Taken from the current Technical Handbook supporting the Building(Scotland) Regulations 2004, for hold open devices, it says,"self closing fire doors can be fitted with hold open devices as specified in BS 5839:Part 3:1988, provided the door is not an emergency door, a protected door serving the only escape stair in the building(or the only escape stair serving part of the building)or a protected door serving a fire-fighting shaft.
It is important that hold open devices deactivate on operation of the fire alarm, therefore some buildings will need automatic fire detection to be installed. Electrically operated hold open devices should therefore deactivate on operation of:
An automatic fire alarm system designed and installed in accordance with BS 5839-1:2002(category L5) determined on the basis of a risk assessment.
Any loss of power to the hold open device, apparatus or switch, and a manually operated switch fitted in postion at the door..
An example of a category L5 fire alarm system could incorporate only 2 smoke detectors, one installed on either side of the door and postioned not less than 500mm and not more than 3m from the door.