FireNet Community

FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Fire Safety => Topic started by: GB on August 09, 2010, 01:52:42 PM

Title: Ancilliary Accommodation
Post by: GB on August 09, 2010, 01:52:42 PM
What is the definition of ancilliary accommodation as ADB Volume 2 2.30?

Does it include service risers?

Title: Re: Ancilliary Accommodation
Post by: CivvyFSO on August 09, 2010, 02:47:13 PM
No.

It would be easy to get confused here, look in appendix D for more info on ancillary use. However, I think for this particular problem you need to look no further than a dictionary, which gives the explanation of "something of secondary importance"

The service risers are a necessary and accepted part of the residential purpose group. (They are of primary importance for the functionality of the place, just like the common corridors and staircases.) Storage cupboards would be of secondary importance, i.e. The flats could function perfectly well without them.

The service risers should obviously be fire protected, but the particular comments in B1 regarding ancillary areas and where they can open up onto, should not need to be applied.
Title: Re: Ancilliary Accommodation
Post by: GB on August 09, 2010, 05:31:04 PM
Many thanks Civvy - some times can't see the wood from the trees!!
Title: Re: Ancilliary Accommodation
Post by: GB on October 11, 2016, 01:44:39 PM
Following on from my original post in 2010 (where has time gone!!) BS 9991 Section 37 states that ancillary accommodation includes engineering services e.g. Gas services; electrical services; communal heat / vent etc - so when does a service riser become ancillary accommodation?

Is it size or use?

If use, then basically all service risers could be classed as ancillary accommodation as BS 9991.

I would be interested in the thoughts of the forum.