FIRE SAFETY => Fire Alarm Systems => Topic started by: AnthonyB on May 11, 2020, 07:56:04 PM

Title: Audibility in flats for evacuation
Post by: AnthonyB on May 11, 2020, 07:56:04 PM
We are all used to the sound pressure levels for evacuation of sleeping persons, 75dB bed head where a Part 1 system is applicable and 85dB at the bedroom doorway where Part 6 applies (& often used as a variation for Part 1 systems added to blocks of flats being changed to full evacuate from stay put).

What does everyone think about full evacuate systems in blocks of flats where the only measured audibility is 83dB at the flat front (fire) door (and by implication far less at the bedroom due to distance and walls/doors?

Apparently Merseyside FRS are stating this is enough for any blocks of flats needing to evacuate.....I can sympathise with the 85dB bedroom door variation where technically it should be 75dB bedhead as flats common systems should be Part 1, but this surely is a step too far?
Title: Re: Audibility in flats for evacuation
Post by: Graeme on May 11, 2020, 08:55:30 PM
Depending on what the doors are made of the dB(A) isn't going to be any more than 60 in the inside hallway - add fixtures carpets , TV's , music then its a bit pointless imo
Title: Re: Audibility in flats for evacuation
Post by: Fishy on May 12, 2020, 01:21:00 PM
Though it's not a 'fire alarm' system per se, the recently-published BS 8629: 2019 "Code of practice for the design, installation, commissioning and maintenance of evacuation alert systems for use by fire and rescue services in buildings containing flats" recommends that the 'evacuation alert' SPL, measured at the doorway of each bedroom (with the door open), should be at least 85 db(A) and it should be no less 60 dB(A) in any of the habitable rooms.  Not sure whether this is the type of system that's being discussed, or it's one of the BS 5839 variants?

Given that this is National guidance for a system with this fire safety function, I'd suggest that anyone would need a very good reason to say that SPL criteria far less than this would be acceptable?

I'd love to see the Merseyside FRS guidance - or perhaps it's just something an IO came up with and has never been written down?
Title: Re: Audibility in flats for evacuation
Post by: AnthonyB on May 12, 2020, 06:14:32 PM
It's mitigation for structural defects in a part occupied unfinished resi development - apparently it's even in an e-mail from them (trying to get hold of it).

Today heard from a builder that does care home work that in the existing older care homes he works at that where the alarms are not goods enough he's allowed by the FRS to stick wireless linked Grade F detection in as a medium to long term solution.....although it could be just the usual rumour machine in this case!
Title: Re: Audibility in flats for evacuation
Post by: Fishy on May 14, 2020, 09:04:57 AM
I do wish people would realise that just because someone from a fire and rescue service has said they don't object to something, that doesn't make it right, nor legal, nor does it protect them from prosecution under the RR(FS)O, Building Regulations and/or CDM.

Following fire service advice just makes it less likely that they'll carry out enforcement action on you, and that only applies to the legislation they enforce, of course!
Title: Re: Audibility in flats for evacuation
Post by: AnthonyB on May 14, 2020, 06:47:52 PM
Yes, but RP's will take it as gospel, especially if it saves them money and inconvenience and after all they aren't going to be prosecuted unless they have a fire - and no one has fires do they!
Title: Re: Audibility in flats for evacuation
Post by: colin todd on May 20, 2020, 12:41:58 AM
Fish Face, you are such a heretic. Now, a wee pub question for you. What would Holroyd have said in answer to Tony's question and where did he get that answer from?
Title: Re: Audibility in flats for evacuation
Post by: Fishy on May 26, 2020, 09:18:35 AM
I took the bait (appropriate for a fish, I guess).  1970 Holroyd report?  Can't find a copy online so my miserable record on pub quizzes remains unblemished...
Title: Re: Audibility in flats for evacuation
Post by: Graeme on May 27, 2020, 03:25:57 PM
I do wish people would realise that just because someone from a fire and rescue service has said they don't object to something, that doesn't make it right, nor legal, nor does it protect them from prosecution under the RR(FS)O, Building Regulations and/or CDM.

Following fire service advice just makes it less likely that they'll carry out enforcement action on you, and that only applies to the legislation they enforce, of course!

I had a Customer who was told to vacuum their detectors daily by the local FRS - they didnt believe me when I said it wasn't necessary as the Fireman said it was....
Title: Re: Audibility in flats for evacuation
Post by: colin todd on May 28, 2020, 02:12:11 AM
Fish Face, I may need to hurry you, even if you need to take a wild guess or I may have to ask Tony to help you.
Title: Re: Audibility in flats for evacuation
Post by: colin todd on May 28, 2020, 02:14:19 AM
I am sure you misunderstood what the fireman said. He would not expect the guy to do it himself. No. no , no he would have expected the guy to delegate the task to his wife when she did the general hoovering.
Title: Re: Audibility in flats for evacuation
Post by: Graeme on May 28, 2020, 03:58:17 PM
This was a Retained Station so full of Joiners , Painters and Plumbers who are all things expert on FD&A systems  ;D
Title: Re: Audibility in flats for evacuation
Post by: colin todd on May 29, 2020, 09:25:15 PM
Funny that because a lot of whole time fire fighters are "retained" plumbers, electricians and joiners.  Proof, in any were needed, of the symmetry that underpins the physics of the universe.
Title: Re: Audibility in flats for evacuation
Post by: Graeme on June 01, 2020, 09:57:33 AM
Very true and all working for free in their spare time  ;)
Title: Re: Audibility in flats for evacuation
Post by: colin todd on June 02, 2020, 01:40:34 AM
Fish face, Am I going to have to give you a clue?????
Title: Re: Audibility in flats for evacuation
Post by: Fishy on June 02, 2020, 04:17:53 PM
?
Title: Re: Audibility in flats for evacuation
Post by: colin todd on June 03, 2020, 01:01:57 AM
Ok Fish face I am going to have to help you. You do recall Holroyd, who was 943849849084802802842  times better than Dam Jude?  And the so called Holyroyd divide that we have had ever since? The clue lies in the divide.
Title: Re: Audibility in flats for evacuation
Post by: Fishy on June 03, 2020, 10:23:33 AM
Well... when I researched Holroyd I did glean that there were recommendations in his report regarding the optimum size of a fire authority. 

I suppose that it's not beyond the bounds of possibility that the Laird of Rushmore might have observed that there is a difference in the Scottish model for this, compared to other parts of the UK... or am I barking up the wrong caber?
Title: Re: Audibility in flats for evacuation
Post by: colin todd on June 04, 2020, 03:03:55 AM
Not even close Fish Face. You need to address the question. Another clue?
Title: Re: Audibility in flats for evacuation
Post by: Seetek on June 06, 2020, 03:49:00 PM
The Holroyd report recommended that fire safety legislation should be divided into two main branches; one dealing with new buildings (and building works in the form of extending or materially altering an existing building), while the other deals with occupied premises.

The ?address? would be Rose & Crown which led to the first ?fire? legislation (FPA1971), possibly.
Title: Re: Audibility in flats for evacuation
Post by: colin todd on June 08, 2020, 12:04:38 AM
The key point is that Fish Face said that (and I quote):
I do wish people would realise that just because someone from a fire and rescue service has said they don't object to something, that doesn't make it right,

Now what would Holroyd have to say more specifically about that. That is what I want to know. Fish Face, am I going to have to give you another clue?