FIRE SAFETY => Fire Alarm Systems => Topic started by: kurnal on September 30, 2011, 01:32:12 PM

Title: Detectomat SRC 3000
Post by: kurnal on September 30, 2011, 01:32:12 PM
Came across one of these very pretty, very compact addressable, radio linked fire alarm systems in a shop in Exeter yesterday.

It has multi sensor heads/ sounders but these appear to be powered solely by a PP3 battery without backup supply. The whole thing appears to be of German origin yet has no EN54 or DIN badges or anything else for that matter.

The manufacturers and importers websites do not reveal any further details of non compliance with EN54, I found some comments on the fire engineers forum that their fault monitoring and reporting do not conform, does anybody know the full story?

Oh just to add icing to the cake it was connected to the Landlords  rafiki sita 200 system that the landlord said was in permanent fault mode.....
Title: Re: Detectomat SRC 3000
Post by: John Dragon on September 30, 2011, 09:09:02 PM
When queried, the distributor told me that they were aware that they did not comply and that it did not matter!

They make a big thing of being "approved by the fire brigade"  (please discuss!!!)

One of our customers has had one fitted (instead of the wired addressable we recommended) and they absolutely hate it, they have twice called us out to silence and reset it (shows how often they test it), as they cannot do it themselves!

Takes ages to silence the sounders and often fails to silence all of them.

The certification given by the installers states that it complies with 5839 part 1.

We decided not to use them!



Title: Re: Detectomat SRC 3000
Post by: colin todd on October 01, 2011, 10:48:44 PM
Kurnal,  you should be american.  It took them a couple of years to discover world war 2.  These have been around for yonks. They are as described above and do not comply with BS 5839-1. People get confused because it is claimed (and probably rightly) that there is compliance with EN 54 (relating to the CIE).

With regard to "approval" of the FRS, yep several have been convinced it is great and there are even documented success stories to prove it (one a bakery as I recall).  One FRS has even promoted presentations on the product to other FRS.  One to whom it promoted asked if the system had been run by a fire alarm specialist and was told siniffily that it had been reviewed by about 8 FRS and so certainly did not need any more review than that.  I remember writing at the time to a chum in the FRS that my old mother used to say that a little education is a dangerous thing, and that my recollection is that she emphasised the word "little". was
Title: Re: Detectomat SRC 3000
Post by: kurnal on October 01, 2011, 11:00:58 PM
Hi Colin
No the Manufacturers do not make any mention of EN54 in respect of the panel or the detectors as far as I can see. They quote EN54 in respect of the break glass call points.

Title: Re: Detectomat SRC 3000
Post by: AnthonyB on October 02, 2011, 02:14:27 AM
There were a glut of brigades that loved it, but I believe a couple are not accepting them now they are clued up on the non conformities.

Not come across one yet fortunately, wasn't impressed when given a demo at Firex a few years ago (esp as it didn't work very well!)
Title: Re: Detectomat SRC 3000
Post by: Midland Retty on October 03, 2011, 02:50:37 PM
I've come across similar products. Whilst I would not advocate them as a viable replacement for more pukka systems, they could be considered useful as an interim measure.

Example being a landlord friend of mine. He keeps battery powered radio linked detectors on standby in case any of his mains powered alarms go down in his HMO portfolio. Thats a sensible idea as far as Im concerned.
Trouble is however that a pack of 8 radio link detectors cost £500
Title: Re: Detectomat SRC 3000
Post by: Big_Fella on October 04, 2011, 12:34:45 PM
As far as I was aware BS5839 states that all radio linked components should be supplied from at least two independant power supplies (e.g. primary & a secondary battery source).

To comply with the relevent section of EN54 only one supply is required.

Therefore to sign off a BS5839 certificate, the radio linked devices should contain a secondary battery source, or this should be a variation on the certificate??

Would be interested to know what building this is referring to Kurnel, as I'm only a stones throw away from Exeter.
Title: Re: Detectomat SRC 3000
Post by: nearlythere on October 05, 2011, 08:32:13 AM
Just as a matter of interest does a variation on a certificate make everything suddenly compliant?
Title: Re: Detectomat SRC 3000
Post by: kurnal on October 05, 2011, 09:36:15 AM
No but it shows that the variation is acknowledged and not a mistake or omission.

The crux of this case though is that the manufacturers do not appear to  make any claims of compliance with EN54 (despite the Construction Products Directive) or BS5839 and the installers do not issue any certificates under BS5839. (Despite using the BAFE logo on everything they are actually only registered with BAFE to maintain fire extinguishers). Interesting though that they did issue a maintenance certificate of their own format stating that their last maintenance was carried out in accordance with  BS5839-1.
Title: Re: Detectomat SRC 3000
Post by: kurnal on November 06, 2011, 01:50:01 PM
Following questions from me the installers have now provided the client with a full 5839-1 installation and commissioning cert showing L1 protection and no declared variations except for a statement that the system is radio linked. Hmm. That will be interesting when we meet them on site in a couple of weeks time.

Theres editorial in this months fire risk management magazine desribing the installation of one of these systems in an old building and the editorial describes the system as "reliable". Should such publications allow paid for editorial in this way without checking  that products conform to apporpriate standards?
Title: Re: Detectomat SRC 3000
Post by: John Webb on November 06, 2011, 03:12:45 PM
.........Theres editorial in this months fire risk management magazine desribing the installation of one of these systems in an old building and the editorial describes the system as "reliable". Should such publications allow paid for editorial in this way without checking  that products conform to apporpriate standards?

The installation mentioned above by kurnal is a grade 2 listed farmhouse and the installation is to conform with English Heritage requirements, although it does not say what the why or wherefore of these requirements are. There is no information on the occupational status of this building which may be a private dwelling. So I suspect there is no compulsion to use a system compliant with BS 5839.
From the comments about this maker's equipment in this topic perhaps in a year's time the the adjective 'reliable' may need revision?
I don't have any problem with such items appearing under 'Trade News' as this one does, but I will always be ready with questions if need be. And of course this Forum is always ready to shine a critical spotlight on things!
Title: Re: Detectomat SRC 3000
Post by: colin todd on November 06, 2011, 11:17:31 PM
If there are not two batteries it IS a variation. If a variation is agreed by ALL interested parties and recorded then the system  complies.  However, who would be stupid enough to agree to one battery-(other than purveyors of one battery systems and those fire and rescue services who chose to endorse it and recommend it to their other fire and rescue service chums- I think I will start endorsing red lorries, I know nothing about them, other than that there is a gear box and engine, but, with that knowledge and a read of sales literature and a presentation by a lorry salesman, that surely qualifes me as an expert). 
Title: Re: Detectomat SRC 3000
Post by: kurnal on November 07, 2011, 10:04:31 PM
I have been shown a document produced by the UK distributor of these systems which indicates that their intention is to place the system in the marketplace as an equivalent level  to a  BS5839 part 6 grade C system, ie domestic premises and perhaps, subject to the findings of a fire risk assessment, very small commercial settings. Even then the detector isreally grade F. (Thanks Dave)
So it appears that the problem is the installation of the system in commercial premises by extinguisher maintenance companies without any knowledge or fire risk assessments being undertaken. It is marketed on   cost. I have come across two and maybe  three of these companies now, all using the BAFE logo  and name on their marketing and fire alarm certificates but  none of whom is accredited under SP203.

They are acredited to SP104/ST101 for fire extinguishers.I will report them to BAFE- and will wait with interest to see if any action is taken.
Title: Re: Detectomat SRC 3000
Post by: kurnal on December 01, 2011, 10:33:30 PM
As an update we had a meeting with all parties on site last Monday. Apart from the known issues with the detectomat system I tested the system by operating a call point and found an even bigger concern. It was a full 30 -40 seconds before most of the sounders operated. The detector sounders gradually started one by one. As we know, BS5839-1 recommends a maximum delay of 4 seconds from operating a call point.

The contractors, installers and shop fitters bluffed and blustered but the client was horrified and told them to install a proper system.

What also makes it worse is this system is providing L3 adjacent room protection to the escape from a single staircase office building above.
Title: Re: Detectomat SRC 3000
Post by: colin todd on December 08, 2011, 12:16:37 AM
Sigh- not 4 seconds big al. 3 seconds. (what am I to do with you).  You should also have tried silencing and finding out what delays occur.

If you have time over xmas, I need something to make metal boxes move under the power of something I am inventing called an engine.  Could you possible invent something, lets call it say a wheel as a working title. If you invent one be sure to tell everyone about it and they can produce motor cars. Lets work together on this as I believe some guy called henry is doing the same in America and we ought to try to be first.
Title: Re: Detectomat SRC 3000
Post by: kurnal on December 08, 2011, 12:52:54 AM
Well your resolution to be nice to me did not last long did it. And after I was singing your praises today to Mr Ince. Oh well at least your mentioning Mr Ford  gives me chance to remind you of that jolly fine motor car that emerged from Linwood in the sixties and seventies - the Hillman imp.

The Glaswegian workforce, who were mainly recruited from the shipbuilding industry were not versed in the intricacies of motor vehicle assembly, and Imp build quality and reliability suffered accordingly.  So lets not do any more re- inventing please.
Title: Re: Detectomat SRC 3000
Post by: nearlythere on December 08, 2011, 08:05:35 AM
Does proper accreditation really exist? Is it not a members club were they pay a fee to have a logo and a set of numbers on websites and letter heads to give the gullible the illusion of rigidly monitored and regulated expertise?

I know of a fire risk assessor (an expert by attending a short course with an end certificate) who asked my preferred installer what a L1 fire alarm system meant. An engineer who works for the same outfit has installed a fire alarm system with twin and earth cabling. Accreditation logos and numbers are overflowing their website, letter heads and invoices.
Title: Re: Detectomat SRC 3000
Post by: Tom Sutton on December 08, 2011, 10:13:59 AM
CT I would tell every everyone aout as well.
Title: Re: Detectomat SRC 3000
Post by: David Rooney on March 05, 2012, 11:57:42 AM
did you ever get anywhere with this Kurnal ? .... I only ask as I notice Mr Leigh is holding a seminar at Firex .... it's almost worth going just for the laugh.....
Title: Re: Detectomat SRC 3000
Post by: kurnal on March 05, 2012, 12:38:44 PM
Yes after much controversy and hoo hah following my fire risk assessment report in which I dared to question the quality of the alarm system I was summoned by the client to a council of war at the site. I was met by a gang of about 12 interested, mostly hostile folk. I explained my concerns and these were dismissed by the installers so I asked them to give a demonstration to show how well the alarm performed. We set off a call point at the main entrance to the shop and I took the client down into the basement. It was at least 40 seconds before any sounders operated in the basement.  The client went spare, told the installers to take it out and to put in a proper alarm system. He apologised for dragging me down,  paid my expenses and asked me to carry out  fire risk assessments throughout the rest of his chain of shops. So all ended well in the end.  
Title: Re: Detectomat SRC 3000
Post by: David Rooney on June 14, 2012, 02:03:34 PM
Top stuff !!