FireNet Community

THE REGULATORY REFORM (FIRE SAFETY) ORDER 2005 => Q & A => Topic started by: safety reports on April 09, 2019, 04:12:32 PM

Title: Long corridors
Post by: safety reports on April 09, 2019, 04:12:32 PM
I have a site which the fire strategy states that none of the corridors are longer than the recommended limits (ie 7.5Mtr) however on at least 3 of the floors the length is actually 12.5mtr - there is an AOV in the corridor, there are only 6 flats leading out onto the common parts corridor & the area has an AOV as well.

Does the AOV mitigate the length of the corridor ? If not what would be best to recommend I was thinking to suggest they install corridor doors to break the length
Title: Re: Long corridors
Post by: Revol on May 17, 2019, 08:28:10 AM
I assume we are talking residential flats here?

I don't feel that an AVO alone would not be adequate compensation for the extended distance, certainly not without some further analysis. In a multi stair building AOVs are required on dead ends of 7.5 meters anyway.

BS 9991 would allow 15 meter dead ends if the building was sprinkler protected.