I am finding numerous premises with plastic drainage pipes which penetrate floors and ceilings. Where these are enclosed at both levels I would be happy but I have recently found soil pipes in a hotel which go from a bedroom down into a garage. The bedroom has FD 30S door and there is L2 AFD.
I would appreciate views and opinions of colleagues on whether they would expect intumescent collars or similar in this and similar instances.
-
Jakespop Have you considered the guidance in Approved Document B3- section 10 ?
-
Have a look at the ASFP guide for risk assessors - you'll find some useful stuff in there
-
I think that if you use approved document Part B you want Section B3, Table 3, for pipes passing through a fire separating element.