THE REGULATORY REFORM (FIRE SAFETY) ORDER 2005 => Q & A => Topic started by: K Lard on February 13, 2014, 03:58:51 PM

Title: Dorgard (Again?)
Post by: K Lard on February 13, 2014, 03:58:51 PM
Would anyone accept Dorgards to a staircase in an office environment (Ground & first floor only) where there is no detection (category M only) and there are three staircases? They were probably installed prior to 2007 when BS 7273-4 came out.
Title: Re: Dorgard (Again?)
Post by: kurnal on February 13, 2014, 05:17:46 PM
No I would see smoke detection on both sides of all doors controlled by the Dorgard as a minimum in all cases.
Title: Re: Dorgard (Again?)
Post by: AnthonyB on February 13, 2014, 08:47:41 PM
No, far too much chance of fire (or more importantly smoke & combustion products) spreading unnoticed through the open doors. Even the original auto release doors had to have local AFD decades ago, there is no reason not to keep the same principle now.
Title: Re: Dorgard (Again?)
Post by: wee brian on February 14, 2014, 12:44:41 PM
ditto - must have detection
Title: Re: Dorgard (Again?)
Post by: K Lard on February 14, 2014, 01:22:44 PM
Thanks for that - it’s mirrored my own thoughts. Looks like it’s a minimum of a category M/L5 with detection along the whole of the corridor and one detector in the landing (To satisfy the BS). Don’t know whether they will go for that - if they take the Dorgards off they will end up being wedged open leaving them worse off.

A bit of history – in 2003 CACFOA recommended that a detector either side of the door would not be sufficient (Extract):

‘The practice of using dedicated smoke detectors either side of corridor
doors that are to be held open by a door release mechanism should be
discontinued. This is because studies have found that smoke entering the
corridor from an adjacent room may not have sufficient buoyancy, movement
and directional flow to actuate the dedicated detector heads.’

Title: Re: Dorgard (Again?)
Post by: colin todd on February 14, 2014, 03:01:51 PM
Big Al,  Lumpa is right. Detectors either side of the door went out with the 4 pennies in the Bathmat Lock phone box (now sadly destroyed by vandals) to send the stop message to the Derby and Joan control.  Have you been too busy answering everyone's questions to do your CPD Big Al.  Try BS 7273-4 and dont worry about what a bunch of fireman said on behalf of CFOA.  They never did understand the subject of door release.  I liked it when they were called CACFOA as the first three letters reflected their output.
Title: Re: Dorgard (Again?)
Post by: kurnal on February 15, 2014, 09:15:28 PM
Big Al,  Lumpa is right. Detectors either side of the door went out with the 4 pennies in the Bathmat Lock phone box (now sadly destroyed by vandals) to send the stop message to the Derby and Joan control.  Have you been too busy answering everyone's questions to do your CPD Big Al.  Try BS 7273-4 and dont worry about what a bunch of fireman said on behalf of CFOA.  They never did understand the subject of door release.  I liked it when they were called CACFOA as the first three letters reflected their output.


Have it your own way Colin but I reiterate that my simple answer to the question posed still stands good -  smoke detection on both sides of all doors controlled by the Dorgard is always required. 

Whether that detection is provided and sited in accordance with the early CACFOA  guidance  that stood us in good stead for so many years  or provided and sited  in accordance with BS7273-4 is immaterial to the fundamental question being posed.
Title: Re: Dorgard (Again?)
Post by: Davo on February 16, 2014, 09:42:03 AM
CT

If the smoke rises and sets off the detector, that's good
If the smoke doesn't rise sufficiently, what have you lost by having the detectors????????

davo
fogged up
Title: Re: Dorgard (Again?)
Post by: jokar on February 18, 2014, 08:02:49 AM
and the fire risk in these premises is?  The probability of a fire is minimal, the probability of it not being detected early is minimal and the chance of the escape route being compromised is minimal as well.  Dorguard are acoustic so they will oprate when a person, decent detector, operates the manual call point. 
Title: Re: Dorgard (Again?)
Post by: Mike Buckley on February 18, 2014, 09:50:54 AM
I would agree with jokar, you need to look at the whole building. If the basic brief is a two storey building, ground and first floor, and three staircases. Travel distances, alternative means of escape, interior layout, no sleeping risk? Do they need dorgards at all?

In situations like this I have sometimes suggested hook and eye with the hook fitted upside down, so that it is held in place by friction and if the door is knocked it falls out and the door closes. It stops the door being wedged and in the jostle during a fire evacuation it is easily dislodged and the door will close. OK no good for protected escape routes etc.
Title: Re: Dorgard (Again?)
Post by: kurnal on February 19, 2014, 07:52:31 AM
I have no idea where we are going with this it could easily develop into a pythonesqe living in a cardboard box sketch.

I would agree with jokar that the risk assessment should identify whether fire doors are needed here or not and whether persons would be at risk if they were open in the incipient stages of a fire before the alarm was raised. But beyond that if they are a requirement then they should not be fitted with anything that might prevent them from performing their fire protection role.
Title: Re: Dorgard (Again?)
Post by: David Rooney on February 20, 2014, 12:48:35 PM
7273 pt 4 says....


13.2.4 Where an electrically powered hold-open device is fitted to a fire door between a corridor and a stairway, a Category L5 system
should conform to the following recommendations (see Figure 4).

a) Smoke detectors should be provided in the section of corridor that forms the route to the stairway.

b) At least one of the smoke detectors recommended in 13.2.4a) should be located between 0.5 m and 1.5 m horizontally of the
door opening (see Note 2).

c) A smoke detector should be located on the ceiling of the adjacent landing within the stairway enclosure.


For all the reasons stated above detectors installed either side of the door is no longer acceptable and basically has been proven to be worthless in many circumstances (otherwise the recommendation would still be in place).

If the end user wants doors held open then his fire detection system needs to be up to scratch, it goes hand in hand and is not an "either or".

So why do fire officers / assessors constantly offer and accept watered down compromises on the basis that "something is better than nothing" when "something" - as in detectors either side of the door in this case is clearly non compliant and in practical terms does nothing for the safety of the end user and is therefore a waste of money??

Tell the end user to meet the minimum standards for AFD or put your name (not his) to a variation based on your risk assessment or do away with the dorguards and risk prosecution if he gets caught with a wedgey.
Title: Re: Dorgard (Again?)
Post by: colin todd on February 20, 2014, 07:45:34 PM
Big Al,  I hate to nag you about your CPD, but CFOA changed its advice when you still had a full head of heair and told people that detectors either side of the Door are NOT sufficient.  it was one of the few things that CFOA ever got right (excluding CFOA(S) naturally).  But you are right, that the CORRECTED  advice did stand us in good stead.
Title: Re: Dorgard (Again?)
Post by: kurnal on February 20, 2014, 09:23:19 PM
Thanks for that Dave.
Look the point I was trying to make - clearly unsuccessfully- was that on one side of the door there is a corridor and on the other side of the door there is a staircase. Currently there are no smoke detectors anywhere. If a dorgard is  to be used then there needs to be smoke detectors  covering either side of the door.  However I did not set out to offer design guidance for the OP and did not suggest that the detectors should be part of a system installed in accordance with BS7273-4 or  BS5839 Lx or point detectors within xmetres of the door for that matter as per the original or modified CFOA guidance.  

it was just a simple point simply made. I accept that perhaps I did not make the best choice of words. Perhaps I could learn a lot from Wee B who made the same point but more briefly. Perhaps I should have said detection not detectors. Oh well.

Starting to think this forum has had its day. How do you keep fire engineers so positive?  
Title: Re: Dorgard (Again?)
Post by: nearlythere on February 21, 2014, 10:26:54 AM
Thanks for that Dave.
Look the point I was trying to make - clearly unsuccessfully- was that on one side of the door there is a corridor and on the other side of the door there is a staircase. Currently there are no smoke detectors anywhere. If a dorgard is  to be used then there needs to be smoke detectors  covering either side of the door.  However I did not set out to offer design guidance for the OP and did not suggest that the detectors should be part of a system installed in accordance with BS7273-4 or  BS5839 Lx or point detectors within xmetres of the door for that matter as per the original or modified CFOA guidance.  

it was just a simple point simply made. I accept that perhaps I did not make the best choice of words. Perhaps I could learn a lot from Wee B who made the same point but more briefly. Perhaps I should have said detection not detectors. Oh well.

Starting to think this forum has had its day. How do you keep fire engineers so positive?  

How was your recent trip K? Hope you behaved?
Title: Re: Dorgard (Again?)
Post by: David Rooney on February 21, 2014, 01:32:14 PM
Thanks for that Dave.
Look the point I was trying to make - clearly unsuccessfully- was that on one side of the door there is a corridor and on the other side of the door there is a staircase. Currently there are no smoke detectors anywhere. If a dorgard is  to be used then there needs to be smoke detectors  covering either side of the door.  However I did not set out to offer design guidance for the OP and did not suggest that the detectors should be part of a system installed in accordance with BS7273-4 or  BS5839 Lx or point detectors within xmetres of the door for that matter as per the original or modified CFOA guidance.  

it was just a simple point simply made. I accept that perhaps I did not make the best choice of words. Perhaps I could learn a lot from Wee B who made the same point but more briefly. Perhaps I should have said detection not detectors. Oh well.

Starting to think this forum has had its day. How do you keep fire engineers so positive?  


I wasn't responding to you specifically K ... you're still my hero !

I was rather generalising that authority figures that tend to be accepting of anything they can get rather than telling owners that plead poverty how it should be, and leave us lowly FA designers in the lurch when we tell the client their "£400" compromise is a waste of money ..... except it gets the Fire Officer off their back so maybe it's not ....

We have a 50 bed (2 Star) hotel in Folkestone with virtually no AFD or sounders where allegedly the FO has said he doesn't need 75db at the bed head according to the owner.  ???

The "poor" owner has just sold his other hotel (that's in a similar condition) down the road for a couple of million and returned from 3 months in Egypt...... it's a hard life  .......
Title: Re: Dorgard (Again?)
Post by: kurnal on February 23, 2014, 09:26:40 AM
Thanks Dave no I was not getting at you either. I am grateful to all contributors for positive contributions, I just dislike personal attacks that don't contribute anything to the debate.

I also can see where these compromises are founded, as an enforcement officer coming into a building for the first time and finding a can of worms that has been passed by your predecessors as satisfactory there is huge pressure to minimise the impact of what needs to be done on the client but to make it safer than it currently is.

Many enforcement officers will not be sufficiently confident to bite the bullet and will take what they see as a practical, functional approach to paper over the cracks often overlooking obvious flaws. 

But it happens to me too, a recent example was in an 18 storey single staircase tower block in which someone had cut a 600mm square hole in a fire door in the staircase lobby and in my fire risk assessment I said the door must be replaced. The assessment coincided with a fire service audit visit. The Enforcement Officer took a different view and said it would be ok provided they did not store more than five mattresses in the store! All I can say to the client is if they don't put it in writing its not worth a light!
Title: Re: Dorgard (Again?)
Post by: kurnal on February 24, 2014, 11:16:15 PM
How was your recent trip K? Hope you behaved?

Hi NT it was good thanks for asking. Find the legislation in Eire and particularly Dublin a bit baffling! Seems to be mega prescriptive when it comes to the approvals for new build and the issue of a fire certificate and in particular the regulation of architects and building surveyors and very much laissez faire when it comes to management of fire safety in occupied buildings and enforcement.  As Dotty would say though there seems to be no bodies on the streets. Makes you wonder whether we really need the regime we have in UK and how it all fits in with the EU directives.
Title: Re: Dorgard (Again?)
Post by: colin todd on February 25, 2014, 10:23:42 PM
Big Al, Always keen to help an old station officer, I can explain the Irish legislation to you, if you want to put 4 pennies in the phone box in Bathmat Lock High Street (like when you sent the fireflash mesages).  Also, you will find that fire risk assessment and some of the management issues are dealt with under HEALTH AND SAFETY legislation. Further, their fire certificate is issued at the design stage, not like when you began doing the hotels over in 1972.  You are right there aren't too many bodies on the street, but then all their fire officers are qualified engineers. We wouldn't have had truck with all these clever clogs in the Bathmat Lock fire service eh?  What is it we used to say when you and I were on white watch playing snooker against each other all night- you can shake a degree all day at a fire but it wont go out.