Hi I realise this is a very big subject however my question is this:
Within my workplace we have a number of small storage rooms of various sizes in order to ensure correct function of the installed sprinkler system ( ceiling heads ) we would like to enforce a minimum clearance distance between the stock within the rooms and the sprinkler heads. I have came across all different figures depending on what the stock is.
Can any one provide some advice/guidance I have trolled through BSEN12845 although it is quite a comprehensive document
Much appreciated
-
Take a look at section 12.1.2. page 75.
Generally its 500mm for OH and 1000mm for High Hazard and ESFR.
-
Hi Kurnal Thanks for the reply
12.1.2 A clear space shall be maintained below the deflector of roof and ceiling sprinklers of at least:
a) for LH and OH:
0,3 m for flat spray sprinklers;
0,5 m in all other cases.
I did come across this however the wording below the " deflector " left me rather confussed ??
excuse my ignorance and I to assume that the deflector & sprinkler head are the same
Much appreciated
-
I would say that the deflector is the plate that spreads the water stream after it leaves the head
|______| - where the head screws into the pipe
/ \
| | - arms with bulb/fusible link in
\ /
\ /
|___| - deflector plate
so that you measure clearance from the appropriate point.
-
Sprinklers can be pointing up (Upright) or down (Pendent) so there can a significant difference in the position to measure distance from. As it is the deflector plate that spreads the spray that's why measurements have to be made to it. The clearances are to ensure the spreading water from a head is not intercepted by the stored goods before it has finished spreading, if you follow me!
-
Thanks for the advice/guidance