Can anyone advise me as to the recommendations regarding pressure testing of FM200 cylinders. Also, what document details the recommendations?
Thanks
-
Of the top of my head, bearing in mind the time of night, I would suggest that the BS for the type & construction of gas cylinder would be the way to go, hich normally has a table of test intervals for that type of cylinder and it's usage (i.e. gas contents & their application). Without looking I cannot be certain, but would bet that it is 10 years like cylinders of similar construction filled with CO2 for firefighting
-
BS ISO 14520-1:2000 Gaseous fire-extinguishing systems. Physical properties and system design. General requirements
I think the pressure testing comes under part 3.
You should test every 10 years, after 20 years test every five.
-
From the General requirements maintenance section of BS ISO 14520-1
"9.2.2 Container
Containers shall be subjected to periodical tests as required by the relevant national standard."
Which would be evry 10 years as the old 20, 10, 5 regime was removed a few years ago when BS EN's replaced the old BS for steel & aluminium gas cylinder testing
-
Thanks guys for your help, very usefull.
VBR
Ashley