FireNet Community

FIRE SERVICE AND GENERAL FIRE SAFETY TOPICS => Fire Safety => Topic started by: Suttonfire on July 02, 2015, 04:23:46 PM

Title: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: Suttonfire on July 02, 2015, 04:23:46 PM
Hi All,

Now that the above is in place, in response to the recent incident in which fire fighters lost their lives in Stevenage, do you think that it is reasonable that a fire risk assessor should recommended that existing plastic/non fire rated fastenings/fixings and trunking should be replaced in accordance with the new guidance.

I appreciate that the standard is not retrospective; however, it has been demonstrated that  clear that fire rated fixings/trunking can introduce hazards on escape routes.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: kurnal on July 02, 2015, 05:17:43 PM
Would you see the reason for including it in an FRA as being for the protection of relevant persons or for the protection of firefighters engaged in operational firefighting?
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: Phoenix on July 02, 2015, 11:11:28 PM
As kurnal has hinted, I can't see that this is relevant for that part of the FRA that falls under the FSO (i.e. most, if not all, of it).
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: Suttonfire on July 03, 2015, 09:27:27 AM
In response to Kurnal's point - both, the updated standard refers to requirements for wiring systems above escape routes, which indicates that it is applicable to persons escaping from the building (as well as attending to fight fires).

Going back to my original point - If it is now accepted (as identified in the updated standard) that non fire rated trunking/fixings etc present a hazard on escape routes, would it you not consider that a recommendation for replacement of the materials would be appropriate in an FRA?
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: kurnal on July 03, 2015, 12:43:30 PM
I doubt that the recommendation in BS 7671 is intended to be applied retrospectively. however if you see something as a potential problem it cant do any harm to raise those concerns as a recommendation in a FRA - but within an appropriate context. IMO we should remember that firefighters engaged in firefighting duties are not relevant persons and that in most cases such wiring issues are not likely to affect relevant persons during the evacuation phase. There are exceptions however, in particular fire alarm cables and cables supported solely by  plastic self adhesive mini trunking which is likely, without supplementary support to fall on a sunny day never mind a fire.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: nearlythere on July 03, 2015, 02:08:47 PM
I doubt that the recommendation in BS 7671 is intended to be applied retrospectively. however if you see something as a potential problem it cant do any harm to raise those concerns as a recommendation in a FRA - but within an appropriate context. IMO we should remember that firefighters engaged in firefighting duties are not relevant persons and that in most cases such wiring issues are not likely to affect relevant persons during the evacuation phase. There are exceptions however, in particular fire alarm cables and cables supported solely by  plastic self adhesive mini trunking which is likely, without supplementary support to fall on a sunny day never mind a fire.
But is it not a maintenance of a measure for the protection of firefighters?
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: kurnal on July 03, 2015, 03:17:54 PM
I don't think so NT, I think that would only apply to firefighting access, fire men's switches , hydrants and rising mains, compartment walls perhaps, and a few similar  items specifically provided for firefighters under current and former building legislation. IMHO.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: lyledunn on July 03, 2015, 09:58:14 PM
I understand the reason why it might not be necessary to include assessing the security of fixing of wiring in escape routes if the concern relates to firefighting operations. However, NICEIC and others commentating on this new regulation have alluded to premature collapse of wiring systems which could impede escape of building occupants. Likely the fire would need to be fairly advanced for this to happen but I guess that it is not impossible and each situation should be assessed individually. Certainly wiring in "escape routes" should be avoided where possible. Where it does exist, it should be limited in extent and have low smoke emission. When I was contracting one hundred thousand years ago we used escape corridors as cable tunnels and no one considered it unacceptable! I am sure that many of those installations still exist.
Another issue is the use of plastic consumer units. Whilst 7671 limits concern to domestic situations, if the risk has been deemed substantial enough to ban their use in such premises then it would seem somewhat remiss of a fire risk assessor not to at least consider them in other situations.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: Phoenix on July 03, 2015, 10:44:01 PM
Can anyone give an instance or two where people evacuating have had problems because of failing cable supports? 
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: lyledunn on July 04, 2015, 09:26:58 AM
Good point Phoenix. I expect that the emphasis of the regulation is on protection of firefighters but those making a case for including it in 7671 have attempted to strengthen their argument by portraying a risk to occupants. This may be nothing other than a perceived risk, no one actually sifting evidence to present empirical justification. However, say if there was only one case  in the last 10 years of cables falling across an escape route to trap just one occupant, would a risk assessor ignore it?
By the way, the regulation applies to all escape routes, including domestic situations. What is currently being debated is the definition of "escape route" in terms of the intention of the regulation!
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: William 29 on July 04, 2015, 12:05:12 PM
I think we have to ask could it be enforced under Article 38? I suspect not.

It could be mentioned within a FRA and rightly so if a risk to FF's can be seen, irrespective of if the RRO applies or not. In the FRAs we produce there is a clear separation of what is legally required under the RRO and what is not i.e. property protection issues.

As already stated you can't apply this retrospectively to buildings, it would cost a fortune on all but very small premises.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: Messy on July 04, 2015, 11:13:12 PM
Is there even any point of me buying this British standard???????

It seems to me that as has been argued, operational firefighters are not relevant persons so do not have to be considered, and Article 38 refers to maintaining equipment that has been installed to protect fire crews, and does not make it a requirement to fit any such equipment.

So if fire resisting fittings are installed (perhaps as a result of the revised BS) then Article 38 says the RP must maintain them. But it doesnt say it needs them so why (as a hard pressed RP) would you bother??

And I dont buy the idea that persons fleeing are likely to get caught up in fallen wiring.




Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: colin todd on July 05, 2015, 01:20:51 AM
Davey, I am sure your LFB pension will run to purchase of a BS, given the importance of those carrying our FRAs having copies of relevant standards.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: lyledunn on July 05, 2015, 09:09:32 AM
If the actual standard does stretch your pension, perhaps a compromise would be to purchase IET Guidance Note 4, Protection against Fire. This makes reference to the intention of the regulation which is to protect firefighters and OTHERS from entanglement in collapsed wiring systems in escape routes in fire conditions. You could also try directing an enquiry directly to the technical helpline at IET. It would be interesting to establish who the "others" might be and examples of the occurrence of  these "others" being entangled.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: Messy on July 05, 2015, 03:19:02 PM
Thanks for the link Lyledunn

But I think I will just stick to assessing and recording significant findings. I honestly don't think entrapped relevant persons (by virtue of collapsed wiring) is an issue in 99.9% of occasions.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: nearlythere on July 05, 2015, 03:51:46 PM
Can anyone give an instance or two where people evacuating have had problems because of failing cable supports? 



Yeh. 2005 in a block of flats in Stevenage.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: colin todd on July 07, 2015, 11:46:59 AM
Did people have trouble evacuating, Almost.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: Fishy on July 08, 2015, 08:25:37 AM
Yes, you should consider it (it's a fire protection measure contained in national guidance, after all) ... but I'd personally find it hard to believe that you'd conclude upgrading was required in many situations. 

The guidance is poorly conceived, in my opinion... what, in any case, constitutes an "escape route" (any habitable space which people might transit during their escape in case of fire, perhaps) and why would you expect there to be a risk to fire-fighters only in those locations, when their duties might take them more or less anywhere in a building?  If they meant protected escape routes - one would hope that you're not planning to get a build up of hot gases at ceiling level in those?  I reckon many Sparks will end up using metal clips everywhere, because they won't want to get caught out.

An exception might be if you're relying upon smoke control - e.g. shopping malls, atria - and you have cables running across the soffits - could be a legitimate recommendation in such circumstances, I'd suggest?
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: William 29 on July 08, 2015, 09:00:59 AM
Watch this space to see how many enforcement notices we get with the "requirement" to upgrade cables in voids etc??
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: colin todd on July 09, 2015, 08:57:21 PM
You are becoming bitter, twisted and cynical, Wullie.  You need a holiday in Scotland.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: William 29 on July 09, 2015, 09:56:08 PM
I should make the trip really seeing as I am part Scottish! Does that mean you think even more highly of me now??
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: colin todd on July 10, 2015, 11:41:41 AM
Which part is Scottish and from where.  these factors have to be taken into account.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: Mike Buckley on July 10, 2015, 12:21:44 PM
Which part is Scottish and from where.  these factors have to be taken into account

Please report Clan and which side they fought on at the Battle of Culloden.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: William 29 on July 10, 2015, 08:48:04 PM
Which part is Scottish and from where.  these factors have to be taken into account.

My dad and grandparents were born in Stranraer.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: colin todd on July 12, 2015, 12:18:12 AM
D&G is almost England, Willie. They go shopping in Carlisle.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: William 29 on July 12, 2015, 08:50:33 PM
D&G is almost England, Willie. They go shopping in Carlisle.


Ooo so close but no cigar!  :-[
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: kurnal on July 12, 2015, 09:51:00 PM
Some natives of Edinburgh have regularly been seen doing their shopping in Guildford.

Light up the King Edward William as citizens of Britain we are all equal even though some are more equal then others.
Title: Re: BS 7671 update - requirement for fire-resistant fastenings and fixings
Post by: colin todd on July 13, 2015, 11:19:20 PM
Apart from buying a Staus Quo album in Guildford last Saturday, Big Al, I havent been shopping in Guildford since Xmas.

And you say citizens of Britain, so does that mean Almost over in NI is not equal to the rest of us?