buy you a pint but........