FireNet Community
FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Fire Safety => Topic started by: Visitor on August 01, 2005, 03:13:33 PM
-
Can anyone point me to legistalative / guidance documents for the storage of small quantities of petrol / generator fuel etc within a warehouse environment.
-
- The petroleum Consolidation Act 1928
- The highly flammable liquid and liquefied petroleum gas regulation 1972
- The Health and Safety at Work Act
- The Fire Precautions (Workplace) Regualtions
- Note CS4 from the HSE
- LPC Recommendation For the Storage and Use of Flammable Liquid - Data Sheet RC20
In summary and in my opinion, quantities less than 50 litres can be kept inside a building if they are kept in suitably design cabinets. The cabinets should comply with the 1972 act - in summary be of robus construction, resist accidental damage and be of at least 30 minutes fire resistance.
Within the cabinet the petrol should be within a closed non combustible container (not glass).
You should never have more than a days supply inside.
The rules for diesel are less strict than for petrol.
Please also be aware of your insurers requirements.