Author Topic: Advanced MX4020 C&E help required  (Read 4363 times)

Offline mudlark

  • Newbie
  • *
  • Posts: 2
Advanced MX4020 C&E help required
« on: December 18, 2006, 09:03:11 PM »
Is there any-one out there with any experience with on setting this up. I'm having trouble  with setting up an investigation timer plus other settings.

Cheers David

Offline mudlark

  • Newbie
  • *
  • Posts: 2
Advanced MX4020 C&E help required
« Reply #1 on: December 18, 2006, 10:18:04 PM »
The main thing is to get an investigation timer working.
It's for a network rail signal control room. The other bits are different styles on diferent buildings, but first I'm having trouble as I'm using addressable sounder bases which I'm using in different groups. Each sounder group is a diferent building. These are set off by detectors in a particular zone whith the default style 1. This I want to go to style 0 after 90 seconds, which I could do using the phase 2 drive method. But I need to use an investigation timer of up to 450 seconds. This I am assuming is done by setting up the panel delay and actioned from the zero button.
Thats where the trouble is in trying to set this up.
I'm setting up the logic to say that a general action of style 0 for the stage 2 timer. But when you press the button the counter starts but goes straight to style 0. Tried to speak to the techs at advel but no luck yet. Probably asked the wrong questions.
What I'm after is an example type data base with diferent types of set ups to look over.
Nothing found on advel site
No details taught to me when I did their course last year either ( must be an advanced one that they do)

David