FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Technical Advice => Topic started by: David Rooney on April 08, 2014, 03:59:53 PM

Title: Grade A and beyond
Post by: David Rooney on April 08, 2014, 03:59:53 PM
A generalised question men....

Very large property, basement to first, approximately 60 rooms in total - building is around 60x20m.

Technically a single family occupancy however there is staff accommodation and also 4 bedrooms to be used by VIP guests on occasion.

Regarding designing a fire detection and alarm system, is it reasonable to spec a pt6 Grade A LD2 system throughout with 75dB at the bedhead in all bedrooms including the visitors/staff bedrooms and providing "minimal" sounders though out the general house hold?

(I realise the family bedrooms would only need 85dB at the door)

Or because of the obligation to protect staff (and maybe visitors) should we be looking for 60/65dB throughout the general living areas in which case we may as well spec a pt 1 L2 system ....??

On a similar vein, would Part M apply to all the WCs likely to be used by staff/visitors - ie. sounder beacons in all toilets??

Many thanks

Title: Re: Grade A and beyond
Post by: Dinnertime Dave on April 08, 2014, 04:59:31 PM
A bit confused on the single family occupancy bit with staff and visitors. If it is purely a single family occupancy then pt 6 makes some recommendations on homes over 200m2.

However, I would think based on the limited information it sounds like the fire safety order applies.
Title: Re: Grade A and beyond
Post by: David Rooney on April 08, 2014, 05:22:21 PM
The place employs one full time butler and a maid.

Should that mean "65dB" throughout and treat the house like a Hotel ??
Title: Re: Grade A and beyond
Post by: Dinnertime Dave on April 08, 2014, 05:26:44 PM
The place employs one full time butler and a maid.

Should that mean "65dB" throughout and treat the house like a Hotel ??

Perhaps not then, I refer to my first paragraph.
Title: Re: Grade A and beyond
Post by: nearlythere on April 08, 2014, 06:50:35 PM
Who are the VIP guests? Is the situation like when we all invite friends to visit and stay overnight?
Title: Re: Grade A and beyond
Post by: wee brian on April 09, 2014, 01:01:14 PM
I was sure there was something that said that domestic staff dont cause a premises to become non-domestic.  But now I can't find it  :-\
Title: Re: Grade A and beyond
Post by: nearlythere on April 09, 2014, 02:52:41 PM
I was sure there was something that said that domestic staff dont cause a premises to become non-domestic.  But now I can't find it  :-\
Thats what I thought WB and it has been covered in the past. They come under H&S@W as employees but the premises are still a private family dwelling. (Depending on who the VIP guests are).
Title: Re: Grade A and beyond
Post by: David Rooney on April 09, 2014, 05:05:56 PM
the guests may be foreign dignitarys ....

Title: Re: Grade A and beyond
Post by: nearlythere on April 09, 2014, 05:31:05 PM
An ambassador's or similar residence?  Senior Military? Minister's freebee weekend retreat? Bishops residence? Your house David?
Title: Re: Grade A and beyond
Post by: idlefire on April 09, 2014, 10:39:11 PM
Part M????

Does Building Regs 2010 actually apply to this fantasy scenario David?

I personally would need much, much more information to give anything like a meaningfull response to the question.
Title: Re: Grade A and beyond
Post by: Mike Buckley on April 10, 2014, 11:55:03 AM
I would agree with the idea that the presence of domestic staff does not change it from a domestic property as with the HSAWA. However with the guests surely the critical point is do the guests pay to stay there? or does the owner profit commercially from them staying there? (more iffy). The actual rank of the person staying there should not matter. (If it did Dotty would never be able to stay anywhere)
Title: Re: Grade A and beyond
Post by: nearlythere on April 10, 2014, 01:27:23 PM
I was considering the place could be a private residence for a family where there was a means for accommodating others who are not paying guests and not actually friends of the family. Take the likes of Chequers which is a private residence for a family. There are times the family plays host to visiting dignitaries and others and not for gain. They may not necessarily be friends either.
I, like most others, have people staying at my private residence. They don't pay and they would be people who I invite as friends or acquaintances to stay (at my expense)
Chequers would be a similar situation where friends, acquaintances and those who become new best friends of the family would stay (again at my expense).
Title: Re: Grade A and beyond
Post by: Mike Buckley on April 10, 2014, 02:08:48 PM
Surely Chequers and similar places will come under the general category of Crown Property.
Title: Re: Grade A and beyond
Post by: David Rooney on April 10, 2014, 06:00:15 PM
Sorry men ... tis an Ambassador's Residence ... arguably the British Government profit from the guests that stay there although they will be non paying. !!

I was basically proposing a Grade A LD2 with 85db at the bedroom doors of the Ambo's family, 75db at everyone else's bed head - guests and staff, and no minimum alarm level set through out the remainder of the property other than being "audible" as per pt 6.

But then I thought about the implications of staff or guests being hearing impaired, hence the question of whether Part M beacons in WCs to EN54-23 is relevant and if the presence of guests whether they're paying or not, would require a minimum alarm level throughout the property ....

How far does the duty of care extend ???!
Title: Re: Grade A and beyond
Post by: Owain on April 10, 2014, 10:42:56 PM
Sorry men ... tis an Ambassador's Residence ... ...
How far does the duty of care extend ???!

How cost-sensitive is the project?

In terms of risk

In terms of fire detection I wouldn't be thinking of anything less than would be provided for a hotel. In terms of sounders I would be looking at a full Voice Alarm system to give information and direction.
Title: Re: Grade A and beyond
Post by: Mike Buckley on April 11, 2014, 11:12:31 AM
The question with an Ambassador's residence is is it subject to diplomatic immunity. I can't find anything  in the RRO except

Application to visiting forces, etc.

51. This Order applies to a visiting force or an international headquarters or defence
organisation designated for the purposes of the International Headquarters and Defence
Organisations Act 1964(a) only to the extent that it applies to the Crown.

On the other hand you have been asked to advise therefore they want it.

My feeling would be treat it as a hotel.
Title: Re: Grade A and beyond
Post by: Golden on April 11, 2014, 11:43:05 AM
Yes its interesting with respect to 'immunity' - I recently carried out an FRA on an embassy and couldn't find any reason to state that it didn't come under the RRO.

WRT the original question I wouldn't view this as an issue of compliance but as the best protection that could be afforded with regard to visitor safety combined with the aesthetics of the building. I'd be looking at good AFD coverage and don't think there's much difference between part 1 or 6 but what level of protection you specify and how you are going to achieve that protection. I can't imagine that the occupiers are going to want obtrusive fittings so you may need some research to find a suitable system.
Title: Re: Grade A and beyond
Post by: nearlythere on April 11, 2014, 12:27:38 PM
Yes its interesting with respect to 'immunity' - I recently carried out an FRA on an embassy and couldn't find any reason to state that it didn't come under the RRO.

WRT the original question I wouldn't view this as an issue of compliance but as the best protection that could be afforded with regard to visitor safety combined with the aesthetics of the building. I'd be looking at good AFD coverage and don't think there's much difference between part 1 or 6 but what level of protection you specify and how you are going to achieve that protection. I can't imagine that the occupiers are going to want obtrusive fittings so you may need some research to find a suitable system.
I think it does come under. It just cant be prosecuted.
Title: Re: Grade A and beyond
Post by: colin todd on April 13, 2014, 06:10:46 PM
I bet Alex the Fish wont let the Lousy Flipping Extra Pathetic Authority into the Scottish embassy in London once we have one.
Title: Re: Grade A and beyond
Post by: Mr. P on April 14, 2014, 08:30:55 AM
Now, that will be something to see. What a visitor attraction it could be! Should be interesting doing a new build or major refurb to house them. Just hink of the arguments over which regs will apply or be most onerous!
Title: Re: Grade A and beyond
Post by: Clevelandfire 3 on April 14, 2014, 11:14:48 AM
Yes its interesting with respect to 'immunity' - I recently carried out an FRA on an embassy and couldn't find any reason to state that it didn't come under the RRO.

Quite right. but be careful may be a building owned by our government which has been leased to a foreign power
, when i say leased don't take it as leased but like almost given to them. well not given to them but you know what i mean. there are reciprical arrangements with those powers. a diplomat may have diplomatic immunity. dont mean the premises does. lets see what big man font of all knowledge colin todd sez about that. bet he has an answer thats helpful and informative.
Title: Re: Grade A and beyond
Post by: Mike Buckley on April 14, 2014, 12:20:48 PM
Yes it would have to be a big building, just think of all those people who suddenly become natives of a foreign non Eu country who will require work permits, visas etc.
Title: Re: Grade A and beyond
Post by: Owain on April 14, 2014, 10:50:30 PM
Yes it would have to be a big building, just think of all those people who suddenly become natives of a foreign non Eu country who will require work permits, visas etc.

Scotland?
Title: Re: Grade A and beyond
Post by: colin todd on April 15, 2014, 06:55:11 PM
Perhaps, when we get independence, we can invade the North and take over Cleveland.  By the way where have you been Clevers?
Title: Re: Grade A and beyond
Post by: Golden on April 15, 2014, 06:56:51 PM
Colin, when you get independence the north will be the south.
Title: Re: Grade A and beyond
Post by: David Rooney on April 15, 2014, 07:08:33 PM
Thanks for responses men, obviously no one has any money to spend on fire detection as we are all broke so they will only pay for the minimum needed.

Hence the key questions that I see remain ....

In these circumstances is 85db at the family bedroom doors acceptable as per reasons of familiarity given in pt 6

75db in guests / staff rooms is taken as read

The usual 60 - 65 db around the general living spaces  ...... yes or no??

Possibility of deaf guests - should we consider beacons in WCs as Part M .... is it a requirement or a nicety in this case??
Title: Re: Grade A and beyond
Post by: Clevelandfire 3 on April 17, 2014, 09:13:17 AM
Perhaps, when we get independence, we can invade the North and take over Cleveland.  By the way where have you been Clevers?

Would you want it? its proper grim.thanks for asking dotty ive been cashing in all the NI ive paid to the NHS all these years by taking board at my local hospital. food was bad but nurses great.

David 60-65dBA should be ok. Unless its going to cost the earth fit beacons in the bathrooms. what provision you putting in for deaf guests elsewhere?
Title: Re: Grade A and beyond
Post by: nearlythere on April 17, 2014, 09:45:25 AM
If and when Caladonia gets UDI will all the invaders be shipped back south and made to reapply for a work permit?
Title: Re: Grade A and beyond
Post by: David Rooney on April 17, 2014, 10:30:01 AM
There is no requirement to cater for deaf guests .... tis our discretion / design.

Title: Re: Grade A and beyond
Post by: Clevelandfire 3 on April 17, 2014, 01:12:15 PM
just wondering why you would install beacons in bathrooms when you are not making provision anywhere else? you looking at buddy system ?
Title: Re: Grade A and beyond
Post by: colin todd on April 19, 2014, 11:39:51 PM
Bet there was no beacons in the toilets in your NHS place , Clevers. I would question if they even cleaned the toilets. I had some lovely food at the Guildford Nuffield recently.
Title: Re: Grade A and beyond
Post by: David Rooney on April 22, 2014, 06:15:23 PM
just wondering why you would install beacons in bathrooms when you are not making provision anywhere else? you looking at buddy system ?

This goes back to an earlier question ... how far does the duty of care extend ?

In the end it is a big private dwelling. I think beacons in WCs is reasonable but would we also expect to see them "in the library... meeting rooms .... dining rooms" etc??
Title: Re: Grade A and beyond
Post by: Clevelandfire 3 on April 23, 2014, 03:14:53 PM
Bet there was no beacons in the toilets in your NHS place , Clevers.


nah, dont need them either nurse led evac theyd come get me if i was mutton. dave, presuming you say its reasonable in the WCs cos yer VIP may lock door so no one can burst in and warn him of fire? so in all other areas if you can use a sort of buddy system then beacons not really necessary
Title: Re: Grade A and beyond